Faulty Alternator

09/17/2014 2:44 PM

Dear All

Alternator installed at Waukesha Gas Engine for two (02 No;s) batteries 200 A each for supply of 24 V to panel. Batteries water make up has incresed to considerable amount, almost have to do daily make up. Whats the matter here? Overcharging? Is alternator faulty? Which part in alternator could be defective? I m mechanical engineer but need to rectify the problem

Register to Reply
Pathfinder Tags: Faulty Alternator
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: faulty alternator

09/17/2014 3:54 PM

Are both 12V batteries (connected in series to give 24V) showing the same problem?

Try swapping the suspect batteries with similar batteries that are working (assuming you have more than one gas engine).

If the swapped working batteries start to show increased water usage you know it's likely the alternator or something connected to it, if the problem moves with the batteries or only one of the series connected batteries has a problem you know you likely have a battery failure and can just replace the battery(s).

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Faulty Alternator

09/17/2014 5:51 PM

Is it a 12V alternator? 24V alternator? 48 V alternator?

What V is it putting out?

How is it connected?

How are the batteries connected?

How do you expect anybody to help?

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: Faulty Alternator

09/17/2014 7:04 PM

use this

Register to Reply
Commentator

Join Date: Nov 2008
Posts: 80
Good Answers: 4
#4

Re: Faulty Alternator

09/17/2014 11:23 PM

The voltage regulator for the alternator if faulty causing the battery to overcharge. This causes the electrolyte to boil.The replacement alternator probably has a faulty voltage built into it. Try a new alternator.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #4

Re: Faulty Alternator

09/18/2014 7:08 AM

I agree it's likely to be a faulty voltage regulator, but OP didn't say it's a replacement alternator. "Batteries water make up has increased...." suggests it worked OK before the problem arose.

He should measure the voltage, if it's much above 28 volt there's a problem. He didn't say what type of voltage regulator, if it's an old electromechanical (vibrating contact) type it should be possible to adjust it. If it's electronic it's likely to need a replacement regulator.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#5

Re: Faulty Alternator

09/18/2014 1:29 AM

Do you know how to read a volt and am meter? If you can't do basic electrical troubleshooting then you really need to find somebody who can.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Faulty Alternator

09/18/2014 4:24 AM

Those batteries will fail very soon, if they haven't done already....assuming the charging is too high as would appear.....

A cheap charger will cause the same problems, as will a defective charger.....or no charger!!!

Give details of your charging control please?

__________________
"What others say about you reveals more about them, than it does you." Anon.