Running of a 500V Compressor Motor On 400V

10/30/2014 5:10 AM

Dear Friends;
We have a screw air compressor Atlas Copco GA808 which has a 75KW 500V motor runs on star delta. As we have 400V power supply system, so initially we want to run this compressor on 400V to test it with load. So what will happen with motor when we run it on 400V? Obliviously its torque will be reduced but for how much percentage?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#1

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 8:41 AM

Your real concern shouldn't be the torque drop, but the motor overheat.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 8:45 AM

its going to cook the motor, stop being an idiot and install the proper t-former

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#3

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 9:12 AM

How about the frequency? What do you have? What is the motor designed for?

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 10:49 AM

500VAC is not a standard for anywhere in the world. My first inclination is that you do not have your facts straight. Either that, or Atlas Copco is doing something very odd with regard to playing with the Volts /Hertz ratio of the motor, but you did not post the frequency data on the motor nameplate.

Option 2, you are ASSuming the motor voltage by reading the voltage rating of a VFD that is controlling the motor. VFDs come in different "classes" of voltage ratings, and some mfrs, such as ABB whom Atlas Copco like to use, use "500V class" as a way to separate drives that are rated for 380-480V input as separate from 400V class, rated from 380-440V input. That would not really apply to the motor, but if you are reading the VFD nameplate and not the actual motor, you might be fine, but you also might need to adjust programming in the VFD.

Option 3, slightly less plausible, is that for whatever reason, this was built with a 500V DC motor. 500VDC much more common in the DC world, but DC motors are uncommon on compressors because of the high duty cycle and required maintenance.

Go back and read the ENTIRE motor nameplate, then maybe we can help.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 11:36 AM

500V is used in mines and quarries

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #4

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 12:50 PM

I'm trying to get my head around a star-delta DC motor, to say nothing of the OP's motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#16
In reply to #6

Re: Running of a 500V Compressor Motor On 400V

10/31/2014 7:25 AM

Puzzeled too. A DC motor on the compressor! All the ones I have checked out ar 400V AC motors. Is this some special application or a home work question or a misread spec plate?

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#18
In reply to #4

Re: Running of a 500V Compressor Motor On 400V

10/31/2014 1:31 PM

Dear Mr.JRaef,

It is true that 500 Volts is not standard, but one company formed about 200 years back in London, still ha s branch and working in India, it is using still 500 Volts.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#7

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 3:55 PM

When you start upon a star, makes no difference where you are, if your voltage is too low, the smoke comes out.

Jiminy Cricket.

__________________
CRTL-Z
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 4:12 PM
  • I'm trying to get my head around a star-delta DC motor, to say nothing of the OP's motor.

D'oh! <slaps forehead>

Missed the "star-delta" thing. Damn these eyes...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 4:29 PM

This sounds like the rating in star mode, the delta mode probably 380v....we need complete info off starter and motor....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #9

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 6:13 PM

Nah, 380 x 1.732 = 660V. There are 690Y400V motors out there for that purpose. But nothing about 500VAC works out mathematically with any world standard for AC distribution voltages.

But here is something that does sort of work out, based on my earlier comment about Atlas Copco "playing with V/Hz ratios".

A motor designed for 415V 50Hz (not 400V or 380V) will have a V/Hz ratio of 8.3:1. if you want full torque from that motor at 60Hz, you would need to supply that motor with 8.3 x 60 = 498V, pretty damned close to 500V. So IF the motor nameplate truly says "500VAC 60Hz" on it, then it will be fine for 415V 50Hz, and if tolerance is +- 10%, 400V 50Hz should be OK as long as the supply does not dip lower than 373V, about 6-1/2%.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#11
In reply to #10

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 8:50 PM

Indeed while 400 V 50 Hz and, for some larger more recent drives, 690 V 50 Hz, are the most common 3-phase low voltages in continental Europe, 500 V 50 Hz 3-phase is still used in some large industrial plants (e.g. cement and chemical plants). As they can't replace thousands of motors easily, there's now typically a mix of 500 V 50 Hz and more recent 400 V 50 Hz as well as in some cases 690 V 50 Hz in the same plant. In some countries the same plugs can be either 400 V or 500 V (mostly legacy connector systems). 500 V 50 Hz is phased out where possible but will likely coexist with 400 V 50 Hz for quite some time.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#12
In reply to #11

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 9:48 PM

We had an old paper making machine got from Germany. The voltage of this machine was 500V 50HZ and so the compressor is also of 500V 50HZ and has a star delta starter. The machine has become right-off and the compressor is spare. Designing a step up transformer from 400 to 500V is a secondary concern.

