Hi,
We would like to use the Shunt Resistors for Measuring the AC Current, we have tried the 100 Amp / 75 mv shunt resistor along with Yokogawa WT 1600 to measure the current of an Induction Motor of 11 KW, 460 Volt on No Load as well as on Full Load.
The results were compared with the Same Instrument (Yokogawa WT 1600) and with same motor with the Hall Effcet CTs. We have found that Both the Readings are near Exactly same.
Now we would like to convert all measurement system from old type wire wound CT based to Shunt Resistor based..
Measurement errors due to Temp Drift would be the Improtant aspect to be kept in mind while designing such system. We would like to know the more Pros and Cons of using Shunt Resistance instead of Wire Wound CTs for AC current Measurement.
we are desiging the system which usees Shunt Resistor of 0.1 Accuracy Class as the system accuracy should be within 0.2 Class.
Your valuable inputs about such trials are improtant for us before switching over from CTs to Shunt resistors for AC Current Measurement.
Re: Shunt Resistors for AC Current Measurement
09/29/2014 3:56 AM
One thing you have to take in care that Isolation is not possible this would be very useful for fresh usages which you go to design or develop infuture
Re: Shunt Resistors For AC Current Measurement
09/29/2014 10:40 AM
The lack of isolation can easily create unexpected complications that cause circuitry to fry. To provide proper isolation one can quickly lose all implied accuracy of using a shunt resistor instead of a current transformer. You can also have bandwidth complications that your CT were limiting that a resistance won't.
If I were you I'd use one of the Yokogawa CT calibrated to be used with this power meter. This way everything stays calibrated.
09/30/2014 12:04 AM
Hi Vishram,
Very good comments here and you have done some good homework. I would add the following to think about.
1. Do a three point current plot. Run and measure your motor under load at 10% and 50% of full load to make sure your shunt is linear. Some people use a precision analog HP AC voltmeter for reiteration. This will also check for current harmonics the Yoko may not see.
2. Some new AC Motor Drives can reach 0.1% accuracy at 10% of full scale internally with no external components and provide you with a usable output to monitor each phase for current balance.
3. Temperature may be a factor depending on the shunt design you select.
09/30/2014 9:30 AM
Isolated Hall probe shut ICs are available from Avago / Winson/ Siliconlabs - pl see Google and search. I do not see any difficulty in using these as long as the sensor is rigidly mounted with respect to the current cable- relative positions are imporatnt as it is measuring flux density due to the main current.
Good Answers: 58
09/30/2014 10:50 AM
I'm not sure I fully comprehend the details of what you are trying to accomplish. However, I have had related problems and for 10 years have been using Rogowski coils and electronic integrators with almost utter reliability. This method has been superior to shunts and Hall effect devices for our high current welding applications.
09/30/2014 7:21 PM
Here is a link to some useful information on the various methods of current measurement and the features of each.
http://fwbell.com/downloads/files/Methods_Current_Measurement.pdf
09/30/2014 8:49 PM
If your goal is to electrocute someone, then go ahead and uses resistors.