Respected engineers,
I am facing a problem (again ) and seeking for an answer "How a germanium transistor can be replaced with a silicon one"? I have provided a vintage Swedish Army power generator with a burned AVR. I LOVE the way it's build and wish to repair it BUT it is too complicated (expensive) to provide 2N174A, the vintage germanium transistor, the heart of the avr. Even if I provide one, it is question how soon I might need another one (knowing me ). Here are some photos and I would really like to hear any opinion about the way of replacing old type germanium transistors with a more easy to find, silicon ones.
The generator has an option for a manual adjustment of the excitement that works fine. It produces both 12V DC and 220V AC if adjusted by a reostat. That bypasses the avr and make the unit usable. The automatic adjustment (needed for bigger power loads) does not work due the fried transistor.
Could anyone suggest what to do to "swap" the germanium transistor with a similar 150W silicon one.
(all catalog replacements are also germanium ones hard to find)
best regards
Mishel
Good Answers: 145
Re: Can a germanium transistor be replaced with a silicium one?
04/30/2014 7:47 PM
My second Google hit was rfparts.com and they have them in stock for $9.95. That would seem like the easiest way to go.
Good Answers: 88
04/30/2014 8:05 PM
Substituting transistors is not that straightforward, even catalog substitutes are not guaranteed to work in all cases, it depends on what is exactly doing in the circuit (switches, amplifies linearly, has to match with something, etc). But with some gain tweaking, a TO-3 like MJ15004 should work in your case, assuming it's used to control exciter current, if everything else in the circuit is verified OK. Type "germanium" should not be critical since the MJ has relatively low saturation voltage even for chopper use and as a newer design and higher power, should be more robust. S.M.
05/06/2014 4:37 PM
The MJ15004 works fine!! I've done some drilling and soldering at the module and checked the generator today with the altered AVR. It gives steady 220 VAC, no problems at all. Tested only with a grinder and a drill (approximately 1KW each).
I will check it again with a more demanding load during the week and inform about the results. I intend to hook the welder and see if it works.
thank you all for helping me
Mishel
Good Answers: 88
05/06/2014 7:25 PM
Hold your horses. MJ works as I expected but look now. If you apply a load that the generator can't keep up with, the motor rev will dip and so will the output voltage. The AVR will increase exciting current to compensate for lower voltage and if it goes over its current or dissipation limits, puf, there goes your power transistor. The idea is to not allow the transistor to get into that area even at the worst case scenario. A good approach is to measure the exciting current at normal conditions (I believe it will be less than 5A) and use an appropriate external power resistor in series with the exciter coil to limit both the power dissipated by the transistor at normal conditions and the maximum current it can send to the exciter coil when gen is overloaded to less than double the normal current. S.M.
Good Answers: 444
05/06/2014 8:02 PM
SM,
Good point. Usually the AVR circuitry limits the drive so that there is a point called the "Ceiling Voltage" beyond which the current in the field won't go any higher, but with all the part substitutions that point may have shifted. I suspect those wirewound power resistors may also play a part in that as well, and it's not the power transistor that's at risk, it's the field and stator windings plus all the iron that needs the protection from the excess heating from overexcitation. Poor power factor loads like some welding machines can wreak havoc on small generator sets like this one.
RAM
Good Answers: 117
05/06/2014 11:47 PM
Beautiful description. Wish I was that good! Good Answer.
Good Answers: 88
05/08/2014 10:38 AM
Being overrated is bad for the character, but thanks anyway. (LOL) S.M.
Good Answers: 27
05/08/2014 2:17 PM
I agree with Yusef1's comment Being able to give a savvy and constructive comment like yours is not being overated!
Your comment just demonstrated / showed a person's experience /knowledge on the subject matter!
vsar
05/07/2014 4:17 AM
Yep, I will be careful and will increase the loads with the eye glued to the instruments (it has both Voltmeter and Ampermeter on it). I am calm because this generator has an electronic circuit that "shuts of" the output voltage if there is a ground problem or over-voltage regime. I guess it is designed to protect from surges and eventual shocks if not grounded properly. That's why I want to repair and keep this one !
And, it is not a small at all, I mean , it should have at least 5KW, fair enough for the welder.
regards
Mishel
04/30/2014 8:23 PM
I did a quick Google search, and it looks like the 2N174A, as others have said, is still available. Lots of times power transistors are in a push-pull circuit with a matching transistor of the other polarity (PNP - NPN) and you wouldn't want to substitute. Best to replace it with the same type.
Good Answers: 67
05/01/2014 12:10 AM
Find out *why* the transistor burned out before replacing it with a new part. Look carefully at the other components (a bright torch and magnifier does wonders) and the circuit board. Any discoloring from heat. There may be other problems. Foreign matter present, possibly causing a short.
I found a slender silver necklace chain in my Ferrups 2 kVA UPS. The chain belonged to one of their assemblers. It shorted the circuit board before falling into a narrow groove in the chassis. I saw the chain only when I turned the unit over. Check carefully for conductive debris that may have gotten inside. You said it was vintage?
