CBCT

07/23/2014 6:52 AM

earth fault limiting value is 100 Amps and o/g feeders are provided with 50/1 CBCT (specs: POC < 10.9 and relay setting range is 10mA). Now there is necessity of increasing the earth fault limiting value to 400 Amps. The question is whether I can use same CBCT or do I need to replace them with higher ratio?

Register to Reply
Pathfinder Tags: CBCT
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: CBCT

07/23/2014 7:27 AM

That "limitation" is amusingly, if not amazingly, high. How many volts?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#5
In reply to #1

Re: CBCT

07/24/2014 12:49 AM

6600 volts

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: CBCT

07/23/2014 8:10 AM

I think we need a little more information.

What are you doing that necessitates an allowance of 400A leakage?

I know one thing, I wouldn't want to be paying your electricity bill.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#6
In reply to #2

Re: CBCT

07/24/2014 1:00 AM

it is industrial application, I want to make REF (Restricted earth fault) scheme effective, because at present the CT ratio is 3000/1 and NGR value is such that earth fault current is limited to 100 Amps so setting of REF to 10% makes current sensing at 300Amps! so if I increase the value of earth fault current to 400Amps then 10% setting would make scheme effective.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9
In reply to #6

Re: CBCT

07/25/2014 4:21 AM

I think there is no need to have REF protection and 100A NER should be good enough even if you have large distribution system connected to your switchboard. That is my view.

Coming to your question - yes, 50/1A CBCT in the outgoing feeders can be retained. I don't think the CT will have any saturation issues when the current is 400A, i.e. 8-times its primary rating. However, you can verify with the CT name plate details.

Even if it is saturating, it may not be a big deal as residually connected earth fault protection can be set in the feeder protection to supplement the sensitive earthfault protection at higher fault currents.

__________________
Raghunath
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#10
In reply to #9

Re: CBCT

07/25/2014 5:11 AM

Thnks for rply, it is quite helpful,

The transformer size is 25MVA, still you would suggest not to implement REF?

And what if (regarding CBCT) current is 800A instead of 400A?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#3

Re: CBCT

07/23/2014 9:14 AM

Nikola? Is that you?

Register to Reply Off Topic (Score 6)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: CBCT

07/23/2014 3:38 PM

I must be missing something if you are using 50:1 CTs to measure up to 100A and now want to use the same 50:1 CTs to measure up to 400A.

Yes, replace the CTs.

__________________
jack of all trades
Register to Reply
Participant

Join Date: Jul 2014
Posts: 2
#7

Re: CBCT

07/25/2014 1:15 AM

YUP

Register to Reply Score 1 for Off Topic
Associate

Join Date: Jul 2014
Location: I live in USA, Colorado in the houses of 7 Summits
Posts: 28
#8

Re: CBCT

07/25/2014 4:15 AM

Bar types are available with higher insulation levels, here you can replace them with higher ratio. It operates on the same principal of windows CT.

Register to Reply