Motor Magnetising Current?

07/08/2014 10:37 PM

I was asked today how to interpret the "Mag. Cur" data on the attached motor nameplate. I believe that it means the magnetising current of the motor at 230/460V 60Hz, but have not been able to find any confirmation of this, despite a troll through the Baldor online technical documentation and a phone call to the local Baldor agent.

Are they saying that the motor draws 3A @230V 60Hz of which 2A is magnetising current?

Does anyone care to enlighten me?

__________________
paulusgnome
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Motor Magnetising Current?

07/08/2014 11:43 PM
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Motor Magnetising Current?

07/09/2014 12:09 AM

You are correct. The reason the number seems so high is due to the fact that an induction motor has no separate field supply, it has to come from the source the motor is attached to, through the stator windings and laminations, then through the air gap (which has poor magnetic properties) and into the rotor metal and rotor bars.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#3
In reply to #2

Re: Motor Magnetising Current?

07/09/2014 2:44 AM

Thanks for that, Ram.

While I'm well familiar with induction motors, I hadn't seen magnetising current written up on the nameplate like that before, hence my question. It is not even very common to see it specified in any of the various motor catalogues I have (GE, Teco, SEW ...) - even had the guy at Baldor scratching his head as it does not appear on any of the datasheets or catalogues that he had access to.

I'm guessing that at 2/3 of FLA the mag current is quite high on this motor because it is a low-power inverter-duty type, yes? And this may be why it features on the nameplate, because it is a bit higher than a more general-purpose motor?

__________________
paulusgnome
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #3

Re: Motor Magnetising Current?

07/09/2014 8:29 AM

I thought it was odd too so I checked NEMA MG-1, it's not a requirement for inclusion on the nameplate, and I didn't spot the definition there either. Maybe it's just Baldor being more user friendly.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#5
In reply to #3

Re: Motor Magnetising Current?

07/09/2014 8:42 AM

It is a 1HP motor, and that current is rated at F.L. (full load); so it looks OK to me.

Regards

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Motor Magnetising Current?

07/09/2014 10:46 AM

It is shown on there because it is intended for use with a VFD, and if you intend to use Vector Control, the VFD needs additional information about the motor circuit. Most, but not all, Vector Drives will be capable of performing an "auto-tune" procedure to gather the necessary info from the motor. But Baldor is being nice here for those who buy a cheap-o version incapable of that. By knowing the magnetizing current in addition to the FLA, you can determine everything else the Vector Drive will need to know.

And for engineers with Obsessive Compulsive disorder who need to cross check everything dozens of times, having this allows them to cross check the motor data that WAS attained via auto-tune.

Magnetizing current takes place primarily via reactive current, so is partially out of phase with the active current and therefore appears, when taken out of context on a nameplate like this, to be a higher percentage of total current than it really is.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#7

Re: Motor Magnetising Current?

07/09/2014 1:36 PM

Funny, you asked a straight forward question and the first thing you got was a reference with a requirement to understand the engineering side of an application vs. the application side of an application.

That would be kind of like asking why there are differenct octane ratings on gasoline and being given a link to study so you can figure it out for yourself.

If some people don't know, they obfuscate (baffle with bullshit).

A simple question deserves a simple answer, GA's to JRaef and RAM.

my own post...OT...just an observation

__________________
common knowledge...less common than common sense
Register to Reply Off Topic (Score 4)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #7

Re: Motor Magnetising Current?

07/09/2014 2:34 PM

I don't know if I agree. One could use, in Lyn's defense, the old "Teach a man to fish..." proverb.

Side note: funny version of said proverb:

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#9

Re: Motor Magnetising Current?

07/10/2014 9:38 AM

Easiest three steps:

Connect motor to Power supply through ammeter and power factor meter.

Note down no load current Io and Power factor CosΘ.

