LV Bus Bars For Switchboard

06/11/2014 1:16 AM

I need to specify bus bars in a switchboard for LV. The design current is 200 A. I read somewhere that the short circuit rating for up to 400A should be 25 kA for 1 sec. What should be the rated current? 2x200 = 400A?

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#1

Re: LV Bus Bars for Switchboard

06/11/2014 2:42 AM

suggest you don't specify these bars. Without an understanding of the supply to the board, without an understanding of the protection serving the board, without knowing the cables supplying the board and without knowing you need to know these my suggestion is hand this job over. It will make sense in the long run and save on fire extinguishers.

Register to Reply Good Answer (Score 2)
Associate

Join Date: Mar 2012
Posts: 48
#2
In reply to #1

Re: LV Bus Bars for Switchboard

06/11/2014 2:52 AM

Please note that all the factors which you are stating are known and have been taken into consideartion before the question was asked

Register to Reply Score 2 for Off Topic
2
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#3

Re: LV Bus Bars for Switchboard

06/11/2014 4:36 AM

at only 200A do you even need a fault rated board?

25kA at 1 sec is a typical type of spec for a switchboard usually hung off the end of a 1MVA transformer. You make no mention of the transformer, where the board is fed from. What is the PSCC at the board? Without this sort information you can't begin to get to the right answer.

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Mar 2014
Posts: 75
#4
In reply to #3

Re: LV Bus Bars for Switchboard

06/11/2014 12:50 PM

Only typical. Not always.

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#8
In reply to #4

Re: LV Bus Bars for Switchboard

06/13/2014 2:33 AM

Typical - depends whether there are current limiting fuses - there might be a huge run of cable reducing the fault, it migt be close coupled. Like I said typical only but in the right ball game. There are lots of variables that must be taken into account and we have been given none of them to play with. I'm thinking our original poster is really looking for an LV panelboard - 8 way TP&N type of thing with a 200A incomer.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: LV Bus Bars For Switchboard

06/11/2014 11:11 PM

consider the fault/short circuit level at the switchboard

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Feb 2014
Posts: 10
#6

Re: LV Bus Bars For Switchboard

06/12/2014 1:13 AM

Regarding bus bar size only:- you need to specify actual current drawn by panel. i.e. in panel rating, design ambient temperature, material of bus bar and its density and Fault level at bus bar.

based on that vendor shall give you final size / cross sectional area of bus bar with considering de rating factor of temp. and other factors.

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#7

Re: LV Bus Bars For Switchboard

06/12/2014 4:57 AM

I don't know.

Register to Reply
Commentator

Join Date: Mar 2014
Posts: 75
#9

Re: LV Bus Bars For Switchboard

06/13/2014 4:22 AM

Where did you read that?

Register to Reply
Associate

Join Date: Mar 2014
Location: Mumbai, India
Posts: 25
#10

Re: LV Bus Bars For Switchboard

07/30/2014 8:42 AM

Unless fault level at this switchboard is known, there is no point in specifying what kA for what time level (0.5, 1, 3 s). Better do fault level calculation upto the point specified.

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

beentheredonethat (1); Blackpaper (2); DHARAMRAJSINH (1); Jignesh Shah (1); Mohamed Akram Khan (1); pnaban (1); silverfox (3)

Previous in Forum: Solar Energy   Next in Forum: Technical Consultant

Advertisement