2000 KW GEN SET 440V Not Developing Voltage

09/16/2014 3:26 AM

Dear Sir

We have received GEN SET 2000 KW 440 V with out engine for repairs indicating not developing voltage.We have checked stator windings 12 groups leads coming out for resistance, inductance found equal,Surge test is also OK ,IR 0.3 M OHMS,Rotor coils 4 nos checked individually for resistance inductance found equal .Surge test OK.Excitor stator and rotor windings resistance/inductance/surge test OK,,Gave seperate AC supply checked all Excitor stator poles are getting magnetised , Rotor 3 phase winding having equal voltage. Customer disconected Electronic AVR gave seperate Supply to execitor stator then also not developing while running GEN SET.Wish what could be reason for not developing voltage

Regards

Sadasivam

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: 2000 KW GEN SET 440V not developing voltage

09/16/2014 3:46 AM

I don't know, but I bet the generator manufacturer does. I'd get on the phone and at least talk the problem through with them and possibly get someone in.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: 2000 KW GEN SET 440V not developing voltage

09/16/2014 5:21 AM

I agree with Crabtree. I think the problem is located in excitation circuit. If the exciter is a dc generator then check the armature current and the exciter excitation. But it will be better to ask the Manufacturer.

__________________
Julius
Register to Reply
Associate

Join Date: Sep 2009
Posts: 33
#3
In reply to #2

Re: 2000 KW GEN SET 440V not developing voltage

09/16/2014 5:36 AM

Excitor is having 3 phase rotor and the converted thro diode as DC to main rotor field supply

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: 2000 KW GEN SET 440V not developing voltage

09/16/2014 6:56 AM

Great! So, how did the phone call with the manufacturer go?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#11
In reply to #3

Re: 2000 KW GEN SET 440V not developing voltage

09/17/2014 4:20 AM

Have you checked the rotor-excitation-diodes ? These diodes convert the AC voltage from the excitation-rotor in to a DC voltage to make a constant magnetic field in the generator-rotor.

These diodes are physically mounted on the generator or excitatory rotor. They rotate at the seem velocity as the rotor.

When these diodes are broken (open circuit), the excitatory-rotor voltage will not feed / supply to the generator-rotor coils with energy and these coils will make no magnetic field.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: 2000 KW GEN SET 440V not developing voltage

09/16/2014 7:41 AM

Wish I could be there to check rotating diodes, fuses, and connections...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6
In reply to #5

Re: 2000 KW GEN SET 440V not developing voltage

09/16/2014 8:18 AM

Ha!

__________________
Good moaning!
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#7
In reply to #5

Re: 2000 KW GEN SET 440V not developing voltage

09/16/2014 10:14 AM

As long as the diodes are polar aligned, he'll be fine.

__________________
common knowledge...less common than common sense
Register to Reply
Associate

Join Date: Sep 2009
Posts: 33
#9
In reply to #5

Re: 2000 KW GEN SET 440V not developing voltage

09/17/2014 1:13 AM

Doide were checked along with socket terminal found OK AC supply is getting converted to DC

SADASIVAM

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#13
In reply to #9

Re: 2000 KW GEN SET 440V not developing voltage

09/17/2014 4:54 PM

Are those OEM diodes, and did you check the fuses and all the connections? The rotational forces are very high and can cause temporary changes to anything that is spinning, then everything reverts to "normal" when the shaft is at standstill.

How can you be certain that the "...AC supply is getting converted to DC..."? There's no way to verify that unless you have a flux probe in the air-gap, and if that were true then your generator would have output.

Only thing left is your instrumentation; you did use an independent meter on your output terminals, didn't you?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 19
Good Answers: 1
#8

Re: 2000 KW GEN SET 440V Not Developing Voltage

09/16/2014 10:45 PM

We had a strange problem once with a rebuilt machine during startup.

Turned out to be pigtail leads (large bare braid) on the diodes which 'bent' while running, thus grounding to diode case bracket. During coastdown, the pigtails would bend back, so all static tests passed.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: 2000 KW GEN SET 440V Not Developing Voltage

09/17/2014 2:36 AM
__________________
Julius
Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#12

Re: 2000 KW GEN SET 440V Not Developing Voltage

09/17/2014 7:41 AM

Of course it is not generating voltage, you need to hook the engine back up to it.

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#14

Re: 2000 KW GEN SET 440V Not Developing Voltage

09/19/2014 12:06 AM

During Separetely Excitation test, what was the voltage generated for 12 V DC Excitation ? If the voltage is any thing lesser than Rated Voltage then the problem is with the Excitation Circuit ?

Have you done any rewinding ?if you have done rewinding of Ex Stator or Main Rotor check that adjuscent pole is of different polarity..

You have checked all windings for static tests and the test results seems to be ok except the IR of 0.3 MOhm, I feel this is too low..try heating the Alternator through the External Source, which may improve the Insulation Resistance..

Check the Fuses..

Regards,

Vishram LELE

Register to Reply
Associate

Join Date: Sep 2009
Posts: 33
#15
In reply to #14

Re: 2000 KW GEN SET 440V Not Developing Voltage

09/19/2014 5:09 AM

No rewinding done on excitor and diodes were checked seperately giving AC to check DC output.Heating of windings done to 5 Mohms. Control panel is at site with customer

Regards

Sadasivam