What are the problems that may be encountered if we run 11KV, 2600A Bus duct in the underground in an oil and gas refinery from outdoor TR to indoor Switchgear ?
Re: Transformer Busduct
09/27/2014 12:40 PM
Accumulation of either water or flammable vapors in a low-lying space.
09/28/2014 2:53 PM
Inadvertent transfer of heavier than air flammable gasses from the hazardous area to the safe area.
Good Answers: 97
09/29/2014 3:21 PM
Conforming to the regulations for Class 1 Division 1 might be considered a "problem"
If life is considered "Cheap".
There are additional regulations for passage from outdoor to indoor as you describe.
CRTL-Z
Good Answers: 116
05/18/2021 2:21 PM
Entry of flammables/water already mentioned by other Posters to bus duct where flashover occurs possibly causing explosion/loss of service/life.
Condensation within a "sealed" bus duct can lead to flash-over, unless there are drying agents or enough heat to keep humidity low - not clear if transfo/busbar carries high LV current or is standby.