s811 Eaton Soft Start

06/24/2014 4:45 PM

What kind of life expectancy should I see on an eaton s811 720 amp starter? Ours are started and run 24/7 for one month at a time and then are rotated to the next unit. Average amperage is 450 amps consistantly. Ours are about six years old.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#1

Re: s811 eaton soft start

06/24/2014 5:21 PM

That information is the specifications section of the manual under the heading MTBF (Mean Time Between Failures). Third listing down is the manual from Eaton.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: s811 eaton soft start

06/24/2014 5:22 PM

You will have to talk to Eaton about this (if the information available in the manual, datasheets, etc does not have it), they should be able to advise you.

__________________
jack of all trades
Register to Reply
Anonymous Poster #1
#3

Re: s811 Eaton Soft Start

06/24/2014 7:40 PM

From my experience you are lucky, but most likely because your duty cycle is very very low.

They have no heat sinks to speak of for the SCRs, they just clamp them in the bus bars. I found, after hooking one up to a scope, that if you set the ramp time for maximum 45 seconds and connect to a heavy load (mine was a rock crusher), the light on the front will blink once per second, 45 times, telling you that it is "ramping". But at 17 seconds, the integral bypass contacts had already closed because the SCRs were over heating already. The starter has a thermal sensor that will override the ramp settings to try to save them by going across-the-line early.

The trick they use is that the bypass contactors (separate for each pole) use the old Westinghouse "Advantage" solid state DC ramped coil control , so the contacts close very very quietly and people don't realize it has happened. But it is no longer ramping and if the motor was not at >80% when that happens, the current surges to almost LRC anyway, which makes the soft starter pointless.

I thing that CH IT starter is the biggest POS on the market, bar none.

Register to Reply
Participant

Join Date: May 2011
Posts: 3
#4
In reply to #3

Re: s811 Eaton Soft Start

06/25/2014 9:42 AM

Thank you for your input. It is hard to get honest opinion sometimes and I appritiate yours.