Rated Short-Time Withstand Current(Icw) & Conditional Short-Circuit Current(Icc)

09/23/2014 9:03 AM

Hi,

Referring to IEC 61439-1&2 could see the short circuit withstand (Icw) is specified for a circuit of an assembly whereas conditional short circuit withstand (Icc) is specified for an assembly.

Would greatly appreciate if some can help me to understand what exactly the above means.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#1

Re: Rated short-time withstand current(Icw) & Conditional short-circuit current(Icc)

09/23/2014 9:14 AM

The definition, clauses 5.3.4 and 5.3.5 both refer to an ASSEMBLY (I have BS EN 61439-1:2011 which is identical to IEC version)

Could you be more specific where it differs?

__________________
rogerggbr
Register to Reply
Participant

Join Date: Aug 2014
Posts: 2
Good Answers: 1
#2

Re: Rated Short-Time Withstand Current(Icw) & Conditional Short-Circuit Current(Icc)

09/24/2014 3:06 AM

Icc: Rated conditional short circuit current. This is the rating that is associated with SCPD (Short Circuit Protective Device), the short circuit current initially flow and cleared by SCPD.

Icw: Rated short time withstand current. This is the rating of the Breaker that the assembly can withstand for a set time duration(say micro second) and breaker need not to be tripped.

Register to Reply
2
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Rated Short-Time Withstand Current(Icw) & Conditional Short-Circuit Current(Icc)

09/24/2014 4:30 PM

I think the definitions are better explained in IEC 60439-1:

4.3 Rated short-time withstand current (Icw) (of a circuit of an ASSEMBLY)

"The rated short-time withstand current of a circuit of an ASSEMBLY is the r.m.s. value of short time current assigned to that circuit by the manufacturer which that circuit can carry without damage under the test conditions specified in 8.2.3. Unless otherwise stated by the manufacturer, the time is 1 s."

That means without any protection device the ASSEMBLY has to withstand 1 sec. this current.

4.5 Rated conditional short-circuit current (Icc) (of a circuit of an ASSEMBLY)

"The rated conditional short-circuit current of a circuit of an ASSEMBLY is the value of prospective short-circuit current, stated by the manufacturer, which that circuit, protected by a short-circuit protective device specified by the manufacturer, can withstand satisfactorily for the operating time of the device under the test conditions specified in 8.2.3 (see also 7.5.2). The details of the specified short-circuit protective device shall be stated by the manufacturer."

That means providing a certain protection device the ASSEMBLY has to withstand this current during this protective device operating time. This time usually is less than 1 sec. [let's say 0.25 sec minimum] and Icc could be more than Icw

__________________
Julius
Register to Reply Good Answer (Score 2)
Participant

Join Date: Sep 2014
Posts: 4
#4

Re: Rated Short-Time Withstand Current(Icw) & Conditional Short-Circuit Current(Icc)

09/25/2014 6:12 AM

rogerggbr, rkguptab, 7anoter4 --- thanks a lot for your prompt replies.

I'm referring to IEC 61439-1&2, Edition 2, 2011-08 which defines 'Icw' of a circuit of an assembly and 'Icc' of an assembly.

The point I'm confused about is the actual meaning of these two values.

As per my understanding is below, please correct me wherever I've been wrong.

Icw: is the withstand strength of an assembly without protective devices (protective devices (SCPDs) in incoming as well as outgoing circuits will be replaced with shortened copper bars during an actual test if conducted). Since the weakest point in a system defines the actual strength of an assembly, this value is defined for a circuit (in effect the smallest outgoing circuit).

Icc: is the strength of an assembly for a time that the incoming SCPD(located within or outside the assembly)breaker take to trip and isolate the assembly. This value can be made higher than Icw by introducing a suitable SCPD in incoming circuit. Here also I feel the strength of smallest circuit matters but not mentioned in IEC definition.

I couldn't understand the importance of "of a circuit of an assembly" part in IEC definition of Icw while its being ignored for Icc.

Please help me understand it better.

Thanks in advance.

