Anonymous Poster #1

Unbalanced Loads

04/09/2014 3:54 AM

Hi everyone, Im looking for an explantion if you can assist: In a Delta-Star transformer, does an unbalanced secondary load result in an unbalanced primary load? if not why is this? is there math to prove this?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#1

Re: Unbalanced Loads

04/09/2014 10:13 AM

Unbalanced loads affect the power factor. Power factor is a system measurement which has effects on the service back to the supplier. There are a number of things to consider.

I recommend the IEEE 3000 Standards Collection and also the IEEE Color Book series. The 3000's are replacing the color books slowly but surely. You can read about it at the links I provided.

If the books are too difficult to understand, I would recommend a solid education in the electrical field.

There is definitely math involved.

__________________
common knowledge...less common than common sense
Reply
Associate

Join Date: Apr 2014
Posts: 51
#2

Re: Unbalanced Loads

04/09/2014 11:41 AM

This is very clear from question that connections are in Delta-Star.

So Secondary is in Star and Primary is in Delta . So even if there is unbalanced load in secondary i.e. star even then there will be balanced load in Delta as in Delta there is no neutral so unbalanced load will keep floating inside delta which will ultimately get balanced.

But in Star there is neutral so unbalance current get floating in Neutral.

Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#4
In reply to #2

Re: Unbalanced Loads

04/09/2014 12:05 PM

An unbalanced secondary will result in a reduced power factor on the supply side, i.e., unbalance.

Active, reactive, and apparent power calculations show this.

__________________
common knowledge...less common than common sense
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Unbalanced Loads

04/09/2014 11:55 AM

The currents in the primary winding are proportional with the currents in secondary winding. If the sum of secondary currents is not zero then also sum of the three primary winding will be different [not zero].A zero sequence current will circulate in close circuit through primary winding. However, since the line current is the difference-vectorial-between adjacent windings the sum of line currents will be zero.

The negative sequence will influence the primary line currents, I guess.

__________________
Julius
Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Unbalanced Loads

04/09/2014 2:19 PM

Yes, an unbalanced load on the secondary results in an unbalanced load on the primary, as can be seen by looking at the equivalent circuit of a transformer. It is a passive device with no internal power sources or loads to supply or prevent any imbalances connected to it; therefore, external events on one set of terminals get reflected to the other set.

Yes, you can find the math in any elementary text on AC circuits such as Stevenson, et al. Typing equations in this editor is too prone to error.

Bonus answer...no, power factor is not a measure of imbalance, strictly speaking it is a measure of the angular displacement of the current phasor relative to the voltage phasor.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 3)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #5

Re: Unbalanced Loads

04/09/2014 11:32 PM

..at last a voice of reason.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#7
In reply to #5

Re: Unbalanced Loads

04/10/2014 12:03 PM

Yes, sorry, I got sucked into that misconception again.

I overstated the relationship, considering the effects on both sides the transformer.

Power factor is not related to efficiency nearly as much as a balanced load.

__________________
common knowledge...less common than common sense
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9
In reply to #5

Re: Unbalanced Loads

04/11/2014 11:03 AM

You are right RAMconsultant, it is a very simple issue. However, there are some others which complicate the subject. See [for instance]:

"Propagation of Unbalance in Electric Power Systems"

http://ieeexplore.ieee.org/xpl/login.jsp?tp=&arnumber=4424221&url=http%3A%2F%2Fieeexplore.ieee.org%2Fxpls%2Fabs_all.jsp%3Farnumber%3D4424221

This, it seems to me, is their opinion about unbalance propagation:

"A. General aspects

In the issue of unbalanced voltage and currents propagation

through the distribution system, the main element is the

transformer. Transformer connection influences in different

ways this phenomenon: there are transformers through which

unbalance propagate unchanged and contrary, transformers that

reduce the unbalance factors.

The solving of the unbalanced operating state of a threephase

transformer means the finding of the following

quantities:

- primary and secondary phase-to-phase voltages;

- primary and secondary line currents;

- current through the neutral conductor (if it is any).

To establish the solution of this problem, the following data

are required:

- transformers rated parameters;

- primary phase-to-phase voltages (considered symmetric);

- consumers parameters that produce the unbalanced

loading.

Because finding the solution of this issue in the general case

is complicated, the analysis will be made considering that the

supply voltage system is perfectly symmetric; the transformer's

magnetization current is neglected and the transformer is a

linear load, in consequence the superposition of effects is

admitted."

__________________
Julius
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #9

Re: Unbalanced Loads

04/11/2014 11:42 AM

...and your point is???

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11
In reply to #10

Re: Unbalanced Loads

04/11/2014 11:56 AM

I think it depends on how accurate result it is required. Neglecting voltage unbalance it could be a considerable error-in my opinion. However the calculation presented-even simplified as it was said-it is sophisticated enough involving matrix and so on.

__________________
Julius
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#12
In reply to #10

Re: Unbalanced Loads

04/11/2014 1:26 PM

HI believe his point was this: "...Transformer connection influences in different ways this phenomenon: there are transformers through which unbalance propagate unchanged and contrary, transformers that reduce the unbalance factors...", note the word "reduce" not "eliminate".

Unfortunately at the end of this section the authors destroy his argument by saying "...Because finding the solution of this issue in the general case is complicated, the analysis will be made considering that the supply voltage system is perfectly symmetric..." Well, duh, how do you expect to see any influence the load side might have if you don't allow the supply side to change?

Here's the original paper, it contains a nice introduction to symmetrical components, and provides a mathematical "proof" of something that is well known, how a zig-zag secondary winding "traps" zero sequence currents, but does not eliminate them. What's missing from the paper is any correlation with actual data, an experiment that can be easily performed in any college AC Machines lab.

Unfortunately OP's question was about delta-wye (and made no mention of a ground), but as an educational exercise you can use the formulas to calculate the following two cases: phase A open on the high side and then phase A open on the low side, and present your results, it is unlikely that you will find that an unbalance on one side has no unbalance on the other. The authors use the term "unbalance factor" for a reason.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#8

Re: Unbalanced Loads

04/10/2014 3:32 PM

I don't bother answering anonomous posts. Oh darn, I just did!

__________________
If it was easy anybody could do it.
Reply
Associate

Join Date: Apr 2014
Posts: 51
#13

Re: Unbalanced Loads

04/12/2014 5:27 AM

If your fundamental still not clear whether secondary unbalance load will results into primary or not then visit link below and see connections and will clear your doubts:-

http://electricalsystembasics.com/transformer-connection-types-applications/

Reply
Reply to Forum Thread 13 comments