Every time comments by Tornado are very nice.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13
In reply to #11

Re: Running of a 500V Compressor Motor On 400V

10/30/2014 11:41 PM

When I started quarries 40+ years ago all our plants were on 525V. Later as new kit came in the plants ran with a mixture of 525V and 433V.

We did toy with the idea of converting them to all 433V, we gave that idea up as an expensive pipe dream. The shear cost of 1500 new motors never mind the new larger cabling consigned the idea to the bin.

I was involved in the first dual voltage system so it became 2nd nature knowing what was on each voltage.

The OP mentioned that this motor was from a printing plant. The last printing plant I worked on again had two systems. This time 433V and 380V. The plant services being to UK specifications, the presses to Belgian and German.

The foundry I worked at used 660V and 433V.

It's not all that unusual in old industries for dual voltages to exist side by side. It's just a bit mind blowing when you first come across it.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#14

Re: Running of a 500V Compressor Motor On 400V

10/31/2014 4:26 AM

500V motor working at 400V (80% of 500V) will be able to give ~64% torque.

If this is good enough for the compressor, I don't think the motor will have any problem.

__________________
Raghunath
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#15

Re: Running of a 500V Compressor Motor On 400V

10/31/2014 6:40 AM

The 'load' is caused by the compressor screw element. This relates directly to the speed and pressure. The motor is matched to deliver the power at full load.

Running at 400 volts will reduce the power to 64% of 75kw = 48kw (it's to do with V2). The motor will therefore become overloaded when trying to deliver little more than half the rated airflow.

The screw element needs to run at half speed to avoid overload, or at half rated pressure.

The latter easy to achieve by setting the max pressure controls, but not very useful because you probably need the full air pressure for your pneumatic machines to work properly.

Halving the speed of the screw by changing pulley wheels would be somewhat easier if belt driving, but your compressor is probable direct coupled through a gearbox, making it impossible.

If you do not reduce the screw speed or pressure, then the motor will try to match the air consumption, and anything much over half load will cause the motor to 'slow down' pulling more current than designed, and soon to overheat.

For testing purposes, ie, running up to speed and pressure, should present no problems, but as soon as air is consumed, over which you have little control (I guess) then things will start to go wrong if unattended.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Power-User

Join Date: Jun 2009
Location: Santa Cruz, CA
Posts: 158
Good Answers: 5
#17

Re: Running of a 500V Compressor Motor On 400V

10/31/2014 10:47 AM

If you Google the "Atlas Copco GA808" you will find several descriptions rating it at 400v.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#19

Re: Running of a 500V Compressor Motor On 400V

10/31/2014 1:38 PM

Dear Mr.signode,

The motor will draw more current and windings will get over heated. The power at 400 V will be (400/500)^2, to that of power at 500 V, and hence (400/500)^2 = (0.8)^2 = 0.64 and hence the current drawn will be 1/(0.64) = 1.5 Times more and there fore winding will get over heated/burnt.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#20

Re: Running of a 500V Compressor Motor On 400V

10/31/2014 2:10 PM

Obviously ignored by many so I shall point this out. How on earth can he test this compressor on load, and obtain meaningful results of any use if the the required voltage is 500V? Torque reduction or not, his test is totally without foundation and any result, has no value.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#21

Re: Running of a 500V Compressor Motor On 400V

11/01/2014 10:47 AM

It is an old compressor. See:

http://www.machinerypark.com/stationary-compressor-atlas-copco-ga-808-used-be-8790

It seems to me the rated voltage is 400 V [it is not 500V!] 50 Hz.

It could be your network rated is 480 V 60 Hz. Then it may work fine.

__________________
Julius
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#22

Re: Running of a 500V Compressor Motor On 400V

11/10/2014 1:22 AM

Dear Signode, Can we request for the nameplate photograph...

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); bigg (1); chaterpilar (1); dhayanandhan (2); Fredski (1); horace40 (1); IQ (2); JRaef (3); Plimos (1); raghun (1); Signode (1); SolarEagle (1); tommm (1); TonyS (2); Tornado (1); Unredundant (1); Yahlasit (1)