Over Current And Earth Fault Relay

09/23/2014 1:24 AM

Dear Electrical Engineers,

In case of 4 pole breaker as Transformer main incomer in the LT panel, whether CT is required or not, in neutral bus to connect to the 3 PHASE OVER CURRENT &1 EARTH FAULT RELAY.

Kumaar Swarit,

Hyderabad

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#1

Re: Over current and Earth fault relay

09/23/2014 1:55 AM

What does your local code specify? You should know your codes better than us, we don't even know what country your from.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4
In reply to #1

Re: Over current and Earth fault relay

09/24/2014 2:22 AM

The usage of neutral CT for o/c and ef relay depends on type , make of relay configuration and wiring to the relay.

For REF applications the neutral CT is required for general 2 element OC and one element EF, neutral CT not required. For sensitive earth fault protection separate Neutral CT is required. It all depends on type of protection and application.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
4
Participant

Join Date: Aug 2014
Posts: 2
Good Answers: 1
#2

Re: Over current and Earth fault relay

09/23/2014 2:40 AM

A neutral CT is a device which measures the current flow in the neutral conductor. In a three phase star system each phase current returns to neutral, but the three phases cancel each other out, resulting in effective zero current in the neutral.The neutral CT is used to detect the imbalance current in the system caused by a ground fault or by some failure in one of the phase loads. Thus CT in neutral is essential to actuate Earth Fault relay

Register to Reply Good Answer (Score 4)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Over current and Earth fault relay

09/23/2014 11:57 PM

One post, one GA ! We need more people like you here

i have a doubt. i am into component design, and in a RCCB, we pass all four wires through a core-balance CT. So the vector sum of the three phase currents AND the neutral current if any, acts on the CT. Any residual current has to be an earth leakage, and the RCCB trips. Now here in this case, if there is an unbalance in the three phase loading, some current will flow through the neutral. Will the EF not trip in such a case (No earth fault, but just an unbalanced load) ? Granted that we are talking about the main ACB of a transformer, but still....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster #1
#6
In reply to #2

Re: Over current and Earth fault relay

09/25/2014 2:44 AM

Dear Gupta Ji,

Thank you so much for adding your view, and me too accept the same .

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jun 2014
Posts: 19
Good Answers: 1
#5

Re: Over Current And Earth Fault Relay

09/24/2014 8:22 AM

Hi, my take on this..... Over-current protection and earth fault/leakage protections are based on different principles. Earth fault protection - vector summation of currents in all live conductors ie. 3 phase + 1 neutral, by using individual CTs, or in the case of earth leakage relays or breakers, usually using one zero sequence transformer (ZCT). Over-current protection needs individual CTs in whatever phase/neutral you intent to protect. Hope this explanation helps. Regards.

Register to Reply
Participant

Join Date: May 2012
Posts: 2
#7

Re: Over Current And Earth Fault Relay

09/26/2014 10:51 PM

if u are using inbuilt mccb you dont need ct .

Register to Reply Off Topic (Score 5)
Register to Reply 7 comments