Cable Size for Star Delta Staring Motor

09/28/2014 4:22 AM

I have 37kw 3 phase,415v ,50Hz operating motor.

I am useing star delata starter for same.

full load current for motor near about 64A.

1.Can i use 3Core 6 sq.mm AL cable having 50A current capacity?

2.there are two run for motor so 64A will divide?

Please guide me thanks

Register to Reply
Pathfinder Tags: cable size
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: cable size for star delta staring motor

09/28/2014 4:54 AM

No.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: cable size for star delta staring motor

09/28/2014 12:33 PM

I can't answer your cable size exactly, we have different standards, let alone different dimensions and units of measure. But here, you are allowed to use 58% of the motor FLC rating for sizing each of the 6 conductors on a wye (star)-delta starter. That is because in wye, the current will be 58% of normal through both sets of conductors, then in Delta it will split evenly but if the conductors were sized at 50%, it would be too small for the Star connection.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: cable size for star delta staring motor

09/28/2014 3:04 PM

Please consult your local electrician who can offer and install a safe solution for you.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#4

Re: Cable Size for Star Delta Staring Motor

09/28/2014 10:44 PM

In India, anything is possible, but apart from being undersized to start with, the length of the cable run and method of enclosure would also be a deciding factor.

Not sure that 6mm² Al would be rated at 50 amp even over there, other than maybe as an open aerial conductor, and that's a small cable for an aerial

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Cable Size for Star Delta Staring Motor

09/28/2014 10:55 PM

Go through catalog of reputed manufacturers like Telemecanique etc who gives not only cable sizes but also fuse/cb, oc relay,contactors sizes too.For cable sizing you need to consider de-rating factors like enclosure,grouping etc too.

__________________
pnaban
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: Cable Size for Star Delta Staring Motor

09/29/2014 12:26 PM

Dear Mr. Anupam Diwan,

The normal full load current for 37 KW Motor, will be approx. for 70 Amps, where as you have mentioned as 64 Amps. O.K.,

The Starting Current will be about 3 to 4 times for few seconds, and gradually reduce and changes to delta, again a small kick load experienced where the current may exceed 70 Amps level and current will reach below 64-70 Amps Level.

For any cable the de-rating factor will have to be duly considered, Hence 6 Sq.MM Al. Cable cannot handle this current.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#7

Re: Cable Size for Star Delta Staring Motor

09/29/2014 12:58 PM

Which national installation standard are you intending to use, Mildred?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8

Re: Cable Size for Star Delta Staring Motor

09/29/2014 9:49 PM

Cable from cb to starter should carry FLC while that from starter to motor carries only 58% of FLC.Apply derating factors & select a cable(1c or 3c).

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9

Re: Cable Size for Star Delta Staring Motor

09/29/2014 10:28 PM

"Please guide me thanks"

Consult the millions of wire sizing tables available at the IHS;

Reference Library

Otherwise, Go directly to jail. Do not pass go, do not collect $200.00.

Register to Reply
Anonymous Poster #1
#10

Re: Cable Size for Star Delta Staring Motor

10/19/2014 9:08 AM

To understand more about cable selection, pls check out here http://www.psa-outline.com/cable-selection/

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Cable Size for Star Delta Staring Motor

01/10/2024 4:26 AM

British Standard 7671.

If in doubt, consult a qualified local Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Crabtree (1); dhayanandhan (1); jack of all trades (1); JRaef (1); lyn (1); pnaban (2); PWSlack (1); spades (1); Tornado (1)

Previous in Forum: Bandpass Filter Respone   Next in Forum: Shunt Resistors For AC Current Measurement

Advertisement