Heating Elements Arrangement.

10/16/2014 3:37 AM

Hi friends, I have 3 phase electrical heater with 18 silicon carbide heating elements of 9kW each and Thyristor unit is used for controlling the elements. Since i'm new to this heating concept, i have no idea on the elements arrangements like delta, open delta, star and star with neutral. Please can any help me to find the best possible element arrangment of elements and thyristor control methods?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Heating elements arrangement.

10/16/2014 5:12 AM

There are several series/parallel combinations in which these elements could be connected. What is the rated voltage of each element? What is the available supply voltage?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2014
Posts: 7
#4
In reply to #1

Re: Heating elements arrangement.

10/17/2014 8:10 AM

mains supply = 415VAC, 3Ph, 50Hz

Elements voltage = 240VAC

Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #4

Re: Heating elements arrangement.

10/17/2014 12:20 PM

Connect in star: (6) elements in parallel between phase A and neutral, (6) in parallel between phase B and neutral, and (6) in parallel between phase C and neutral.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Heating elements arrangement.

10/16/2014 7:57 AM

Have you tried the manufacture? They would have a wiring diagram.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#3

Re: Heating Elements Arrangement.

10/16/2014 1:22 PM

Here we need a crystal ball because we don't know enough about the discussed devices. Like others said, how are the elements arranged? Which is the nominal voltage per element? Is there one single or several thyristor units? Phase-angle or 0-volt controlled burst-fired? Or simply a basic static relay?

Remember that unlike mechanical contacts, semiconductors alone don't allow a galvanic separation.

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#5

Re: Heating Elements Arrangement.

10/17/2014 9:50 AM

"I have...." Look at it and see how it is connected. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#7

Re: Heating Elements Arrangement.

10/17/2014 2:17 PM

Connect them in delta, in banks of 3 branches of two series heaters each; that way if you have a burnt element the voltage won't increase accross the others, making them fail in a very short time, see:

Please dont connect them in star, it will cost you a lot of money in down time and heater replacements.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: Heating Elements Arrangement.

10/17/2014 3:42 PM

That will reduce their power output to less than rated. (207.5/240)2.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#9
In reply to #8

Re: Heating Elements Arrangement.

10/17/2014 4:57 PM

Exactly, which will make them slightly "under-used" for the application, with the plus that you avoid voltage unbalance accross the series banks due to a unit going bad.

You hardly ever demand 100% of anything's capacity anyway.

I'm appalled, you read my post, thanks !

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #9

Re: Heating Elements Arrangement.

10/17/2014 5:41 PM

In any scenario, an open element will increase the resistance of its sub-network, and thereby unbalance the voltage upward. I haven't calculated whether this would be worse in the parallel-star arrangement versus the series-parallel delta scheme.

And then, one wonders what the geometric arrangement is, and the various jumper links that would be needed.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2014
Posts: 7
#11

Re: Heating Elements Arrangement.

10/21/2014 12:49 AM

Thanks friends..

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Circuit Breaker (1); ozzb (1); Plimos (1); sureshkumart (2); Tornado (4); Yahlasit (2)

Previous in Forum: Capacitor Fuse Blowing   Next in Forum: Rotational Angle

Advertisement