Dear All,
We need to test and Install Tariff Energy Meters for our 132 kV substation for a CT ratio of 400/1 and VT ratio of 132/Rt3 / 110/Rt 3/110/Rt3. When I reviewed routine Test certificate given by the manufacturer, the Full load current error was found to be 0.08. i.e for a 1 Amps.
But during acceptance testing, The Meter indication showed only 0.9 Amps for a current injection of 1 Amps from Omicron kit. My doubt is with an error of 0.08, the Meter indication should have been 0.92 . i.e the meter should have indicated atleast 2 digits after the decimal point. Since it is a tariff meter, The exact value of CT secondary is very critical. Similarly PT value indicated 63.5 V. PF stood at 1.00 (unity). On asking the Factory personal who imported the Meter from overseas, we were told that Ampere reading is always shown in single digit after decimal and PF is unity because it is injected from Omicron kit. Is it the correct way of indication of meter used for tariff purpose. Kindly help me out. Please let me know if any further information is required.