Register to Reply
3
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#5
In reply to #4

Re: Rated Short-Time Withstand Current(Icw) & Conditional Short-Circuit Current(Icc)

09/25/2014 6:46 AM

It may help to think of how the tests are done.

Icw tests are for a defined magnitude (RMS and peak) and a defined time, e.g. 50kA for 1 second, 105kA peak. This type of test will normally include various busbars in a complete assembly (the standard describes more detail) and could also include any suitable device e.g. an Air Circuit Breaker with trips disabled.

Icc tests are carried out for a specific device, also called prospective tests. The potential (prospective) magnitude is defined, but the actual measured values and the time to clear will be device dependant. It can also cover the whole assembly, busbars etc. but the device cannot now be changed if the test is to remain valid for future boards.

Usually these days we do both tests on every new design, so we have covered all possible options. That's not all tests on all devices, just those that are appropriate for their use. The incomer, for instance, will have both Icw and Icc tests, small feeders usually just the Icc.

__________________
rogerggbr
Register to Reply Good Answer (Score 3)
Participant

Join Date: Sep 2014
Posts: 4
#6
In reply to #5

Re: Rated Short-Time Withstand Current(Icw) & Conditional Short-Circuit Current(Icc)

09/25/2014 8:47 AM

Hi, thanks for reply, your reply has given me more information on the tests and concepts.

If a tested equipment name plate carry only one value of 'Icw' and 'Icc' what should we understand.

thanks in advance

Register to Reply
Participant

Join Date: Sep 2014
Posts: 4
#7

Re: Rated Short-Time Withstand Current(Icw) & Conditional Short-Circuit Current(Icc)

09/29/2014 12:42 PM

Quoting Chris Smith, DIRECTOR at CIS ASSOCIATES Ltd

IEC 61439-1/2, and for that matter IEC 60439-1, withstand rating of busbars is based on the concept that the assembly must be able to withstand the prospective fault level at the point of connection. Thus an assembly has only one Icw rating.
When authoring IEC 61439-1/2 we were very much minded to facilitate the simplest possible design verification for the broadest range of manufactured variants possible from a given design. The objective being to eliminate the need for assemblies to have application specific design elements which were not verified or based on a verified design, as was often the case with IEC 60439-1 assemblies.
For assembly designs were a wide range of assemblies are to be made using verified designs each module of the design is verified and then the modules required for a given application brought together in the built assembly. Some module ratings may be derived from those which have been verified by testing using the rules/procedures defined in the standard. The principle remains that all elements of a IEC 61439-1/2 assembly should be verified designs.
It is therefore true to say that an assembly might be made up using, say, a horizontal busbar rated at 80kA 1s and a series of distribution busbars rated at 50kA 1s but then the assembly can only be rated at 50kA 1s because it is as strong as it's weakest point.
In much the same way many assemblies if tested without devices achieve a Uimp of 12kV but because the devices fitted are normally rated at 6kVimp or 8kVimp the assembly when complete can only be rated at 6 or 8kVimp depending on which devices are fitted.

Register to Reply
Participant

Join Date: Nov 2015
Posts: 1
#8
In reply to #7

Re: Rated Short-Time Withstand Current(Icw) & Conditional Short-Circuit Current(Icc)

11/06/2015 12:53 AM

Thanks for the discussions.

For accepting an LV Switchboard, are both Icw and Icc are required or any one of the 2 in the verification test is acceptable? IEC 61439-1 requires one or more of the 2.

I have recently come across a situation, the specification requires a low voltage switchboard with rated voltage 440V, 100kA/1 sec. The Manufacturer is able to provide a verification report for a switchboard rated at 415V, 100kA/1 sec. (ASTA test report indicates Icw 100kA/1sec and Icc 100kA/1sec @415V) For Icw, voltage is not the criteria, however, for Icc, the test voltage must be 1.05 times the rated voltage. Therefore, a switchboard tested for Icc at 415 V will not meet 440V specification.

Much appreciate your input to the above.

Register to Reply
Register to Reply 8 comments