Dual Solenoid Valve for Reliability?

05/06/2014 6:56 AM

What is the best pneumatic configuration for two pilot operated 3/2 way solenoid valve to be used for on-off of a ball type quarter turn shutdown valve.

There are two outputs from the same logic carrying same valve driving each of the solenoid valve.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Dual Solenoid Valve for Reliability?

05/06/2014 6:25 PM

Explain what you want to a valve company.Go here and search: Search GlobalSpec
Or ask one of these:

ASCO Valve | ASCO RedHat Solenoid Valves | World's Leading ...
STC Solenoid Valves - StcValve.com
Be ready to explain in clearer terms than these.

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#2

Re: Dual Solenoid Valve for Reliability?

05/06/2014 10:44 PM

Contact Parker (Parker-Hannifin) http://www.parker.com/portal/site/PARKER/menuitem.223a4a3cce02eb6315731910237ad1ca/?vgnextoid=c00aeea74775e210VgnVCM10000048021dacRCRD&vgnextfmt=default&vgnextfmt=EN

They have a very extensive line of pneumatic valves, fittings and other devices. I have had extreme success in years past. They, at one time, also had the best set of training books in the pneumatics fields. Now they have on-line training.

Many people, including myself, used to make process control pneumatic computers for chemical processing before the IBM and Apple became popular. They were great for explosion proof areas. They could do most things that a PC could and many things they couldn't do. One of the best things about them is that pneumatics can do many things that electrical units require interfaces for.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Power-User

Join Date: Dec 2008
Location: Australia
Posts: 143
Good Answers: 24
#3

Re: Dual Solenoid Valve for Reliability?

05/06/2014 11:05 PM

Hi, I'm not sure if this will help.

In my experience a 3/2 solenoid takes a single pneumatic input, and has 2 pneumatic outputs. It takes a single digital on/off signal.

When the solenoid is signaled to open it will direct air supply to one of the outputs (which can be used to move a single acting actuator on a valve). When the solenoid signal is removed, the solenoid internal spring forces the input closed, and the previously pressurised output is vented through the second output.

When pressure is removed from single acting actuator, the actuator spring pack moves the valve to its fail position. In case of either power failure or air failure, a single acting actuator will cause valve to fail to the set position based on spring pack within the actuator.

If you have double acting actuator (i.e. requires air to open & air to close), then you either need 2 x 3/2 solenoids or 1 x 5/2 solenoid.

A 5/2 solenoid will direct a single pneumatic input to one of two pneumatic outputs (one is directed to each side of the actuator, so when the solenoid is switched using a single digital signal, it will either open or close depending on how it is configured).

A double acting actuator (on electrical fault) will fail to the spring position in the solenoid. But on air failure will fail to last position.

Hope this helps.

Anthony

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Dual Solenoid Valve for Reliability?

05/06/2014 11:08 PM

All the more reason for the OP to seek professional help instead of asking strangers on an anonymous forum for help to do his job.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Dual Solenoid Valve for Reliability?

05/07/2014 5:54 AM

<...There are two outputs from the same logic carrying same valve driving each of the solenoid valve....>

Therein lies the rub. Are those outputs logical OR with a spring return, logical AND with a spring return, or air-each-way? Valve suppliers' sales offices need to know...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ajwinemaker (1); lyn (2); old salt (1); PWSlack (1)

Previous in Forum: RS232 Data Transmission Problem   Next in Forum: Question About Transmitter Connection

Advertisement