10/31/2014 3:09 PM

Dear Friends,
I need technical solution for my problem;
Specification:
I have two motors, type:
1. HCT/ATEX 45-2T-2 (R/MIN=2800), (400V-3,60A), (KW-1,50)
2. HCT/ATEX 45-2T-3 (R/MIN=2860), (400V-5,00A), (KW-2,20)
Also, every motor has its own inverter:
Inverters are from INVERTEK DRIVES (Optidrive).
My project is to provide thoose two motors working in first (lower speed) all the time , and sometimes they need to work in second speed (higher - maximal possible).
Those speeds must be provided by changing frequency with inverter.
My questions are:
1. How to know which maximal frequency (Hz) are motors made for? - ( I think maximal frequency would be the higher speed)or they can work on any frequency?
2. Also how to make electrical diagram correctly ( If I have inverters; do I use only delta connection or I can use only star connection. Or I need to use star for start and delta for running?
3. Can somebody help me to design electrical diagram?
I hope you can understand my problem, also I will be very happy if somebody can solve my problem, I am affraid of making false wiring diagram.
With kind regards,
Joe
9

Register to Reply
Pathfinder Tags: Atex motors delta inverter star
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Inverter, Atex motors, star, delta

10/31/2014 5:00 PM

Please go and talk to an electrican who has basic control system knowledge on how to work with frequency drives. You have way to much to learn. This is a simple project. Let someone else take it on.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#2

Re: Inverter, Atex motors, star, delta

10/31/2014 5:20 PM

I apologize for not reading in detail the motor descriptions but if ATEX compliance is required, depending on the zone specific requirements must be met and it's something for specialists as if something goes wrong there will be serious liability issues.

I won't provide detailed solutions because it would end in a longer discussion and especially ATEX-conform design is not always that simple. Many supposedly ATEX-conform installations are indeed not fully conform, very common errors are for example wrong cable glands, cable routing errors of intrinsically safe circuits, ia vs. ib confusion, inappropriate motor protection, etc. And to make things even more complicated even experts don't always agree on how to define zones.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Inverter, Atex motors, star, delta

10/31/2014 9:29 PM

You won't get any help here.

"ATEX" is a French acronym meaning "Atmosphere Explosible", and encompasses a series of standards pertaining to equipment and personnel within hazardous locations.

By having no knowledge of the requirements and certainly no idea of the life ending potential of the job to hand you are a walking time bomb.

Seek professional, qualified, certified local help who is aware of the dangers of, and requirements for, electrical installations in explosive environments.

Sadly, you probably won't be one of the casualties if you proceed using advice gathered from unknown strangers on an anonymous forum.

Register to Reply
Member

Join Date: Oct 2014
Posts: 7
#4

Re: Inverter, Atex motors, star, delta

11/01/2014 5:18 AM

OK,
I get you technical charactertistics of fans,also maximamal airflow (m3/h) for every fan is:
MAX 1. 10650 m3/hMAX2. 12750 m3/h
I realised that with fvd I will use only one type of connection or star or delta.
If I want provide those two maximal airflows, which type of connection should I use? (What frequeny would it be?) If I want half (m3/h)/2 I change only frequency; nothing else?
Summary which type of connection and what frequency would it be for lower speed, what frequency would it be for higher speed?
Do you need any additional informations to provide me an answer?

Register to Reply Score 2 for Off Topic
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#5

Re: Inverter, Atex motors, star, delta

11/01/2014 6:52 AM

The first thing would be to know the zones as well as the type of the involved flammable gas or gases (if it's gas). From there you can check if the planned equipment is suitable or not, see the rating plate, the indicated ATEX specifications follow very strict rules.

Even if you use an approved drive you still have to check that the way you operate the motor does not represent a risk. Even when using only ATEX components with the required approval for the intended use you must still follow strict design rules.

Also it's not only about the electrical part, the whole system must be explosion-proof as explosions can also have non-electrical origins (e.g. mechanically created sparks or overheated parts).

But as said, unless your're a seasoned ATEX specialist you'd better hire an external consultant.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Inverter, Atex motors, star, delta

11/01/2014 7:47 AM

Chances are, he may be in an environment where he is the consultant. We see a lot of that here.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2014
Posts: 7
#7

Re: Inverter, Atex motors, star, delta

11/01/2014 10:05 AM

Forum is here to ask stupid questions and answering on them correctly or incorrectly.
There is no reason for arguing...
Who know is it my school project maybe?
Does anyone from here can answer me on question? If there is no enough informations please ask me... Do not think on ex zone vents are ex but not in the ex zone.
I need simple answers... Frequency range for my needs, and connection star or delta.
And comments if you have positive please.
Kind regards

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Inverter, Atex motors, star, delta

11/01/2014 10:10 AM

I am positive that you need to find someone to educate you that speaks your language and knows your level of knowledge.

