How To Rectify Supply When 3 Phase Supply Gets Reversed From Grid End?

08/25/2014 3:31 AM

Hey Guys,

Is there any device which automatically rectify if the RYB phases gets reversed from GRID end? otherwise we ourself need to change the phases.

Register to Reply
Pathfinder Tags: 3 Phase changer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: How to rectify Supply when 3 Phase supply gets reversed from GRID END?

08/25/2014 4:52 AM

This could be done with a phase monitoring relay and a reversing motor starter, but it sounds really weird.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#4
In reply to #1

Re: How to rectify Supply when 3 Phase supply gets reversed from GRID END?

08/25/2014 8:20 AM

It's a weird world, so stuff happens, Your answer is the best approach, a reversing contactor is mechanically interlocked, there's no risk of phase to phase short, but just to avoid simultaneous coil pull, the O.P. should allow a few mSec. between brake and make.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#2

Re: How to rectify Supply when 3 Phase supply gets reversed from GRID END?

08/25/2014 5:42 AM

Why would the grid reverse a phase?

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply
Power-User

Join Date: Jul 2014
Location: Savannah, GA. The post office decided to change my address again.
Posts: 253
Good Answers: 19
#3
In reply to #2

Re: How to rectify Supply when 3 Phase supply gets reversed from GRID END?

08/25/2014 6:20 AM

I was curious about that one too. Never heard of the grid reversing phase before. But I don't live where the op does.

__________________
Never seem more learned than the people you are with. Wear your learning like a pocket watch and keep it hidden. Do not pull it out to count the hours, but give the time when you are asked.(Lord Chesterfield)
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#7
In reply to #3

Re: How to rectify Supply when 3 Phase supply gets reversed from GRID END?

08/25/2014 9:06 PM

The commercial units I found were from India, so I suppose that might be a problem there. Possibly phase reversals occur during repairs and it makes no difference if there are no users of all 3 phases.

http://www.saboindia.com/automatic-phase-sequence-corrector.html#automatic-phase-sequence-corrector

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#9
In reply to #2

Re: How to rectify Supply when 3 Phase supply gets reversed from GRID END?

08/26/2014 1:13 AM

Supply authorities would be crazy to reverse phases. The amount of damage that could be done by motors going the wrong way round and possible health risks to people would put them out of business in a hurry?

So who is the grid supplier?

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#11
In reply to #2

Re: How to rectify Supply when 3 Phase supply gets reversed from GRID END?

08/27/2014 6:05 AM

I worked in Beirut during the war where power lines were regularly damaged in the shelling. The repairs were ad-hoc and there was no guarantee that the phase rotation would be the same after repair. In addition if one phase was lost there would often be DIY repairs in the street which usually involved linking the dead phase to one of the other phases still present. It worked for the single phase consumers but caused havoc for three phase consumers like ourselves (the neutral current of a three phase transformer is spectacular under those conditions).

I had to build a protection system with a contactor and phase rotation relay (as well as over and under-voltage trips) which could detect and protect against these faults.

In some countries little attention is paid to the phase rotation when wiring or repairing the local power distribution system and both phase loss and rotation detection is needed.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#5

Re: How To Rectify Supply When 3 Phase Supply Gets Reversed From Grid End?

08/25/2014 12:23 PM

http://dir.indiamart.com/impcat/phase-sequence-corrector.html

Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: How To Rectify Supply When 3 Phase Supply Gets Reversed From Grid End?

08/25/2014 2:12 PM

If you are rectifying the 3 phase into DC (which is what "rectify" means in the electrical world), then the phase sequence of the AC coming into the rectifier is wholly unimportant!

Now were you using the term "rectify" to mean "to make right"? Then I would have used the term "correct" to avoid that confusion. If that is what you meant, then the solution is to either use a phase sequence monitor relay to INDICATE that the sequence is wrong so whomever connected it can "correct" the situation, or use the signal to operate a set of reversing contactors on the incoming line connections so that everything down stream of those contactors sees the "correct" rotation sequence.

This, by the way, is a real concern for people who use portable generators to power up fixed equipment. Classic example is waste water pumping lift stations. If the utility fails, the pump station can overflow. So the municipality has a fleet of service trucks that have portable generators on them. In a perfect world all generators are phased to match the pump stations. But occasionally one small municipality has to loan their crews to another, and the coordination is virtually impossible. So in these smaller communities we would always install the contactors and monitor relays so that the change was automatic as soon as they connected the generators. The reason was that usually the power failed during a storm, so you don't want electricians swapping wires during a storm.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: How To Rectify Supply When 3 Phase Supply Gets Reversed From Grid End?

08/25/2014 10:17 PM

The place I served my apprenticeship at had its own power station dating from the 1930's. In the early 50's the newly formed national grid came to the area so it was decided to import power as the station was struggling with the ever growing demand.
Our plants had been running BYR since day one, the grid was RYB.
Simple enough, swap the phases at the intake sub. All our LV was 550V until the mid 60's when several new plants were built. These were to use 433V for the LV and some genius decided the phase rotation was to be RYB. Not really a problem as the new plants were stand alone.

The early 70's and I arrived on the scene. One of the first projects I got involved with was major alterations to an old plant. All the retained bits of the plant was to remain on 550V, all new bits were to be 433V. Do we make it BYR to match the old 550V parts of the plant or RYB to match the other 433V plants? We went with BYR as again this wasn't tied in to the other plants.

A few years down the line and the plants had spread out somewhat. Still not a problem until the idiots (management) wanted a new office block and IT centre mid way between.
I was asked to arrange the power feeds. 2 x 200A RYB from plant "A" and 2 x 200A BYR from plant "B".
Most of the plant electricians were totally oblivious to the different phase rotations and thought I'd taken leave of my senses when we connected the various feeds in.
I've got to admit, it did look strange.

In about ½ mile square you could run across

3.3KV BYR
3.3KV RYB
550V BYR
433V BYR
433V RYB

11KV was always BYR

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #8

Re: How To Rectify Supply When 3 Phase Supply Gets Reversed From Grid End?

08/26/2014 5:03 PM

Similar situation here in California. PG&E (Pacific Gas and Electric), the largest utility in Northern Calif., is ACB rotation. Southern California Edison (SCE) is ABC rotation, as is most OEM equipment, including portable generators, and it is the default rotation for VFD outputs. It causes no end of issues when people get new equipment or move it from an SCE service area to a PG&E service area and ASSume it was set for proper rotation . I've had some very interesting arguments with people in the field when I try to explain to them that it is all relative, they don't seem to understand, or don't want to I guess...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: