Air Cool Chiller

04/30/2014 10:53 AM

we install air cool chiller capacity 60TR including 3 compressor , 2 ID fans (R22)

entering water temp. -12c°

leaving water temp. -10.5c°

Amb. temp.- 43c°

Comp. current are- 42, 46, 50 amps resp.

Due to increasing amb. temp. compressors tripping with certain interval

What i do? please suggest !

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Air Cool Chiller

04/30/2014 11:29 AM

1. Clean the condenser.
2. Induce global cooling.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#2

Re: Air Cool Chiller

04/30/2014 11:33 AM

What are the design conditions to go along with the actuals you have given? What kind of compressor, voltage, FL current? Any reason for the difference in the 3 currents?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Air Cool Chiller

04/30/2014 1:17 PM

How do you know that the compressors are tripping due to increasing temp..? Why are the breakers tripping? Overamp draw? Overheating? What size are the breakers? What is the full load rating on the compressors? What is the total amp draw? What is the quality of power supply, are you experiencing brownouts?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: Air Cool Chiller

04/30/2014 1:48 PM

I would talk to the equipment supplier in the first instance, Boss, and arrange a service visit from one of their specialists.

__________________
Good moaning!
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Air Cool Chiller

04/30/2014 6:10 PM

Sorry, are you saying your ambient and water temperatures are below freezing?

I am guessing not, but thought I should at least ask just in case.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#8
In reply to #5

Re: Air Cool Chiller

04/30/2014 8:32 PM

he means C not F

Register to Reply Score 1 for Off Topic
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10
In reply to #8

Re: Air Cool Chiller

04/30/2014 8:59 PM

Ok...are you sure? In previous posts he has clearly indicated degrees Celsius and other metric units.

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#11
In reply to #10

Re: Air Cool Chiller

04/30/2014 9:03 PM

his ambient is almost 110F..........I dont need the chill temps to know why he's tripping

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#16
In reply to #11

Re: Air Cool Chiller

04/30/2014 11:39 PM

In certain parts of the world, "tropicalized" equipment is specified. Equipment specifically built to handle much higher ambient and corrosive conditions. Sealed controls to keep out bugs and mold and sand. Oversized condensors. Here's hoping the original designer knows about the actual operating conditions.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply Off Topic (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #8

Re: Air Cool Chiller

04/30/2014 9:35 PM

He means + rather than -.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#13
In reply to #12

Re: Air Cool Chiller

04/30/2014 9:42 PM

I still say use a charging chart or its overcharged

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14
In reply to #13

Re: Air Cool Chiller

04/30/2014 9:50 PM

That's why your post 7 is a GA. Less likely, but perhaps possible, would be noncondensables in the system, such as from prior maintenance without proper vacuuming.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Air Cool Chiller

04/30/2014 8:28 PM

how are the fans being staged?

Register to Reply
3
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: Air Cool Chiller

04/30/2014 8:31 PM

put a set of gauges on it, wait 10 minutes, set up a 60 second video, fire it up......show me the video and I'll tell you(that its overcharged for your condition)

Register to Reply Good Answer (Score 3)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9

Re: Air Cool Chiller

04/30/2014 8:34 PM

use one of these or you'll never get it right

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#15

Re: Air Cool Chiller

04/30/2014 10:54 PM

Your machine is likely "designed" for operation at 35C, so cooling air is at best 97% density.

Suggest that you replace existing ID fan motors with ones sized for next higher speed and next higher HP, then drive with VFD directly controlled by compressor head pressure (higher pressure = higher speed). Fans will actually "drive" at about 15% higher speed than current.

At this capacity unit, costs should be relatively low- US$500 to US$750.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#17

Re: Air Cool Chiller

05/01/2014 1:46 AM

In addition to the suggestions reported here you can check the pressures and gas leakage. There could be many causes. Proper diagnosis is required and it can be done with the help of service expert.

Register to Reply
2
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#18

Re: Air Cool Chiller

05/01/2014 2:45 AM

Hello Dinesh,

It would be a lot easier to give you advice regarding your chiller problem if you provided more information!

- What is the chiller tripping on? Overcurrent (overload), High Pressure, Low Pressure, Oil Pressure?

- What are the operating pressures?

- Condenser in & out temperatures?

- I understand this is an air cooled condenser - at what pressures/temperatures are the fans set to operate and is the condenser clean?

- Has this problem just developed or has it been a problem since installation?

- Have you checked why you have a difference in your line currents? Is your supply voltage balanced?

- Does the tripping only occur when the ambient temperature is high and not at night or during cooler times?

Your Delta T (temperature difference) across the chiller of only 1,5 deg C points to a very inefficient system. Was this a new or second hand chiller? Is your water flow correct? Are the tubes clean?

The solution to a problem normally becomes much clearer when you look at the complete system and take readings so that you not only see the effect but also the cause.

Hope this is of assistance to you.

Good luck!

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Good Answer (Score 2)
Active Contributor
India - Member - New Member

Join Date: Jul 2013
Location: India
Posts: 13
Good Answers: 1
#19

Re: Air Cool Chiller

05/01/2014 9:52 AM

- I clean the condenser 4-5 times in day with water spraying

-its tripping only day time when amb. temp. is high (not in night)

- Due to increasing amb. temp. consequently any one of three compressor current increasing and its tripping

Register to Reply
3
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#20
In reply to #19

Re: Air Cool Chiller

05/01/2014 11:30 AM

Hi Dinesh,

Why are you cleaning the condenser so frequently? Is this installation in an area where the condenser fouls quickly?

You didn't answer the question as to what the chiller was tripping on but from your post it would appear as if the chiller is tripping on overcurrent (compressor current increasing and its tripping).

You need to follow the pointers given in my previous post and provide answers to those questions of which the most important is the operating pressures i.e. when your ambient temperature goes up the high pressure will also increase. The low pressure reading will also give an indication as to whether the chiller may be overcharged. An overcharge of R22 will result in a dramatic rise in head pressure. Before making any pressure readings ensure your manifold gauge set has been reset for your altitude. Also your system should be charged correctly for the installation altitude (a system charged at sea level and installed at higher altitude would be undercharged and charged at altitude and installed at sea level would be overcharged).

A rise in operating current is an indication of the compressor having to do more work (in this case working against a rising head pressure) and from what you wrote about having only a 1,5 deg C drop in chilled water temperature this rise in current is not being translated into cooling.

The rise in current could also be caused by a rise in the cooling load which results from the higher ambient temperatures.

- Was this chiller sized correctly for the application?

- Was any heat load calculation done for this installation?

- Is the chiller used for comfort air-conditioning or process cooling?

- Is it possible to reduce the load on the chiller by switching off some of the loads during which you can monitor what happens to the chiller?

- Have you tried starting the chiller earlier when the ambient temperature is lower which would allow the chiller to bring the chilled water under control before the ambient temperature increases?

- Have you consulted the suppliers/installers of this chiller regarding this problem?

My recommendation is to start dealing with the facts of what is causing this problem - the rising current is one of the results not the cause. You will need to take all the proper measurements in order to be able to identify the cause and indicate a solution.

Hope the above is of assistance!

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#21
In reply to #19

Re: Air Cool Chiller

05/01/2014 6:02 PM

Sounds like it's undercharged to me....You probably need to pump these units down to get the oil back in the sump...but all we can give is possibilities without the info required for a proper diagnosis....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bigg (1); Crabtree (1); dinesh bagal (1); energygod (1); Fredski (6); jack of all trades (2); Keith Grewar (2); mrswamy (1); Ried (1); SolarEagle (2); Tornado (3)

Previous in Forum: Metallic Bellows Designing Piping   Next in Forum: Steering Column

Advertisement