We don't do homework here.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #7

Re: Inverter, Atex motors, star, delta

11/01/2014 10:26 AM

The motor nameplate should show what possible voltages may be connected in either star or delta. Your 2800 rpm motors are presumably 50 Hz. Full rated fan flow should be at that speed/frequency. Half flow will be at half speed/frequency. Most VFDs have ways to program preset speeds, which can be selected by one or more switches.

As others have noted, wiring methods, cable gland sealing, etc., must be taken into account. I too urge consulting with knowledgeable persons.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2014
Posts: 7
#10

Re: Inverter, Atex motors, star, delta

11/01/2014 10:32 AM

Things you wrote me doesnt help me I knew them by myself. I am enough intelingent to understand someone who can help me.

I am not intersted in clasification of zone 0 1 2 ... Exd Exi Exe Exn equipment... Imagine you have that kind of motore how would you run it? You dont know the answer

Register to Reply Score 1 for Off Topic
Member

Join Date: Oct 2014
Posts: 7
#11

Re: Inverter, Atex motors, star, delta

11/01/2014 10:43 AM

Tornado

Thank you on answer.

I have no problem with vfd.

Its simple parametring 2 working frequency.

I am wondering only do I connect motor in delta or in star? What you think is better?

With frequency 50hz in any connection or star or delta I will have 2800 rpm am I right?

So higher speed is 50 hz, lower i need to find out.

I can connect it as star, and with frequency of 50 hz it will have 2800rpm and maximal m3/h.

Now how to know minimum frequency motor is made for?

Kind regards

Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #11

Re: Inverter, Atex motors, star, delta

11/01/2014 10:52 AM

What does the motor nameplate say? Most VFDs are probably connected in delta, but I know of no absolute requirement for that. The motor speed depends on the frequency, not on the voltage, but you need to be sure that the supplied voltage matches the motor requirements.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13

Re: Inverter, Atex motors, star, delta

11/01/2014 11:01 AM

<unsubscribes> Will listen for the explosion.

Register to Reply
Member

Join Date: Oct 2014
Posts: 7
#14

Re: Inverter, Atex motors, star, delta

11/01/2014 11:13 AM

Tornado,

Vfd and motor are compatibile.

I am not person who specified equipment I need only connect them. In first it was looking simple vfd cable motor connect and than change frequency.

But now i have guestions.

Which data from motor are you interested in?

It has to be simple. It is not a magyc to connect motor.

You need star and delta parameters?

Kind regards

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16
In reply to #14

Re: Inverter, Atex motors, star, delta

11/01/2014 11:32 AM

Your questions do not make any sense at all. You need to bail out and get knowledgeable persons involved.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#15

Re: Inverter, Atex motors, star, delta

11/01/2014 11:14 AM

At his point I'd suggest a nitrogen or CO2 inertization of his whole plant. :) :) :)

Goodbye

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#17

Re: Inverter, Atex motors, star, delta

11/01/2014 1:18 PM

Joe9,

The problem here is, as I posted in the other forum where you posted this question, that the very nature of your question demonstrates an insufficient level of knowledge to take on this project. The very fact that the motor is in ANY way associated with an ATEX environment means there are many more complex details regarding the use of a VFD for it, yet you are unfamiliar with even the most rudimentary elements of the task at hand. So in helping you, we become participants in a potential disaster. Even though we are essentially anonymous, we are nonetheless Engineers and cannot in good conscience and professional ethics, facilitate this.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#18

Re: Inverter, Atex Motors, Star, Delta

11/02/2014 2:19 PM

I have to ask but are your inverters installed in the safe area or the hazardous area?

Also, what do your variable speed drive manuals and application notes available off the manufacturer's website have to say about proper connection? Your question regarding this just seems odd as your connection depends on available voltage and what country you are in.

Contact the motor manufacturer if the available motor literature is of no help, especially if you want to overrun the motor(s) higher than the line frequency (50 or 60Hz).

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19

Re: Inverter, Atex Motors, Star, Delta

11/03/2014 9:18 AM

Either

  • seek training within the facility, or
  • delegate the task to someone who has received the training, or
  • both.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Oct 2014
Posts: 7
#20

Re: Inverter, Atex Motors, Star, Delta

11/03/2014 1:41 PM

Thank you very much on your answers.

Iam not a person who will do this. I just wanted to know how it works.

One person explained me detailed this problem. To me everything is clear I just wanted to know theory.

Some of you helped me to know but some of you not.

Question maybe looked funny because of my bad english. I even wasnt trying to be smart. forum use for sily questions. also when you were thinking that i want do this i get much more answers.

Kind regards

Register to Reply
Register to Reply 20 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jack of all trades (1); Joe9 (6); JRaef (1); lyn (3); North of 60 (1); Plimos (3); PWSlack (1); