What is Better?

04/10/2014 7:23 AM

I have to use an underground cable to transmit the electricity from the power supply to the main distribution board; and the distance is around 400 meters and due to the high cost of the copper cables comparing to the Aluminum cables. So, I am wondering what type of cables to use for the following cases:

Case 1:

380 V, 3ph, 80- 100 KW (estimated load for a small farm house, might be higher)

Case 2:

220 V, single phase, 80-100 KW (estimated load for a small farm house, might be higher)

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: what is better?

04/10/2014 8:29 AM

from what I've heard "copper is cheap and abundant", just don't let the Meth-heads know where ya buried the cable.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: what is better?

04/10/2014 8:50 AM

Sounds to me like you need to have a proper load calculation done on both properties before you go any further with designing these conductor runs. A 100 KW of three phase power is a lot of power for a "small farm house". Even at 220 V single phase... 100 KW sure sounds like a ridiculous amount of power for a "small farm house".

This sure sounds like a school project to me, as such, doing a couple of proper load calculations and coming to realistic demand values would be a good learning opportunity and is the basic data you need before continuing with this design..

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Participant

Join Date: Apr 2014
Posts: 2
#3

Re: What is Better?

04/10/2014 9:13 AM

thanks all for your replays, it is not a school project and i am doing it for my own benefit; and for the load I only estimated it real quick because I am Planing to have like 10 air conditioners (window types ) lighting fixtures (internal & external ), 3 water pumps, etc.

Also, the copper will cost triple the amount if i used the Aluminum, but i am asking what should I also consider beside the price since it is going to be for lifetime step.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#5
In reply to #3

Re: What is Better?

04/10/2014 9:29 AM

as soon as you mention 3PH most people here think of commercial or industrial operations, typically residences aren't supplied with 3 PH. its true that aluminum can carry this amount but its not the best idea. aluminum has high expansion and contraction rates so its connections are critical. overheating and fires are very possible. many places in the US have banned its use for these reasons.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#7
In reply to #5

Re: What is Better?

04/10/2014 10:57 AM

Actually aluminum is the primary material used for primary feedlines from the utility connection point to the main distribution box.

Very few places use copper in residential or light commercial primary feeders now.

Register to Reply
Power-User

Join Date: Jan 2009
Posts: 250
Good Answers: 7
#10
In reply to #5

Re: What is Better?

04/10/2014 12:51 PM

"typically residences aren't supplied with 3 PH"

this is true for the US only.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #3

Re: What is Better?

04/10/2014 9:48 AM

Use a search engine and find a cable sizing site. Don't ask strangers.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#11
In reply to #3

Re: What is Better?

04/10/2014 1:26 PM

You should re-calculate your load and this time estimate it real slow.

That's enough power for many small farm houses...unless they are farm "grow houses".

Estimating power "real quick" usually leads to "real expensive" construction costs.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#13
In reply to #3

Re: What is Better?

04/10/2014 2:18 PM

On a 100 KW feeder based on a 220 VAC single phase power source for a 400 meter run you would be needing either 4 4/0 (12 mm dia) aluminum conductors in parallel for each leg or 2 MCM 500 (18 mm dia) or 1 MCM 1000 (26 mm dia) sized conductor for each leg.

On a 380 VAC three phase feed you would be right at the limits with a single 4/0 (12 mm dia) size aluminum feeder for each phase and the common return.

No matter how you cut it its going to be expensive.

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#4

Re: What is Better?

04/10/2014 9:19 AM

In Dubai, United Arab Emirates, that distance would be too far a distance, so you would need MDP (mini distribution pillar) installed between your house and the nearest substation. I don't remember but the max. distance for underground cable run from utility supply must be 300 meters. Once that achieved, then I could help you with design. the MDP has two to three outgoings that one could bring your house supplied with? :)

__________________
--
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: What is Better?

04/10/2014 11:03 AM

It sounds as though British Standard 7671 would be very useful bedtime reading.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#9

Re: What is Better?

04/10/2014 11:05 AM

80 - 100 KW seems very high even for air conditioning loads and especially so for a small farm house.

What dimensions of house are we talking here and what ate ambient outdoor VS indoor temperatures you will be dealing with?

I was recently over in Turkey and they typically see 120+F summertime temps with high humidity and blazing sun. Even with that I did not see a single house that had more than 6 10K - 15K BTU room air conditioner units installed of which not one of them uses much more than a KW at best.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12

Re: What is Better?

04/10/2014 2:14 PM

This is an extremely long run for a residence....normally you would have a step down transformer within shouting distance....Bearing in mind that higher voltage requires a smaller wire size, I would get a step up transformer at the beginning of this run, and step up to 600v 3Ø and use aluminum wire(4/0), and then step down the voltage next to the house...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#14

Re: What is Better?

04/10/2014 3:52 PM

My first response would be use transformers at each end to increase the transmission line voltage, and thus reduce the current carrying requirements and have less losses as well. Most EE's will suggest saving money by investing in a step - up - step - down configuration. Of course, now you would have 2 - 100kw PT's. So there might be a trade off in cost/ distance, I'm betting the smaller guage cables will offset the Xfmr costs.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#15

Re: What is Better?

