REF Protection

09/16/2014 11:12 AM

Dear ALL

If an REF relay operate for a fault outside its zone, what are the possible reasons??

Regards

BYJU

Register to Reply
Pathfinder Tags: protection REF transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Nov 2012
Posts: 21
#1

Re: REF Protection

09/16/2014 12:07 PM

1)Check the value of stabilising resistance.

2) Check the relay pick up

during a throughfault(outside of REF zone) just outside the zone maximum currunt will flow through 1 line CT and 1 NCT(current in 2 CT will be in opposite polarity i.e 180 deg apart). this current will circulate and generally will not enter in REF relay path. but, due to lead resistance there will be voltage across the REF path . This voltage may drive a current in REF path and operate REF relay if we do not install a external resistance in series with the REF relay. This is stabilising resistance, and if it is of low value then current will flow in the REF path during through fault.

Register to Reply
Commentator

Join Date: Mar 2009
Posts: 57
#5
In reply to #1

Re: REF Protection

09/17/2014 12:17 PM

Thank u

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Mar 2009
Posts: 57
#6
In reply to #1

Re: REF Protection

09/17/2014 12:23 PM

Dear Sir,

If the communication channel fails for a Overhead Line distance protection, what will be the course of action ?

Rgds

BYJU

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2

Re: REF Protection

09/16/2014 11:34 PM

Please record all your problems in one post and raise query. It will be easy to understand to suggest appropriate solution .

Please indicate whether REF relay trips or directional relay trips or both trips.

Check Neutral CT location. Is it located before earthing of neutral or after earthing.

Are Neutral CT and phase CT characters and ratios matching.

My experience in most of the cases referred to me is CT ratio and location of CT are issues.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 21
#4
In reply to #2

Re: REF Protection

09/17/2014 12:02 PM

besides checking ratio it should be confirmed that in all 4 nos CTs we use PS class secondary core. usage of metering core in any ct may create prob

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#3

Re: REF Protection

09/17/2014 5:25 AM

Looking at his/her other posts, it must be mid-terms in the Middle East

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

avra.setcl (2); byjuram (2); dj95401 (1); ramvinod (1)

Previous in Forum: Kelven Water Dropper   Next in Forum: Carrier Communication Fails

Advertisement