Problem In CCPD

07/21/2014 10:01 AM

we have got 500kv transmission line and facing problem in it.There is indication of VT failure every night and the voltage of y-b and b-r drops to 350 and 470 respectively.Normally after 6 or 7 seconds the voltages become normal but some times the b-r voltages shoots to 570 and causes tripping of line.

we have checked all secondary cables.removed burden like auto recloser and fault locator(both non functional since long).changed ccpd of yellow phase.but no improvement.Now planning to change ccpd of blue phase.On red and yellow phase wee have power line carrier system(wave traps etc).

Remember problem only during night time.can some one help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Problem in ccpd

07/21/2014 10:05 AM

Tell me there isn't a loose connection in the r phase, Murphy. Something that only appears when the temperature is lower.

__________________
Good moaning!
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Problem in ccpd

07/21/2014 1:48 PM

Do you have any capacitors being switched on/off line?

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#3

Re: Problem In CCPD

07/22/2014 3:54 AM

Are there large motors/transformers or similar, being switched at night nearby?

Maybe from another company?

What about a modern 3 phase voltage monitor(s) being installed till the problem is found....?

Renting is the usual method in my time....though a purchase could pay for itself......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 65
#4
In reply to #3

Re: Problem In CCPD

07/22/2014 4:21 AM

actually there are four 500kv transmission lines from our station.Only indication is on this line.capacitors are not installed on this line.I think motors should not effect such a large system

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6
In reply to #4

Re: Problem In CCPD

07/22/2014 5:44 AM

You know what thought did!!! Of course large motors affect the power delivery around them!!

You now need to tie in the time of the problem and a change of "running" in those motors......or not!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Feb 2009
Posts: 35
#8
In reply to #4

Re: Problem In CCPD

07/23/2014 7:03 AM

You must be on a very good & high pay scale to be allowed to do what you are doing.

I recognise the ccpd schematic you posted, it is a circuit to reduce neutral(earth) & secondary voltage distortion in the Cap EVT.

Your problem may be solved with other ballast or different settings in the ccpd.

Refer problem to Siemens, the probable maker of the ccpd, for assistance.

Register to Reply
Associate

Join Date: Feb 2009
Posts: 35
#10
In reply to #8

Re: Problem In CCPD

07/23/2014 11:44 PM

CCPD,

Something about this problem niggles in my 80 year old brain about an experience on duo-bias transformer protection about 35 years ago.

Every thing worked out on commissioning tests except the switching to check the magnetic inrush, it was found that the interconnecting tertiary circuit was not connected between the separate phase relays.

You may have a similar problem, I think there should be a interconnected tertiary circuit between the separate phase CCPD's that is either not connected or open circuit. Compare the CCPD connections with the other line CCPD's.

I still recommend you contact an expert of the CCPD maker.

Register to Reply
Commentator

Join Date: Oct 2010
Posts: 65
#5

Re: Problem In CCPD

07/22/2014 4:40 AM

we have changed the blue phase ccpd of the line.lets see what happens today or tonight.I have uploaded the drawing for the connection of the ccpd.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: Problem In CCPD

07/22/2014 2:45 PM

CCPD - you mean Capacitive Voltage Transformer (CVT) I guess.

It seems the capacitor in CVT is having problems.

May be, it is time to replace.

__________________
Raghunath
Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#9

Re: Problem In CCPD

07/23/2014 1:50 PM

I remember working as a contractor at a cement plant and they had some equipment there that they were asked by the local power company to start only at night during low load conditions and furthermore they were supposed to call the power company prior to starting or stopping this equipment due to load fluctuations demanded by the plant. Perhaps this is similar situation as previously stated.

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 65
#11

Re: Problem In CCPD

07/30/2014 3:31 AM

it has been a week since we replaced the blue phase ccpd.The problem has not appeared again.But the results of removed ccpd are perfect.

Register to Reply
Anonymous Poster #1
#12

Re: Problem In CCPD

08/06/2014 3:31 AM

Hi mate, check your Voltage Transformer Neutral connections (Primary and Secondary)

Some times there is loose connections or bad connections to "EARTH" then you have floating neutral which causes this problems of voltages not correct

Good luck

Register to Reply
Register to Reply 12 comments
Copy to Clipboard

Users who posted comments:

Andy Germany (2); Anonymous Poster (1); Crabtree (1); Instruform (2); jan63 (3); Massey (1); raghun (1); wareagle (1)

Previous in Forum: Contactors   Next in Forum: Current Transformer

Advertisement