04/10/2014 6:58 PM

After I'd stopped laughing I came up with a 185mm² 4c SWA for 380V. Even that is pushing things with 4% VD @ 100KW.

PS that was for copper, I couldn't be bothered to look out the BS7671 tables for Al.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#16

Re: What is Better?

04/10/2014 10:29 PM

Half a kilometer distance from the distribution line is a far enough of a distance that I would consider a distribution transformer and get your power feed at a higher voltage from your utility.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#17

Re: What is Better?

04/10/2014 11:12 PM

Putting things in perspective and comparisons:

100KW is 1/10 of a megawatt, that's a lot of electricity.

If all this is for a small farm house, what are you doing in it? Sounds like you may be operating a moonshine still and heating the mash with electric heating. That's a lot of moonshine, do you have a market for it?

Unless you have your own hydroelectric power plant a guy who lives in "a small farm house" won't be able to afford the electricity at 100KW.

Suggest you re-evaluate the predicted loads and start from the beginning. Also get yourself an EE specializing in power distribution to assist you. The mistakes you make could be very costly or dangerous without him

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#18
In reply to #17

Re: What is Better?

04/10/2014 11:39 PM

Hydroponic pot farm? Grow lights and a deep well?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#19
In reply to #18

Re: What is Better?

04/10/2014 11:53 PM

You got yer lights, pumps, ventilation, climate control.....adds up

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#20
In reply to #18

Re: What is Better?

04/10/2014 11:58 PM

Maybe both! Moonshine marinated pot! I love the idea. Marketing slogan-->"A high with a buzz!"

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#21

Re: What is Better?

04/11/2014 12:44 AM

That's a long way to run LV at that sort of loading (as others have said that is a lot for what you have described) especially underground.

Recheck your loading calcs/estimates and then perform a conductor sizing exercise.

If you want to know whether Al is as good as copper......yes it is iff it is correctly sized, correctly installed and properly terminated with unobstructed access to the terminations for inspection and maintenance, and there is enough cable slack to reterminate a few times during the life of the installation if required. It's most definitely less costly than Cu.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#22
In reply to #21

Re: What is Better?

04/11/2014 3:08 AM

al, I agree it is a long run for L.V. I have said it above in #4 or so as I cut and paste:

In Dubai, United Arab Emirates, that distance would be too far a distance, so you would need MDP (mini distribution pillar) installed between your house and the nearest substation. I don't remember but the max. distance for underground cable run from utility supply must be 300 meters. Once that achieved, then I could help you with design. the MDP has two to three outgoings that one could bring your house supplied with? :)

__________________
--
Now I am also saying this. If he is in Dubai or not but we all agree on this that his L.V run is too long of a run. As far as I have known, the utility would accept a max. run of 300m or so. 1) He is saying an underground cable run. So first he must get either confirm or get approval from the power company whether or not his long run would be acceptable according to the local regulations. If not, then they could give him some info as to how far they either having the MDBP already installed in the area or would be installing one for his premise? If they already have one already there then he could get the distance as to how far? It must be in the 30 0m length. If not already (as it must be the case look like:) then he must ask whether they could provide one near his home. If they say they could then at what distance it would be from his premise. If there is a near substation and they could install an MDP between his premise and the substation, what distance the MDP would be of his premise then? Once that distance is known then we could calculate the rest distance from M.D.P to his premise. Then we could find the cable size, the voltage drop, etc. Say the distance of the substation to his house is 400 m. In the view of the 300 m requirement, they must have an M.D.P installed from the substation at a distance of 120 m, per say. Then 400 m - 120 m = 280 m which one has size the cable for. That would the distance be between the utility supply (M.D.P) and his premise, the house or so. That would save money on cable etc.2) If there isn't any other way and he has some overhead transmission and distribution in the area, then he could run an overhead line with Dist. transformer and H-Pole right next to his premise. That is not my line of work though. He could have a PT with that KVA? 3) These people don't put enough info to begin with. They just like the forum's brainstorming? They don't bother visiting the utility offices because the Arabs setting in those offices are like dogs, barking at people. They think the rest of the people are just their SLAVES. I think they need proper education that a small band of people called Jews in Israel has beaten their ass not once but multiple times. Only dog is best barking in his or her yard, nothing else...My apology in advance!

__________________
--
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#23
In reply to #22

Re: What is Better?

04/11/2014 3:18 AM

....don't hold back now.

Yes, dealing with authorities is not a joy ride any where in the world.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#24

Re: What is Better?

04/12/2014 9:57 AM

Old Salt is right, get an EE to recalculated your load and design. My house typically uses 1 kw, and I can see how a big house with lots of HVAC could use 10 kw, but 100 KW can power over 10 houses, even big houses in the UAE.

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#25

Re: What is Better?

04/14/2014 2:53 AM

use al cables of suitable size after calculating for drops etc. armoured cable will be better

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 25 comments

"Almost" Good Answers: