Dear All,
Why don't we conduct Impulse test on LV system? When we were testing 415 V Transformer or 415 V Switchgear, we conducted only 2kV Power Frequency test, why not an Impulse test?
"Engineering is Passion"
Good Answers: 445
Re: Impulse Test on LV system
06/19/2014 11:22 PM
Because what's the probability that a sharp rise time steep front impulse wave similar to lightning is going to reach your low voltage equipment after it's traveled from the transmission line, past a lightning arrester or two, through a few transformers, past a surge arrester or two, and into your switchgear without having a lot of the energy taken out of it?
06/20/2014 1:52 AM
Dear Sir,
Thanks for that update.
06/20/2014 7:15 AM
...and because it doesn't say "carry this out" in the equipment Standard Test Procedure.
Good Answers: 11
06/20/2014 10:12 AM
It is still only an option in the latest standard for LV switchgear (IEC 61439-1:2011), not mandatory i.e. alternative methods can still be used which are usually cheaper.
It was always considered a type test rather than routine, but is very useful in searching out hidden mistakes or degraded insulation. Not always easy to perform other than in workshop/lab conditions.
rogerggbr
06/20/2014 12:49 PM
Dear All,
I am really thankful to all the people who replied to my question. I got an idea about this aspect now. Thanks.
06/20/2014 1:07 PM
Dear All,
Thanks for all your clarification.