Conductor Size Required for Transformer, Generator for Frame Earthing

05/11/2014 2:10 PM

What is the required conductor( frame to earth electrode) size for transformer, generator frame earthing with reference standard?

__________________
Fakrul
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Conductor size required for transformer, generator for frame earthing

05/11/2014 3:06 PM

According to the codes and standards in effect where this is being installed. With the complete lack of information in your post, no other answer is possible.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Member

Join Date: Mar 2010
Location: Dhaka,Bangladesh
Posts: 9
#5
In reply to #1

Re: Conductor size required for transformer, generator for frame earthing

05/12/2014 9:41 AM

Thanks for your response. Please consider it for BS/IEC/NFPA.

__________________
Fakrul
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Conductor size required for transformer, generator for frame earthing

05/11/2014 3:11 PM

Impossible to answer, except to say, the correct one per local and national codes.

Do a search; here's one:

IS SP 30: National Electrical Code : Bureau of Indian ...

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/11/2014 10:29 PM

It is about this big.

If you really don't wish to duplicate this type of wiring then you should understand your circuitry a little better than what you've told us and consult with the wiring authority for this installation.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/12/2014 3:53 AM

British Standard 7671 gives full protocols for cable sizing, as has been repeated in this forum on countless previous occasions.

Reported as a possible duplicate thread.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#6

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/12/2014 10:05 AM

What is the fault current at the transformer, generator?

Register to Reply
Member

Join Date: Mar 2010
Location: Dhaka,Bangladesh
Posts: 9
#7
In reply to #6

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/12/2014 1:19 PM

Thanks for your response.Please consider 1000 KVA, 11/.415 KV ,Dyn 11 Distribution transformer.

__________________
Fakrul
Register to Reply
Associate

Join Date: Apr 2011
Posts: 45
Good Answers: 4
#8

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/12/2014 1:59 PM

In all the power plants I have been for the last 40 years, the wire size is a minimum of 1/2 inch. I do not know what the actual wire size is. There are so many different grounds in a plant that it seems to be a standard size due to the fact that it is not load bearing. Check local codes to get the correct size.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#9

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/12/2014 6:02 PM

Do not confuse Grounding with Grounded, a common mistake.

The largest conductor going to the electrode,in the ground,is #6 Copper.

There are exceptions ,of course, to every rule, and this rule is no exception.

Per NEC,article 250.

Read and understand this section thoroughly before proceeding.(CYA)

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Associate

Join Date: Apr 2011
Posts: 45
Good Answers: 4
#10
In reply to #9

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/12/2014 8:16 PM

I did not get confused. He is grounding the FRAME and not grounding the load.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#11
In reply to #10

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/12/2014 8:36 PM

My reply was directed to the OP,not you.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Member

Join Date: Mar 2010
Location: Dhaka,Bangladesh
Posts: 9
#12
In reply to #9

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/13/2014 2:47 AM

Thanks for your response and cooperation. I need conductor size from frame to the electrode. Could you please provide me the clause no from Artical 250 of NFPA that I can check. Actually I am confused about the issue and want to make my conception clear.

__________________
Fakrul
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13
In reply to #12

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/13/2014 9:08 AM

If you're going to check on the answers given, why not look for the conductor size yourself.

You could give the size of the conductor that you've calculated and we'll tell you if you're right.

In other words "do your own work."

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#14
In reply to #12

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/13/2014 9:16 AM

As I stated,it is important that you read and understand the Article 250.

To give you a portion out of context would be dangerous.

You must understand the theory as well as the process to safely perfom electrical installations.

If you do not understand it on first pass,do some further research or experience to enlighten yourself.

The code book is not designed to be a cookbook,with recipes on "how-to-do", it is merely stating what must be done to achieve a safe installation.

There are so many variations on installations that a strong undestanding of priciples is required.

This is why many years of experience is required before a hopeful electrician can even apply for a license.

Memorizing the entire code book will not get you there.

This is not an exclusive club, to exclude others, rather all who are qualified are welcome.

General advice is all I can give you for the safety of all concerned.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#15

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/14/2014 6:40 AM

Please inform me your mail ID thro this forum's mail box so that I can send you a chart on the same.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#16

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/23/2014 1:03 AM

See also: British Standard BS 7430 Code of practice for Earthing

Ch.18-19 [mainly 19.7.2 Size.

IEEE-Std 665-1995 IEEE Guide for Generating Station Grounding

ch. 5.3 Generator and isolated phase bus grounding

__________________
Julius
Register to Reply
Member

Join Date: Mar 2010
Location: Dhaka,Bangladesh
Posts: 9
#17
In reply to #16

Re: Conductor Size Required for Transformer, Generator for Frame Earthing

05/23/2014 1:37 PM

Thanks for your response and guidence.

__________________
Fakrul
Register to Reply