Total Water Consumption for 150Mw Thermal Power Station

05/27/2014 7:12 AM

What would be the total water consumption for a 150 MW thermal power plant, with an air cooled condenser.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: total water consumption for 150Mw thermal power station.

05/27/2014 7:15 AM

Anything from not much to quite a lot depending upon how the resource were managed.

  • Where is the raw water composition analysis?
  • Where are the discharge consent limits?
  • What is the steam make-up water composition to be?
  • What is the ambient temperature and humidity?
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#2

Re: Total Water Consumption for 150Mw Thermal Power Station

05/27/2014 7:42 AM

Depends on the design, location, and maintenance of the plant. You might even find some designs where the workers consume more water than the thermal plant. If this is a fossil fuel thermal plant you could produce more water vapor from combustion than consumed by the workers.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Total Water Consumption for 150Mw Thermal Power Station

05/27/2014 9:44 AM

Steam pressure? (Low-Medium-or - high pressure? Critical? Super-critical?)

In addition to the above you are missing a lot of information that is required before anyone could venture a guess.

The amount of information will be far greater than what you could/should post in this forum.

If the plant exists you should be able to contact the design engineering firm or review the plant design DATA to find the information.

If this is a plant in development stage, you will need to contact the design team lead engineer.

If you are going to attempt to design the plant, you will need a fully staffed team of experts.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Total Water Consumption for 150Mw Thermal Power Station

05/27/2014 12:48 PM

Per hour?

Per day?

Per week?

Per month?

Per year?

Over the lifetime of the unit?

<unsubscribe>

Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#5

Re: Total Water Consumption for 150Mw Thermal Power Station

05/27/2014 3:29 PM

A lot less than with a plant using a cooling tower. But since you are air-cooling, it takes more (~16% MWthermal more to produce max load in MWe) heat (and steam) to produce that 150 MW. I am guessing your steam flow is maxed out at 600,000.

With 3% losses incidental (packing, valves, glands, small leaks, etc.) you need a 32 gpm water system. With a 6 hour warm-up/start-up at 10% steam rate (vented), you need a lot more (43, 165 gallons/start by WAG method). You should allow your unit only one full startup per day, but add another 15,000 gallons loss during shut-down for any venting that must take place. Now are looking at a grand total daily to operate of 104,245 gallons/day (73 gpm). So you opt for a 100 gpm water treatment system to purify make-up condensate, and install a minimum tank size of ~3x daily use of 1 acre foot (1233 m3).

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#7
In reply to #5

Re: Total Water Consumption for 150Mw Thermal Power Station

05/29/2014 9:45 AM

It is rare that I reply to my own post, but I must admit an error was made in my assumption about the OP's plant. I had stated a maximum steam flow of 600,000. That might be close for a 60 MWe plant. Correct value is nearer to 1,500,000 lbs/hr steam flow. This will necessarily upgrade the size of water treament equipment to around 250 gpm, along with a needed increase in size of condensate storage tanks, to cover start-ups and shut-downs, to a minimum of 3000 m3 (~1MMgallon).

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Participant

Join Date: May 2014
Posts: 4
#6

Re: Total Water Consumption for 150Mw Thermal Power Station

05/28/2014 11:31 AM

For air cooled condenser in 150 MW power plant, water is required for compressors and vacuum system apart from boiler. Water required for steam generation depends on efficiency of boilers. As a thumb rule for compressors and vacuum system, one requires 15 m3/h make up water in standard cooling towers with < 0.1% drift losses. Hope this is okay.

Vikram Shah

Expert- water treatment, recycle and water conservation

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Total Water Consumption for 150Mw Thermal Power Station

06/01/2014 11:45 PM

James,

No need to guess, a study by the Central Electricity Authority (CEA), New Delhi concluded that a dry air condenser system would reduce water consumption to 1/5 to 1/6th that of a "normal" water cooled system, from 3.0 to 0.55 M³/Hr/MW, based on a study of 2x500MW plants; or from 450M³/Hr down to 82.5M³/Hr.

They also concluded that the "hits" that efficiency and heat rate take (approx. 7%) made this only viable when the plant was located in an area with very scarce available water resources.

RAM

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#9
In reply to #8

Re: Total Water Consumption for 150Mw Thermal Power Station

06/02/2014 9:34 AM

Yes, thanks, I was just throwing out some WAG numbers without doing a lot of research on it, sorry. Still seems like a lot, and there will be large variations depending on start-up frequency, reliability,etc.

__________________
If it ain't broke, don't fix it. Just build a better one.