Why don't we conduct Impulse test on LV system? When we were testing 415 V Transformer or 415 V Switchgear, we conducted only 2kV Power Frequency test, why not an Impulse test?

__________________
"Engineering is Passion"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Impulse Test on LV system

06/19/2014 11:22 PM

Because what's the probability that a sharp rise time steep front impulse wave similar to lightning is going to reach your low voltage equipment after it's traveled from the transmission line, past a lightning arrester or two, through a few transformers, past a surge arrester or two, and into your switchgear without having a lot of the energy taken out of it?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#2
In reply to #1

Re: Impulse Test on LV system

06/20/2014 1:52 AM

Dear Sir,

Thanks for that update.

__________________
"Engineering is Passion"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Impulse Test on LV system

06/20/2014 7:15 AM

...and because it doesn't say "carry this out" in the equipment Standard Test Procedure.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#4

Re: Impulse Test on LV system

06/20/2014 10:12 AM

It is still only an option in the latest standard for LV switchgear (IEC 61439-1:2011), not mandatory i.e. alternative methods can still be used which are usually cheaper.

It was always considered a type test rather than routine, but is very useful in searching out hidden mistakes or degraded insulation. Not always easy to perform other than in workshop/lab conditions.

__________________
rogerggbr
Register to Reply
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#5
In reply to #4

Re: Impulse Test on LV system

06/20/2014 12:49 PM

Dear All,

I am really thankful to all the people who replied to my question. I got an idea about this aspect now. Thanks.

__________________
"Engineering is Passion"
Register to Reply
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#6
In reply to #4

Re: Impulse Test on LV system

06/20/2014 1:07 PM

Dear All,

Thanks for all your clarification.

__________________
"Engineering is Passion"
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (1); Raghavendran R (3); RAMConsult (1); rogerggbr (1)

Previous in Forum: Over Voltage Protection Pickup on an Isolated System   Next in Forum: Maximum Voltage Drop in Cable Size for Transformer Feeder

Advertisement