Anonymous Poster #1

Types of MCCB

10/23/2014 6:30 AM

Hi,

MCCBs protects from overloads and earthfaults. What all types of MCCB are available?What is class C and class D MCCB?

Regs,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Types of MCCB

10/23/2014 6:38 AM

What is Google?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Types of MCCB

10/23/2014 6:51 AM

just not getting to the point answer on google...!!

Regs,

Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3
In reply to #2

Re: Types of MCCB

10/23/2014 8:45 AM
__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply Score 1 for Good Answer
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Types of MCCB

10/23/2014 11:56 AM

C and D typically refer to trip classes but not on MCCBs, those are used on MCBs, a different device. MCCB is for Molded Cse Circuit Breaker, typically high interrupt capacity and adjustable trips (although not all the time if in North America). MCB is Miniature Circuit Breaker and the trips are always fixed, so f you want different trip carachteristics, you order them that way, by using ABCDK etc denoting the trip curve you want.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Anonymous Poster #1
#5
In reply to #4

Re: Types of MCCB

10/23/2014 1:37 PM

1. By adjustable trips of MCCB, are you referring to different trip class: like 10A, 10, 20, and 30?

2. What do you mean by: trips are always fixed in MCB? I am aware that B, C, D, K, Z and S curve exists in MCB.

Regs,

Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Types of MCCB

10/23/2014 2:34 PM

Trip class is different and has to do with motor protection. MCCBs can have thermal - magnetic trips, or just magnetic. In IEC breakers both will be adjustable within a range, for example the thermal trip on a 50A MCCB can be adjusted from 25 to 50A, and the magnetic trips from 100 to 500A. On a magnetic only version, there are no thermal trips, because they are for use in conjunction with a motor starter thermal overload relay anyway. On MCBs, nothing is adjustable, the thermal trips and magnetic trips are fixed. If you want a different response rate to a short circuit or over current, you select the different curves, ABCD etc, by purchasing a different breaker part number based on one of those curves.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 3)
Anonymous Poster #1
#7
In reply to #6

Re: Types of MCCB

10/24/2014 12:17 AM

Thanks JRaef:

>>thermal trip on a 50A MCCB can be adjusted from 25 to 50A, and the magnetic trips from 100 to 500A.

- is this 25 to 50 A and 100 to 500 A range for 50 A MCCB applied to say 100 A MCCB(and all other MCCBs) by simple ratio ie. thermal trip 50 to 100A; and magnetic trip from 200 to 1000A ??

I have 17 kW motor, giving current of 24.5 A FLC.

1. Starting current for DoL starting would be: nearly 245 A. (10 times)

2. Starting current for Star Delta starting would be: 123 A. (5 times)

3. Inrush currents would be for star delta starting (as I have studied): 490 A. (20 times).

4. 24.5 A FLC would give a MCCB of 61.25 Amps (so 63A MCCB can be selected as per standard ratings), and conductors should be of 30.6 A.

is this okay?

Regs,

Reply
Anonymous Poster #1
#8
In reply to #7

Re: Types of MCCB

10/24/2014 1:25 AM

Hi,

1. What is the meaning of "frames" of MCCB. I came across it when studying MCCBs catalogue.

2. What is four pole with switched neutral MCCB ie. 4PwSN ?

Regs,

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Types of MCCB

11/03/2014 10:05 AM

Why do 20 Questions (rhetorical question)?

Please put all the questions in the original post next time, as it enables a quicker response to arrive.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#10
In reply to #8

Re: Types of MCCB

11/03/2014 1:15 PM

Switched neutral means that you've a 4th pole which is switched but not protected, it's explained in some other topic. Switched neutral is often optional but in some cases it's mandatory (depends on local regulations). Of course it's forbidden to switch a PEN.

Protected neutral means that the neutral is protected like a phase, though in some cases it can be rated below or above 100%. Protected neutral is interesting if there's a high amount of non-linear loads (harmonics can lead to neutral currents exceeding phase currents).

BTW There are also MCCB (Moulded Case Circuit Breakers) featuring a specialized motor protection release, they can be used without thermal relay and the good ones are also sensitive to phase unbalance (but one tripped you must switch on again manually unless you've an expensive magnetic or, for the larger sizes, motor drive; while thermal relays often have a manual/automatic reset selector).

Reply
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); JohnDG (1); JRaef (2); Plimos (1); PWSlack (1); Tornado (1)