Cable Sizing for Motor Feeder

06/03/2014 2:14 AM

hi,
I have some doubts for cable sizing for Motor Feeders. in the cable sizing formulas we multiply by length and divide by number of RUN.
CASE: 22 kW. 3-ph, motor located at 125 mtr from the MCC Panel.
1. what length should I consider if it is DOL starter controlled LTMotor?
2. what length should I consider if it is star Delta starter controlled LTMotor?
And if possible please provide the Reference IEC/IEEE/IS/BIS where these formulas and the solution of above two doubts are available?
I've searched IEEE 141, but only voltage drop formula is available but nothing mentioned about the DOL/Star-delta motor feeder voltage drop.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: cable sizing for Motor Feeder

06/03/2014 3:15 AM

So, what is wrong with using the applicable national electrical standard, such as British Standard 7671?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#2

Re: Cable Sizing for Motor Feeder

06/03/2014 11:11 AM

1 and 2. Why should starter / controller selection change the LENGTH 125 mtr ?

Please clarify.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3
In reply to #2

Re: Cable Sizing for Motor Feeder

06/03/2014 5:01 PM

Good question!

__________________
Good moaning!
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#4

Re: Cable Sizing for Motor Feeder

06/04/2014 12:28 AM

The very first thing is once located - distance between starter and motor will remain fixed (will not change) unless either starter or motor are re-sited. Regarding cables you need calculate resistance and drop of voltage in the cable due to distance and size of cable and if this is more than 10% (Some standards allow up to 15%), better go for a higher size of the cable to reduce resistance.See that voltage regulation permitted by local law is not fouled. One good idea is to use copper cables but it will cost high and at some locations law may not permit it. Consider these aspects and decide cable size and not the length , which remains fixed once located, notwithstanding the size of motor and type of starers you use.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Cable Sizing for Motor Feeder

06/04/2014 6:01 AM

Refer EC&M website

__________________
pnaban
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6

Re: Cable Sizing for Motor Feeder

06/05/2014 12:58 AM

A DOL-started motor can take a starting inrush of 6 to 8 times the rated full-load current. Star Delta staring will be 1/3 of that. This inrush current will have some bearing on the cable sizing, whatever the source of information.

Reputed controlgear manufacturers give complete details of all equipment required for starters (contactors, relays, SCPDs, and cables) based on motor rating. You can refer to any catalogue for that.

If the control cables are also very long, you may want to check the effect of (a) voltage drop due to cable impedance and (b) non-switching-off by the stop button due to cable capacitance. There are excellent papers about this on the web. However, since you mention MCC and the motor being far away, this may not be a factor.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Cable Sizing for Motor Feeder

06/07/2014 4:03 AM

As M.R.Iyengar already said, the cable length stays unchanged. What, I think, you meant it is: if the voltage drop has to be calculated -or limited- for DOL start or Star/Delta .The current at star connection will be 1/3[ as kvsridhar already said], but the torque will decrease in the same proportion. If it is an usually motor Design B as per NEMA MG-1 or Design N as per IEC 60034-12 at rated voltage the minimum starting torque will be 1.3 [NEMA MG-1 Table 12-2 for 30 hp [22 kw] 2 poles, IEC 60034-12 Table 1- 2 poles for 16<Pn<25 kW], then in star starting case Tlock=1.3/3=0.43*Trated.

If the voltage drop -from the rated- will be 10% then Tlock=0.9^2*0.43=0.348*Trated.

Now, it depends on the required load starting torque. A pump or a ventilator could manage the case, but a lift or other constant torque installation could not.

__________________
Julius
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#8
In reply to #7

Re: Cable Sizing for Motor Feeder

06/07/2014 7:12 AM

I am in agreement with 7anoter4 & kvsridhar regarding the current to be taken for calculations of the drop of voltage. Besides If the largest available cable size ( may be with the user or in the vicinity market or the one motor terminal box can accommodate doesn't sort out the issue then comes the questions of multiple runs. This while takes care of current handling also reduces resistance because of parallel runs. But one must consider the connecting the cable into the motor terminal box. The Glands size may have to be considered.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Crabtree (1); kvsridhar (1); LongintheTooth (1); M.R.Iyengar (2); pnaban (1); PWSlack (1)

Previous in Forum: Test Procedure   Next in Forum: C to Matlab

Advertisement