Participant

Join Date: Apr 2014
Posts: 3

Relation Between Stray Capacitance and Ungrounded System

04/29/2014 9:48 AM

hi all



about this netwrok regardless of the connection star or delta,let's assume this is 380 v system,so,at normal case: if we measure voltage AC it will be 380 ,and voltage AG OR BG OR CG will be 220 as a result of capacaitvly grounded network.
at faulty case : voltage AG will be equal to BG = 380
so AG=BG=AC=BC= 380,,,
I really want to understand how does it come and why the voltage increases to 380 at faulty case..and relation of stray capacitince .and the voltage across each capacitor at the 2 cases.

Register to Reply
Pathfinder Tags: stray ungrounded
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: relation between stray capacitance and ungrounded system

04/29/2014 9:51 AM

If one of the phases faults to earth/ground, then, self-evidently, the voltage of the other two phases will be 380V to earth/ground now, just as they are 380V to the other phase before the fault occurred. A single phase-to-earth/ground fault does not necessarily operate simple circuit protection devices such as fuses in IT systems, which is why something a little more involved must be used for the best safety.

http://en.wikipedia.org/wiki/Earthing_system - see "IT" systems.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Relation Between Stray Capacitance and Ungrounded System

04/29/2014 10:32 AM

It has very little to do with the stray capacitance, it has everything to do with how ungrounded systems react to the first fault on any leg. The stray capacitance merely provides an artificial floating reference point, and all three legs only read the same voltage when the system is unloaded or perfectly balanced. Under any other conditions the neutral "floats" giving the condition known as "neutral shift". High availability systems take advantage of this phenomena in their protection schemes by monitoring each phase to safety ground voltage. When a fault occurs the voltage to ground on the other phases rise to 1.73 x normal and triggers an alarm and the system continues running normally, but that fault need to be cleared ASAP or the second fault will cause real problems and the protective devices will operate.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#3

Re: Relation Between Stray Capacitance and Ungrounded System

04/29/2014 1:46 PM

First the definition of a capacitor, Two conductors separated by an insulator. In this case the "capacitor" is/can be the current carrying conductor and the conduit, what ever. If the conductors are of sufficient length, you can light a 100 watt bulb, by this, or even electrocuted.

Ships use this system extensively to minimize corrosion, and maintain system operation in the event of a short to ground. As your meter has relatively high input impedance, (this includes the old Simpson 260) you can measure this voltage.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #3

Re: Relation Between Stray Capacitance and Ungrounded System

04/29/2014 5:09 PM

The Simpson 260 has an AC input sensitivity of only 1,000Ω per Volt, as opposed to a modern Fluke Digital Multimeter which has an input impedance of 10MΩ, the same as the old VTVM, which results in far less loading on the AC circuit.

The Simpson will very quickly discharge that loosely coupled capacitor, while the Fluke will read its voltage. That's why Fluke (and others) now have models with a Dual Input Impedance switch to replicate the input impedance of the analog meters, allowing its use on both power and electronic circuits.

Also, that would be one really huge capacitor if it could pass enough current to light a 100 watt bulb! Unlikely to occur with 2 wires running parallel to each other; what does occur is inductive coupling, and that can bite you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#5
In reply to #4

Re: Relation Between Stray Capacitance and Ungrounded System

04/29/2014 7:49 PM

Several thousand feet of cable stuffed in metal conduit routed along steel bulkheads does just that. With these values, even the Simpson 260 would read it.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #5

Re: Relation Between Stray Capacitance and Ungrounded System

04/29/2014 9:06 PM

No doubt at that length. Had a strange case of a 120 Volt relay in a power plant that would not release when the AC was cut, traced it through 1.6 miles of control wiring, did the calculations, and sure enough there was enough capacitance to keep it "energized" despite having no control power feeding it.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Relation Between Stray Capacitance and Ungrounded System

04/30/2014 8:17 AM

That is:

  • useful to know and
  • a good justification for going DC instead with suppression across the coil.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor
Engineering Fields - Nuclear Engineering - New Member

Join Date: Feb 2013
Location: Washington (the state), 2 blocks from the Columbia River
Posts: 21
Good Answers: 4
#8
In reply to #6

Re: Relation Between Stray Capacitance and Ungrounded System

04/30/2014 12:03 PM

I have almost run into this in a current project, we need to control a unit 2500 feet away: my tech lead pointed this potential problem out and had a bulletin from Square D about this "long distance signalling" problem. I went to the Schneider Electric website (SE now owns Square D) and got the latest. There are two bulletins: Bulletin No. 8502DB0001 and Bulletin No. M-379F. Good reading, and gives alternative methods of control too. The text in both is pretty much the same, but there are many more tables in the 379F. Do note the tables are pretty specific to Square D, as they are set up for the Square D starter number, size of wire, supply voltage to give a final number of maximum feet distant. In some cases surprisingly short, but the numbers have been worse-cased.

__________________
The reward for a job well done is another job.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Apr 2014
Posts: 3
#9

Re: Relation Between Stray Capacitance and Ungrounded System

05/08/2014 5:44 PM

thanks all..
but still no one answer my point,
i want to understand this quotation "When a fault occurs the voltage to ground on the other phases rise to 1.73 x normal"
What is the reason for this rise!!!

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10
In reply to #9

Re: Relation Between Stray Capacitance and Ungrounded System

05/08/2014 8:12 PM

Reread post #2, normally phase to neutral voltage is ph-ph V/√3, when you put a phase conductor to ground you have "shifted" the ground and made all ph-ph and ph-n voltages read the same. For more info draw a before and after diagram, then Google on "neutral shift".

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ahmedrahman (1); JL Dowell (1); JWthetech (2); PWSlack (2); RAMConsult (4)