Abnormal humming sound from Transformer

06/25/2007 4:19 AM

Dear Sirs,

We have 500 KVA transformer for our construction power supply , which is giving abnormal humming sound when it is on "no load" when it is loaded about 15 kva load then the humming sound slightly subsides

What could be the probable cause for it?

We have conducted magnetic balance test also we could not find any considerable inferences out of it

Dear friends kindly give me your valuable suggestions on this matter

Regards

R.THIRUNAVUKKARASU

__________________
R.THIRUNAVUKKARASU
Register to Reply
Pathfinder Tags: TRANSFORMER HUMMING SOUND
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Jun 2007
Posts: 64
Good Answers: 3
#1

Re: Abnormal humming sound from Transformer

06/25/2007 7:45 PM

* Hum is mechanical and is caused by the alternating current shaking the steel laminations. Magnetostriction plays a roll in this. Generally, well designed and built transformers are solid enough so that there will be no audible hum. However, this can vary widely for individual units of the same design. Vacuum impregnation of resin varnish glues the whole core into one big block. If this is not complete, mechanical hum can result.

* If there is DC on the line, this can cause the core to saturate on one half cycle and cause hum. This can be caused by asymmetrical waveforms due to equipment with solid state switching devices. For a large transformer such as the one you have, this is unlikely to be a large enough effect, but you should check the waveform to rule it out.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Abnormal humming sound from Transformer

06/26/2007 12:26 AM

I'm no engineer but I deal with rather large Pad mount utility transformers on a daily basis it seam to me that we have had this problem before and it was either a matter of Single phasing or(blown Bayonet fuse) or a low oil coolant level in the transformer caused by a bad seal IE. Bayonet fuse seal -over pressured blown and then the oil leaked out allowing the tranformer to hum . I could be quite wrong however this is simply a laymans view of your problem , Hope this was helpful for you

Kelly R. Bartholomew

Register to Reply
Active Contributor
Engineering Fields - Electrical Engineering - New Member United States - Member - New Member

Join Date: Jul 2007
Posts: 15
#6
In reply to #1

Re: Abnormal humming sound from Transformer

08/22/2007 11:15 AM

To go along with the above. It is definitely a saturated core. 500kVa? The more material used in the transformer, the more room for mistakes, however small, they can add up quickly. Testing distribution transformers, I have found that the amount of HUM depends upon the quality of work done by production personnel. I'd make for certain that the 500kVa, is a 500kVa. I have seen multiple cases after having opened a transformer...that the 500kVa, was not...

With the saturated core, you are going to have to worry about considerable losses.

__________________
Justin
Register to Reply
Anonymous Poster
#3

Re: Abnormal humming sound from Transformer

06/30/2007 12:39 AM

I noticed that the newer Power transformers for 10KVA upward and even smaller ones such as in a microwave hum a lot more than they used to, 30-50 years ago. I believe the reasons are; as follows:

Changes in lamination metallurgy allowing the use of smaller cores. The smaller laminations carry much more intense fields.

Changes in construction,.. rather than being bolted together with insulated (from the core) bolts (the old fashioned way). They are welded along the edges in several strips which provide paths for eddy currents.

When loaded the transformer becomes more of a resistive loan ( power factor of 1). so the forces in the core are more uniform, the eddy currents are in step with the magnetic fields and cancel. When unloaded the transformer is much more of an inductive load meaning the field strength is maximum when there is no current,... if a capacitor is used for phase shift such as for mercury lamps, operating off a single phase supply, this means that the two phases are much less evenly distributed so that the collapsing magnetic fields react more strongly to the eddy currents which are higher because of the different core material, and smaller size and the welds accross the laminations. Also the power waveforms of the AC (from the power company) may be more flattened on top, and bottom due to all the clipping from surge protectors which result in differential spikes being created by the unloaded, inductive transformers.

Lots of new high powered Transformers buzz like the Dickens,especially unloaded, I believe these are the reasons.

Geoffrey Reed

Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#4

Re: Abnormal humming sound from Transformer

07/01/2007 1:37 AM

Not a hands on electrician, but checking on the internet under Electrical resonance transformer noise comes up with some answers that might help?

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#5

Re: Abnormal humming sound from Transformer

08/22/2007 10:37 AM

It is normal for a unloaded transformer to hum more than a loaded one. Check you load ( in amps) and the dB (hum) level you will notice a marked change in humming level when the load (amps) goes up.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Associate

Join Date: Jul 2010
Posts: 32
#7

Re: Abnormal humming sound from Transformer

12/07/2010 3:40 AM

Hope the data in this link will clear your doubt. http://www.federalpacific.com/literature/drytrans/10transformernoise.pdf

Register to Reply
Anonymous Poster #1
#8

Re: Abnormal humming sound from Transformer

12/20/2022 7:24 AM