Calculate Io x Sin(Cos¯¹Θ). This is magnetising component of No load current,

Or else if you do not have meters to do above experiment, ask motor manufacturer (whom you already contacted) to also please advise No Load PF of the motor.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10
In reply to #9

Re: Motor Magnetising Current?

07/10/2014 10:26 AM

Why not IEC,BS,NEC,NEMA,VDE etc stipulate that no-load current should be printed in the motor name plate. It will serve as a guide to check after rewinding or after many years(hrs) of service whether no-load current has changed as well as to select a capacitor for motor starting or PF correction.

__________________
pnaban
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#11
In reply to #10

Re: Motor Magnetising Current?

07/10/2014 11:01 PM

Practice in those countries, where the quoted Standards apply, do not find economical to rewind small motors. These are use and throw.

For large motors, which are re-serviced, generally, data to be published on Name Plate is agreed between manufacturer and purchaser. Also Shop Test Reports include such information.

For the Electrical Equipment which is of standard design and manufactured in mass (called On Belt production), it is not economical to do standard tests as per quoted standards and .......

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12
In reply to #11

Re: Motor Magnetising Current?

07/10/2014 11:15 PM

As equipment for extensive testing of motors are not available in every work/ repairshop,name plate information like speed,FLC, no-load current,noise level,pf, capacitor for PFC,capacitor for parallel capacitor starting etc are very essential.

__________________
pnaban
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#13

Re: Motor Magnetising Current?

07/15/2014 7:33 AM

Your Imag is always going to be the same irrespective of the load, Ideally if there is no load , your motor current is the same as Imag.As load increase, the motor current is the vector sum of the Imag+Iload

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#14
In reply to #13

Re: Motor Magnetising Current?

07/15/2014 10:33 AM

Imag will change if deterioration of laminations,insulation between adjacent layers of laminations,rotor,number of turns in motor winding coils etc takes place. When we test a large motor after rewinding Imag & pf are different from its original value in manufacturer's literature it means something has gone wrong.

__________________
pnaban
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#15
In reply to #14

Re: Motor Magnetising Current?

07/15/2014 2:00 PM

Pnaban,

When we dismantle core, the lamination bends and straighten in handling and at times some teeth get bent, may be slightly. To straighten the bends, we hit lightly with a rubber or wooden mallet.

All above is cold working of Core Plates.

Cold working results in stresses in core plate, which changes or reduces the permeability of magnetic material.

Above results in earlier saturation of core, that means increase in magnetizing current and no load losses.

I experienced once this when rehabilitating Siemens, 1850 HP, 3.3 kV motor of Boiler Feed Pump of 80 MVA Power Plant in 1977.

After experiencing above change in core properties, I had to dismantled the finished core and got it stress relieved in GKW in India. Then GKW was known for supplying CRGO and CRNGO plates to Transformer Manufacturer and core plates to motors and alternator manufacturers in India. GKW had Stress relieving conveyor. It was a regular practice at GKW (Guest Keen William) to stress relieve all plates after punching.

After stress relieving, insulating of plates again and assembly, when tested for magnetizing test, I found that original magnetizing curve is reached.

After above experience, we added stress relieving of Stator Core Laminations as regular activity of Rehabilitation process.

Background is that I was part of Rehabilitation Team of Company and we had a developed standard check list and testing procedure before during and after completing the rehabilitation of machines. We had 3 Power Plants of 80 MVA, each with 10 Nos. of 3.3kV motors from Germany, AEG and Siemens, post war production - 1955 supplies which had lived their life by 1972 when I joined as Trainee. We started Rehabilitation in 1976-77.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#16
In reply to #15

Re: Motor Magnetising Current?

07/15/2014 10:35 PM

For 1850hp,3.3kV motor it may be economical & justified but what is the HP/Voltage limit(minimum) of motors above which stress relieving is economical?.

__________________
pnaban
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

eltech (1); JRaef (2); lyn (1); Paulusgnome (1); pnaban (4); powersolutionsFBD (3); RAMConsult (2); The.Tinkerer (1); Yahlasit (1)