Maximum Voltage Drop in Cable Size for Transformer Feeder

06/19/2014 11:25 PM

What Shall Be the Maximum Permissible Voltage Drop for sizing the incoming cable of the Any transformer ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: Maximum Voltage Drop in cable size for Transformer feeder

06/19/2014 11:53 PM

8%? What do you think it is?

Where is your location?

Why is it important to you? Is there a possibilty of people getting hurt?

What is the code telling you?

Internet search came up with 8% on a quick glance!

__________________
Common Sense Dictates
Register to Reply
Participant

Join Date: Jun 2014
Posts: 2
#2

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 12:29 AM

I need to calculate the cable size based on voltage drop for Primary side of transformer.

The location of the Transformer is transformer yard of indoor substation.

I think the voltage drop shall be maximum 5 % of source voltage .

can u tell me the reason for 8% voltage drop & any reference ?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #2

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 7:25 AM

Then get out a copy of the local standard, such as British Standard 7671 for UK, Eire and Singapore installations, and stop wasting time on CR4.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 2 for Off Topic
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#7
In reply to #6

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 7:45 AM

On the primary side of the transformer Mr Slack. For once I don't think you can quote the IEE regs. Is that kettle still on??

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#11
In reply to #6

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/21/2014 10:07 AM

You'll not find it in BS7671 Mr. Slack.

http://www.eon-uk.com/downloads/network_design_manual.pdf

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#3

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 1:42 AM

The Voltage Drop shall be limited to 3% of the rated voltage as per IS 7098 (Part II), IEC-502.

__________________
"Engineering is Passion"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#4

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 6:49 AM

Like many questions on here we don't really have enough information to give you an answer.

The answers so far seem to assume your primary is LV i.e. less than 1000V.

I'm thinking your primary is more likely HV in which case volt drop is the least of your worries. You need to be looking to the fault current a cable will withstand and how it is protected. Totally different approach.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#5
In reply to #4

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 7:15 AM

Sir, I believe that the maximum voltage drop acceptable shall be 3% during running condition and shall be limited to 15% during starting. We calculated using IS 7098 or IEC 502, Although cable shall be sized to withstand Fault level of 50kA for LT system (in our case), considering the Cable Derating factors and the above criteria.

__________________
"Engineering is Passion"
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#8
In reply to #4

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 8:33 AM

I agree, but I'm not qualified to answer. OP said "any transformer". I think cable sizing for transmission transformer, where tap changer is available, would be different from sizing for LV usage.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13
In reply to #8

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/22/2014 12:06 AM

That would involve an On Load Tap Changer, not a cheap piece of kit and not really economical for a smallish transformer. The OP also mentioned starting loads, an OLTC doesn't react that quickly. (Not the ones I've had dealings with anyway.)

It would help if the OP could give an indication of the size of the transformer.

Another consideration is available cable sizes. Recently I was costing the installation of a 11/.433KV transformer. I could have got away with a 35mm XLPE cable, 95mm is more readily available and worked out cheaper.

The way the original question is worded I get the feeling we are doing someone's homework.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#14
In reply to #13

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/22/2014 1:44 PM

I was agreeing with silverfox that, as is too often the case, too little information was given. OP said 'all transformers' which, even this dumb old ME knows, encompasses a w-i-d-e variety. (BTW, I don't think OP mentioned starting loads. As usually happens when too little info is given, folks started making assumptions and others kept following that rabbit. )

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 1:01 PM

For medium voltage or high-voltage cable no voltage drop is to be considered. You have to check the short-circuit withstanding and the ampacity for the maximum circuit conditions. The limits are the maximum permissible temperature-for long time loading 70 [pvc] 90 [EPR, XLPE] for short-time 130 [pvc] 250[EPR, XLPE].Of course, the connected with apparatus maximum allowable temperature has to be considered. At a low voltage system you may consider the total voltage drop -income cable-transformer-outgoing cables-up to motor terminals in steady state load and in starting conditions.

__________________
Julius
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#10

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/20/2014 4:44 PM

Is this a homework question? If your wondering about allowable voltage drop on any transformer and your working in the field, please let us know your location! I will make sure to stay miles away from you and your craftsmanship or work.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12

Re: Maximum Voltage Drop in Cable Size for Transformer Feeder

06/21/2014 11:03 AM

If a large induction motor is to be started-namely D.O.L.-the voltage drop has to be carefully checked. However, in my opinion, most of the voltage drop will be in transformer and in low-voltage cable. See [for instance]:

http://www.idc-online.com/conferences/PAPERMichaelHamilton.pdf

__________________
Julius
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); betikabap (1); bigg (2); dj95401 (1); IdeaSmith (1); PWSlack (1); Raghavendran R (2); silverfox (2); TonyS (2)

Previous in Forum: Impulse Test on LV system   Next in Forum: Relay Coordination

Advertisement