during a throughfault(outside of REF zone) just outside the zone maximum currunt will flow through 1 line CT and 1 NCT(current in 2 CT will be in opposite polarity i.e 180 deg apart). this current will circulate and generally will not enter in REF relay path. but, due to lead resistance there will be voltage across the REF path . This voltage may drive a current in REF path and operate REF relay if we do not install a external resistance in series with the REF relay. This is stabilising resistance, and if it is of low value then current will flow in the REF path during through fault.