09/10/2014 5:11 AM
Please let me know how to read Overload / Short circuit ranges from a MCB's Tripping Characteristing Curve. Assume that the MCB is a 10kA, C curve as per IEC 60898
Re: MCB Characteristic Curve & Overload / Shortcircuit Protection
09/10/2014 5:16 AM
Declined. An MCB is not suited for use as a motor overload device. Contact the manufacturers directly to obtain characteristic curves for the device in question.
09/10/2014 5:28 AM
I have a C type characteristic curve. When I is equal to 5In to 10In vertical asymptote. to time zero (in the graph time is in Vertical axis & current rating in horizontal axis).
I want to know 5In - 10In is overload range or short circuit range?
09/10/2014 5:36 AM
The graph is being read correctly though not interpreted correctly: one axis is the current, the other the trip time and to differentiate between <...overload range or short circuit range...> would be meaningless.
For the correct protection of a motor an overload device is needed in addition to a wiring protection device. The topic is called "co-ordination" and British Standard 7671 gives full details.
If in doubt, consult a qualified Electrical Engineer.
<unsubscribes>
09/10/2014 5:56 AM
Curve is attached.
Please define the areas of Overload protection & Short Circuit Protection.
09/10/2014 6:03 AM
Why?
India - Member - New Member
Good Answers: 164
09/10/2014 11:59 PM
As i mentioned in the PM, 5x cannot be called an overload. It is a 'low' short-circuit.
One definition you can think about : "Overload" is a higher-than-normal current through the normal, INTENDED path. "Short Circuit" is a higher-than-normal current through an UNINTENDED path.
09/10/2014 10:06 AM
Postpone the interview until you've had time to get the answers to all the interview questions.
Otherwise, it won't go well.
Anonymous Poster #2
10/10/2014 12:24 AM
Hi!
The tripping curve of a MCB is quite important because it decides the protective functionalities such as overload or short circuit protection. It is described as a characteristic curve with a couple of parts. Each part has a different function to protect electrical equipment. For example, the overload protection curve is always laid at the bottom of the co-ordinate while the fault protection ones are set at above areas of the co-ordinate. Therefore, the protective devices will operate correctly.