Breaker Question

09/14/2014 1:03 AM

Hi, Im Just a newbei, can you suggest how can I Know designated current capacity for a breaker that i will use. What are the parameters to be considered?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: Etherville
Posts: 12362
Good Answers: 115
#1

Re: Breaker

09/14/2014 6:00 AM

The first issue is getting people to understand the question. Can you explain a little more ? I can't speak for anyone else, but I have no idea at all about what you are asking. Add some more detail, and I'm sure that somebody here can give you what you want.

__________________
For sale - Signature space. Apply on self addressed postcard..
Register to Reply
4
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Breaker

09/14/2014 8:08 AM

First, one has to know the electric power source you will be using. The region a system will be used will often identify the local power grid capabilities but many times other electric power sources (battery, vehicle alternator, solar panel, etc.) maybe used.

Second, one must know the load this electric power will be operating. If it is a dedicated circuit then often the manufacturer of the device to be operated will have relevant information about which parts should be used to drive their product. If it is not a dedicated circuit then the standard conventions of local wiring codes will be the guide to follow.

Lastly, to follow relevant wiring codes the environment (explosive gas, salt water, rain, ice, earthquake, direct burial, vacuum, etc.) this circuit resides will determine which parts of the code should be followed.

Each of these three overly simplified steps can have many sub-steps depending on the application. You should notice that your question gives us absolutely no information at all in each of these three greatly simplified steps.

Hire an approved electrician or electrical engineer to do this work. The lives you save will be grateful.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 4)
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#15
In reply to #2

Re: Breaker

09/15/2014 12:41 AM

GA, Fred. Seems they're not sure of what their doing, so the only safe answer is just what you said.

Be safe and Hire an certified electrician and go to school to learn the fundamentals of electricity. Always stray on the safe side of life.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Breaker

09/14/2014 8:58 AM

CODE. CODE. Or CODES. CODES. As red said, it's all there.

We use NFPA/IEC/BS/IEEE or whatever the local flavor is.

Google circuit protection and read.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4

Re: Breaker Question

09/14/2014 10:14 AM

I'd just use a 500 amp breaker and avoid nuisance resets

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #4

Re: Breaker Question

09/14/2014 3:34 PM

Those resulting cable fires are a bit of a nuisance thou aren't they?

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#19
In reply to #4

Re: Breaker Question

09/19/2014 5:32 PM

And see his house from afar when the fire rages

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#5

Re: Breaker Question

09/14/2014 12:38 PM

Consider the electrical code.

Consider not to touch anything.

Consider to read up on breakers as a way forward.

Consider an electrical engineer or certified electrician for calculation and installment

Consider the lethal force of electricity.

Internet search is a pretty thing:

http://en.wikipedia.org/wiki/Circuit_breaker

What is your intent? Why would you want to know?

__________________
Common Sense Dictates
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#6

Re: Breaker Question

09/14/2014 12:45 PM

current capacity is mentioned on the breaker that you will use. Tripping characteristics, Short circuit fault level withstanding level rating, voltage rate, setting of over current long and shirt time, instantaneous current and time, earth fault/ground fault setting, Frame size, rated current, 3 pole/4pole etc are the parameters to be considered.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7

Re: Breaker Question

09/14/2014 2:22 PM

Without knowing the applicable codes governing electrical installation and years of experience required to do it properly, you should not attempt any unsupervised installation of, or materials or component selection for, any electrical circuitry or device....

http://www.schneider-electric.us/documents/support/codes-and-standards/circuit-breaker-markings-iaei.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#9

Re: Breaker Question

09/14/2014 3:42 PM

Here is a rule-of-thumb you could go by. Whatever the maximum current flow is, go with a breaker that is 20% greater. That means going up one breaker size (15, 20, 25, 30). You must also up the wire size that will handle the maximum current.

__________________
Mr.Ron from South Ms.
Register to Reply
Participant

Join Date: Sep 2014
Posts: 2
#10

Re: Breaker Question

09/14/2014 7:45 PM

220V is the Electrical Source, the load i 20A. I will use AWG #12 for wire. Is 20A breaker is applicable to use???

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11
In reply to #10

Re: Breaker Question

09/14/2014 8:32 PM

No 30A #10...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#12
In reply to #10

Re: Breaker Question

09/14/2014 10:04 PM

No, you just would come back to ask for an auto reset breaker.

__________________
Common Sense Dictates
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#17
In reply to #10

Re: Breaker Question

09/15/2014 10:21 AM

Standard breakers should not be used for more then 80% of their load rating. Though the breaker is rated for 20 amps that load rating is for short term not to accede 3 hours.

So you will need to use the next size up which is 30 amps. Same with the wire you shouldn't put more the 80% of the load rating on it for long durations. If you increase the breaker size you increase the wire or the wire will fry before the breaker trips.

Breaker is to protect the wire not the device powered by it.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#18
In reply to #10

Re: Breaker Question

09/15/2014 10:28 AM

You described the wire in American Wire Gauge, which is only used in America, to the best of my knowledge. The Metric world describes wire size in cross/sectional area, square millimeters.

220V could be either industrial, commercial, or residential wiring, there are typically different electrical codes for each type of installation, with industrial being more strict than commercial and commercial being more strict than residential. A multi-unit apartment building must follow at least commercial level building codes.

I would Strongly Recommend (which is Engineer-speak for 'I cannot order you do do something, but follow this as if it were a direct order') that you talk with a friendly local Electrician, Union Electrician if you can find one. They will be able to help you out with your project much better than a bunch of semi-anonymous yahoos (of which I am one) providing snarky answers to poorly-worded and ambiguous questions.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Power-User

Join Date: Dec 2009
Location: Tampa Florida USA
Posts: 180
Good Answers: 3
#13

Re: Breaker Question

09/14/2014 10:37 PM

There should be a number on the breaker right before the "A".

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#14

Re: Breaker Question

09/15/2014 12:17 AM

Hopefully she can help?

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: Breaker Question

09/15/2014 4:31 AM

It's all in the applicable local electricity standards, for example British Standard 7671 for the UK. If in doubt, hire a qualified local Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

adreasler (1); Alanvaderi (1); dj95401 (2); Fredski (1); IdeaSmith (2); jack of all trades (1); Kris (1); lyn (1); Munster (1); ozzb (1); PWSlack (1); redfred (1); ronseto (1); sharpstick (1); SolarEagle (2); Zhei (1)

Previous in Forum: HEI Distributor Internal Wiring Oddity   Next in Forum: AC Generator

Advertisement