Good Answers: 444
Re: Can a Germanium Transistor Be Replaced With a Silicium One?
05/01/2014 11:54 AM
This is a power transistor that acts as the analog output amplifier for the AVR. A slight mismatch won't upset anything, but since the part is still available why make new problems. The above advice is important to follow, if the transistor keeps acting as a fuse you have to find out why.
In addition to examining the circuit board for shorts, burnt traces, etc., you need to check everything from the output of the transistor to the field winding since a short anywhere along the line will smoke the transistor. The fact that the manual portion works ok may be a good sign meaning that somewhere between the output of the transistor and the first thing it touches is where you should concentrate your efforts.
05/01/2014 3:20 PM
Thank you all for your inputs,
here are some more details regarding your posts....
- I also found some offers of the original one and I am aware that it is always better to use the original transistor. I may sound cheap but having in mind the price, shipping cost and the possibility that I might need more than a one transistor () I am considering the "swap" option. It should not be critical since it is not Push-Pull or other circuit design that needs good pair (match). The original transistor is used as a regulator of the rotor field (excitement) and it has an adjuster in the circuit so, as far as I understand, the working point of the new (close match) can be altered in some range so it is possible to have automatic feeding of the rotor, more or less. I have never attempted any similar steps so I thought it would be better to consultant brighter brains for electronics (before I f... something again)
-the unit works with the manual regulation of the field excitement so I would say it is not very likely that part of the unit has any problem. I don't like the manual regulation because when I use inductive loads (electric arch welder) the output voltage of the generator drops significantly and the arch is not good. Manual adjustment provide a usable performance for constant loads (pure resistive) but poor for more demanding inductive loads. .
-Yes, I think I found the reason, at least one of them. It is overheated resistance 100 Ohm/10W (open - no reading at all) and I change it (the one with the adjuster). The unit might have some hidden problem that will bring me back to the first paragraph.
-will ask tomorrow for MJ15004 and try it! Several other options have been suggested by some friends in the field (BU208, BUT11) but I've decided to ask experts for advice.
-I guess we can say it is vintage, it's made in the early 70' for the needs of the Swedish Army. The engine is JLO L230, two stroker with mechanical centrifugal speed regulator (good compression and generally well maintained unit) and the generator is 220V AC and 12V DC, brushes collector/automatic voltage regulator (the module with the burned transistor). This is the Genset before the restoration started, it is all better now except the AVR
thank you all again
greetings from the rainy Macedonia
Mishel
Good Answers: 117
05/02/2014 8:51 AM
Good feedback! Thank you!
You are the kind of poster we all love here!
05/01/2014 11:12 PM
No easy swap out from Germanium to Silicon.
The "turn on voltage" for a Germanium is .3volts and silicon is .7 volts(approx).
Best to bite the bullet and get an original spec. replacement.
05/02/2014 3:07 AM
How about simply replacing the whole AVR with a modern fixable unit......you might even find a cheap 2nd hand one in a unit where the prime mover is already destroyed for some reason, maybe on ebay for example....
Fixing an old pre-silicon unit means that even if it works eventually, the same problem could happen again......or an even worse one! It sounds like something that you should not be investing in.....
Identify the type and size of alternator you have exactly and go look......or sell it and buy new/secondhand.....
Good Answers: 27
05/02/2014 8:27 AM
To replace the damaged transistor with another type and expect it to work properly will require some circuit redesigning changes! You will need to alter and change the biasing conditions, which may also require changing the device's driver stage and input signal characteristics!
It is very possible your initial problem was triggered by overheating. It is very common to find the cause was due to the dried out condition under the power transistor and its mounting heatsink that triggered thermal runaway! In this case, I would suggest that whichever route you decide to take, the replacement device, insulator, and heatsink must have enough ample THERMAL COMPOUND between them for effective and maximum heat transfer!
vsar
05/02/2014 10:53 AM
It simply requires the silicon be biased correctly. Germaniums have approximately 0.2V from emitter to base, where silicon has approximately 0.7V, so typically you increase the resistor value from the base to the supply. But do you know how it is biased? Do you have a schematic showing the voltage on the collector? Since it is bad now, you can't measure it.
05/02/2014 1:56 PM
Yes, there is a schematic at the unit but without values. I will see the values of the resistors at the actual module and let you know. I intend to try the MJ15004, I saw the specs and have ordered it and think it can't damage anything...if it does not saturate-no worries-no excitement-no output voltage. This would be my first step, simple swap. The second would be to change the value of the base resistor and see if that opens the transistor and initiate the excitement.
Good Answers: 27
05/02/2014 2:28 PM
Your picked of MJ15004 is an audio power device and comes in a different package type which is not compatible with the original 2N174N packaging! Since it is of different package, the terminals and physical layout will also be different! So be aware of the electrical as well as the physical differences!
Good luck!
vsar
05/02/2014 3:41 PM
GA
I have been known to forget that too......
05/02/2014 6:24 PM
Good note
I just drilled two new holes at the module and hooked the MJ15004, it is easy to follow terminals since there is a schematic at the actual board. I was told by local radio technician to add one resistor in serial before the base, approximately between 50 and 80 Ohms...should I? Sounds logical to me to bias the silicon transistor down since is more sensitive than the original one??
thank you for helping me
Good Answers: 27
05/02/2014 7:29 PM
Normally the main body of the device serves as the collector terminal and and typically they are considered hot, not insulated. Be sure to insert a plastic or Mylar insulation between the device and the aluminum heatsink! I don't see the schematic and therefore can't tell if logical or not? I don't know what you mean about being more sensitive than the other? I guess it will be a learning process for you! Good luck!
vsar
05/04/2014 2:45 PM
Ok, this is the schematic of the module. The value of the R12 (the base resistor at the transistor V3-2N174A) is 3.9KOhms.
As I said before, I was told to add 50-100 Ohm in serial to the factory base resistor if I use MJ15004. I put a small adjustable 100 Ohm and intend to experiment and see how it works with a different values.
I also add a heat sink and of course, I electrically separated the collector from the chassis (Mylar insulator). This is how it looks, ready to try, hope won't fry :)
Any other thought before I put it in a slot and start the engine
regards
Mishel
05/04/2014 7:28 PM
Considering it's an emitter follower in a darlington arrangement, I would not change anything. It should work as long as all other parts are good. The bias is controlled by V1. I hope you tested V1 and V2.
05/05/2014 4:00 AM
Yes, I have tested all the diodes and transistors at the board (disconnected) and they are all OK. I am going to bypass the resistor now and test it tomorrow how it works.
Thank you
Mishel
05/12/2014 5:56 PM
Hi everyone,
I tested the generator during the weekend and I am confused with the results. Now, without any load connected at all, the generator instrument shows 10A of current, the output voltage rises slowly (by itself) up to a point where the automatic circuit for protection shuts it off. And that is it! I turn off the engine, start again - the same story repeats, the voltage rises slowly, (it takes aprox 5 seconds to reach the 250 VAC) and at that point the protection shuts off the excitation. The generator runs nicely with the manual excitation. It runs properly both manual and automatic at 12 VDC. I noticed that the resistor that I had to change (the original was burned) is hot. I did not connect any load or did anything else.
I know it's maybe close to be "off-topic" but any suggestion would be highly appreciated. I pulled out the module with the avr and check the output transistor (MJ15004) and it is ok. I am going to re-check other active components and try to figure up what draws those 10A
thanks for reading
Mishel
Good Answers: 88
05/13/2014 5:52 AM
A seriously leaking C1, dried-up C3 if I can see well on the scematic, leaking junctions on the other transistors, zener V7 or burned R15 could be the fault. System IS made to have slow response, so don't worry about its timing, only for driving to protection at no load. I assume that with some loading, this does not happen. About the 10A, something does not fit here. Where is it measured? On 220V(!), 12V (charging a starting battery) or on exciter coil? If on exciter, It's propubly already half-burned. S.M.
05/13/2014 6:46 AM
how can this be "over rated"?? :)
10Amps showed at the main ampermeter at the generator at 220V AC. I will check all the things you mentioned and will inform you.
thank you so much
Mishel
Good Answers: 88
05/13/2014 4:16 PM
10A on 220V AC is 2.2 KVA(!). Real power or complex, what kind of no-load is that? No way. Your ammeter's (possibly its internal shunt resistor) is dying/dead/zombie. S.M.
05/14/2014 4:56 AM
well, I don't know the reason but it happened twice in a row. I did not want to go any further before I check the MJ15004. I hope it's just the instrument. I am going to the local shop and see if they have new capacitors on stock.
regards
Mishel
05/17/2014 4:46 PM
need assistance (again)
Zener V7 is OK, R15 is OK, will recheck all the junctions as you advised. The problem is with the values of C1 (8μF) and C3 (5μF)! I can't find the exact values anywhere.
Can I put 10μF for C1 and 4.7μF for C3? The voltage is 40V for both.
thank you
Mishel
Good Answers: 88
05/17/2014 7:52 PM
Absolute values are not critical, caps filter the rectified AC to be used as negative feedback when it goes over the zener preset level, also determine the system time response that MUST be slow. Just use higher voltage and temp rating caps. But forget all that untill you troubleshoot and get an explanation of the high "no-load" current you see, else it will be useless. Check for example for rusty grounding points on the gen. Not wize trying to fix possible multiple faults at random order. It will be more difficult, expensive and take longer. S.M.
05/18/2014 4:47 AM
Will do all these in a week. I shall be away and the genset is at the cottage while the module is here at home. Hopefully will find the cause ,
Thanks a lot!!
Mishel