NGR Vs Dedicated Solid Earthing

06/25/2014 1:16 AM

My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: NGR Vs dedicated Solid earthing

06/25/2014 1:33 AM

With NGR you most likely refer to a Neutral Ground Resistor.

If you do an internet research you will find lots of good information to read and comprehend. After you have done so you might be able to write that comparison on the fly. Without the proper knowledge you will get stuck in your sentences and fail your customer.

I am of the opinion the customer is always right, so why even opposing them?

__________________
Common Sense Dictates
Register to Reply
Participant

Join Date: Jun 2014
Posts: 3
#2
In reply to #1

Re: NGR Vs dedicated Solid earthing

06/25/2014 2:00 AM

Dear @IdeaSmith

As i am trying to search though internet but always it looks that I should install NGR (neutral ground resistor) for transformer.

But due to space limitation and price variations we are not going to provide. So i need back up to prove my statics. Plz help out

Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#3
In reply to #2

Re: NGR Vs dedicated Solid earthing

06/25/2014 2:12 AM

Sorry I can not help here. For me it sounds a bit (and forgive my frankness) you are going "cheap".

Space limitations around a transformer that usually comes with a NGR seems like an excuse and "price variations" puts you in the corner of "quoted not enough" to get the job.

You are on your own with this one!

__________________
Common Sense Dictates
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#4

Re: NGR Vs dedicated Solid earthing

06/25/2014 2:16 AM

And by the way if this is you:

A competent electrical engineer with a technical background of Power Equipment's and heavy machinery with relevant experience.

... I would stay away from this question. How much worth is your reputation for you?

__________________
Common Sense Dictates
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: NGR Vs dedicated Solid earthing

06/25/2014 4:01 AM

If Google keeps finding sites that recommend the use of NER (NGR) and none against there use then maybe it's giving you a hint.

Think along the lines of limiting earth (ground) fault currents.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Jun 2014
Posts: 3
#6
In reply to #5

Re: NGR Vs dedicated Solid earthing

06/25/2014 4:13 AM

That's why i choose this forum to Help me out. I know the benefits of NGR. But in our case we are not using and need to justify.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: NGR Vs dedicated Solid earthing

06/25/2014 7:28 AM

That's a commercial decision. CR4 is for technical matters.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#8
In reply to #7

Re: NGR Vs dedicated Solid earthing

06/25/2014 8:16 AM

Actually, this is a technical matter. The decision on solid grounding vs. resistance grounding has impacts on equipment and protection choices, as well as system operation.

For the OP's situation (medium voltage system), low-resistance grounding is a very common practice, to limit fault currents to levels that can be withstood by the electrical apparatus until the fault can be detected and cleared.

There are good resources available from several of the NGR manufacturers that explain the differences between the various grounding schemes and how/when to apply them. You can get (free) literature from the following:

Post Glover

I-Gard (formerly IPC Power Resistors)

These companies are long-time manufacturers of grounding resistors, and are respected in the industry. I would suggest that the OP contact them for technical recommendations.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #8

Re: NGR Vs dedicated Solid earthing

06/25/2014 9:09 AM

I've only worked on solid earthed 3.3KV up to 2MVA
Above that all our 3.3KV systems were via NER's.

NER's make sense to me. What doesn't make sense is designing a system and then trying to fit the circumstances to the decision.
I think someone has got things a bit back to front and is trying to dig themselves out of a hole.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#10
In reply to #9

Re: NGR Vs dedicated Solid earthing

06/25/2014 9:14 AM

I share that notion!

__________________
Common Sense Dictates
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11

Re: NGR Vs Dedicated Solid Earthing

06/25/2014 3:49 PM

If you are providing the transformer protection but are not providing a NGR then are we to assume that you are providing alternative protection for the transformer instead?

If so, detail that offer to the customer as a variation, if not tell the customer they will need to change their protection scheme to work with your offering. Either way the customer must approve the variation.

If you don't know or cannot show why your offering will meet the customers requirements then you have a problem and shouldn't have offered this solution.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#12

Re: NGR Vs Dedicated Solid Earthing

06/26/2014 7:28 AM

Grounding the neutral through Resistor and thus limiting the earth fault current to low levels (typically 300A) is worldwide practice for MV systems. IEEE Red book explains the practice saying

  • Medium Voltage systems ranging from 3kV to 15kV are basically for supplying motors and the resistance grounding of these systems ensures that no damage is done to the stator core laminations (in the event of stator earth fault).

The above can only be waived,

  • if the owner maintenance practice doesn't include repair / rewiding of motors (instead go in for outright replacement of faulty motor)
  • if the 22/3.3kV transformer rating is small and that too with higher %Z as to limit the expected earth fault current to desired low levels
  • if the owner's 3.3kV system doesn't include motors and has only step-down transformers connected to the busbars.
__________________
Raghunath
Register to Reply Score 1 for Good Answer
Register to Reply 12 comments

"Almost" Good Answers: