Anonymous Poster #1

Star Delta Cable

09/29/2014 2:50 PM

I have one question.

star-delta starter motor have 2 run cable.if motor full load current is 40A so it will divide in two part i.e 20A in main contactor and 20A in star or delta depend upon running?

please confirm

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Star Delta Cable

09/29/2014 3:14 PM

I have one question. Why do you want to use underrated contactors?

__________________
Good moaning!
Reply
Active Contributor

Join Date: Sep 2010
Location: India
Posts: 11
#4
In reply to #1

Re: Star Delta Cable

09/30/2014 3:04 AM

its not about contactors its about cable.what i want to know is actual current in both cable ie connected to main contactor and connected to star (starting)/delta (running) contactor.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Star Delta Cable

09/29/2014 4:39 PM

I do not understand your question but if you have 2 cables of the same size and length, they will each carry 1/2 half of the load. Is this what you wanted to know?

Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Star Delta Cable

09/29/2014 8:50 PM

No, because if you are starting in Star, the current will be 58% of normal at that time, so everything needs to be sized for that as a minimum and in accordance with your local codes for proper sizing (for example here in the US we must over size at 125% of that value).

Then it is fine for when it is connected to run in Delta, where yes, the current will be evenly split between the two sets of cables.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Star Delta Cable

10/01/2014 2:18 PM

As jraef explained, if we shall follow NEC Art.430.22 Single Motor (C) Wye-Start, Delta-Run Motor then the cable ampacity of the cable in the Wye-Start has to be at least 1.25/sqrt(3)=0.72 *Irated.[Irated as per Table 430.250 Full-Load Current, Three-Phase Alternating-Current Motors].

Since the transit from star to delta is short -usually-the ampacity could be less.

IMO NEC considers the ampacity for continuous load [no switch to Delta?].

If there are two parallel cables connected to the main motor terminals-and it is not the cable connecting the star point or the other for delta connection-and if the cable are identical-same conductor, same length [same temperature?]-then the main supply current will split in two equal parts.

__________________
Julius
Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Anupam Diwan (1); Crabtree (1); JRaef (1); wareagle (1)

Previous in Forum: NEC Split Air Conditioner   Next in Forum: DG Set

Advertisement