Separation Between Electrical and Instrumentation Ducts

08/20/2014 9:33 AM

The common sense and engineering practices command to put on different underground raceways electrical and instrumentation cables. Same way is wrote at NEC, according to level of voltage. But so far, I have no found one specific practice, norm or code, that give some rules about that, so with the pull hole to.

I will appreciate any comment about that

Regards,

Register to Reply
Pathfinder Tags: Underground raceways
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 9:55 AM

Our practice [ in power station design] is to put the instrument cables in the upper most row in steel [grounded] ducts and keeping 10 inches [center line to center line] distance between rows, in pvc ducts, low voltage and control cables and in lowermost row medium voltage cables. In manhole the instrument cable are in close top solid bottom cable tray. The steel ducts and cable trays are grounded in manhole.

__________________
Julius
Register to Reply
Participant

Join Date: May 2011
Posts: 4
#5
In reply to #1

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 11:53 AM

According to the commentary, the arrangement is done in man holes that look big. Right now, we are inspecting an installation were the cables run together in the same tray holes, according to the project engineering drawings, the average tray holes is 1x1x1.6 meters. It was one misunderstand of specification ("instrumentation underground raceways shall be done by electrical discipline"), In order of that we recommended split electricity and instrumentation.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 2:58 PM

I do not believe that you are qualified to, "inspect an installation".

I also believe that your practice is unethical and should be stopped!

You should immediately refund the commission your were paid, and leave the site.

Recommend to the customer who hired you that they should hire a QUALIFIED inspection organization that does not rely on total strangers whose qualifications are unknown and have no obligation to provide correct answers to questions such as yours.

Register to Reply
Participant

Join Date: May 2011
Posts: 4
#8
In reply to #7

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 4:10 PM

I only comment what is found, and only look for specific code or norm that support, separate installation.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 4:15 PM

You want the forum to do the work for which you are being paid.

THAT IS UNETHICAL!!!!

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#2

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 10:19 AM

I do not believe there is a real code standard on this because of the occasional ambiguity of what is considered electrical and instrumentation cables. Is a one microsecond wide 2kV 400 ampere pulse four times a day considered electrical or instrumentation?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6
In reply to #2

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 1:20 PM

look at the drawings and the specs on them. if it isn't clear then pick up he phone and call the person who drew them. is that so hard?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 10:27 AM

I agree with redfred, actually no standard is available. But - if it is possible- I shall run this cable in separate steel duct-from instrument or communication cables.

However, NESC [ANSI C2] /2007 requires 3 inches [clearance] concrete between supply and communication conduit system [Rule 320 B(2)].

__________________
Julius
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#4

Re: Separation Between Electrical and Instrumentation Ducts

08/20/2014 10:48 AM

Redfred is right.

Where I used to work, we had high voltage and low voltage (control) lines running in the same conduit in some of our process equipment. Because that's how they always did it with no problems they claimed.

And until we started to get erratic results, only then did it come down that we could do one of (2) things.

  1. The first is to make sure the control and feed back lines were shielded.
  2. Run separate conduit for High Voltage and control lines, (lines were still shielded).
__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply