Transformer Power Rating

06/24/2014 9:13 PM

Hi guys,

I have a transformer connecting to 240V (RMS) single phase, stepping down to 28V RMS, The load current is 6 A.

Just trying to calculate the power rating for the transformer. My thought are:

P = VI = 28*6 = 168W

Do I need to include power factor in since transformer power rating is in VA?

If so, assuming power factor is 0.8, power rating would be 168/0.8 = 210VA

Would be great if you can share your thought and confirm my result for me.

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Transformer power rating

06/24/2014 10:16 PM

What sort of load is it: inductive, resistive, capacitive? You are thinking in the right direction, but just need some detail to tell what the likely power factor actually is.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: May 2014
Posts: 19
#3
In reply to #1

Re: Transformer power rating

06/24/2014 10:29 PM

The output of the transformer goes into a rectifier plus couple of capacitors and used as DC power supply for other systems. So I have no idea how to work out power factor from that. Guessing it's resistive/capacitive?

For Safety reasons, I am thinking of choosing transformer power rating of 220 to 250VA. You reckon that would be over estimated bit too much?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Transformer power rating

06/24/2014 10:40 PM

Sounds reasonable. If the transformer isn't fully loaded, it will be slightly less efficient, and cost a bit more initially; but better safe than sorry.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#6
In reply to #3

Re: Transformer power rating

06/25/2014 11:59 PM

As a rule of thumb, if you take the average dc amps out of the rectifier and multiply that by the secondary volts rms will yield the required VA. Usually that is very close to the power you calculated already, but adding 10 to 20% never hurts. Are there intermittent loads beyond the nominal you have measured that you may need to include?

If you are trying to replace the transformer, the replacement should be about the same physical size/ weight or larger. If it is smaller you need to do some head scratching as to why.

Register to Reply
Power-User

Join Date: Jan 2009
Posts: 250
Good Answers: 7
#11
In reply to #3

Re: Transformer power rating

06/26/2014 10:54 AM

"Guessing it's resistive/capacitive?"

it's inductive (current charging the capacitors lags voltage).

brgds

Snel

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Transformer power rating

06/24/2014 10:28 PM

Yes I believe that is correct, however your efficiency might be a bit low....You can determine the efficiency by dividing the input va by the output watts....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Transformer power rating

06/25/2014 4:07 AM

Do you want the power rating or throughput? Because they are a bit different.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7

Re: Transformer Power Rating

06/26/2014 2:21 AM

What is REALLY needed is the "VA" rating of the transformer.

Remember, the VA remains the same regardless of the load.....

Your power supply may not be designed to use the maximum power that the transformer could safely deliver...for example....

With the VA, you know just what (pun intended) the transformer can/was designed to deliver....

A reasonably simple explanation can be found here:-

Why_are_transformers_rated_in_VA_instead_of_watts?

For example:-

If you take a drinking glass to the tap in the kitchen and just turn the tap partially on to fill the glass, that is not using the full potential of the tap/water supply.

Turning the tap on fully would be using it fully, (assuming that even fully on the tap does not slow the amount of water passing through it!) the amount of water delivered would now be constricted only by the water pressure and the cross section of the pipe.....(Voltage and thickness of supply cable/wire in the transformer example! )

I hope this helps you to understand better.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#9
In reply to #7

Re: Transformer Power Rating

06/26/2014 3:13 AM

I'm off to get bigger glass. Half an hour should see me dried out again.

I understood the problem before you introduced the water. Still understand it electrically but away you go with your glass of water .......

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #9

Re: Transformer Power Rating

06/26/2014 4:46 AM

...but does the OP (TDoan)??

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Participant

Join Date: Jun 2014
Posts: 1
#8

Re: Transformer Power Rating

06/26/2014 3:00 AM

IF you multiply the rated current by the rated voltage for the same transformer side (high voltage side or low voltage side) you will get the '' VA '' which is the apparent power

Now multiply that with whatever power factor you have for the load and you will get the real power

Register to Reply Score 1 for Good Answer
Register to Reply 11 comments

"Almost" Good Answers: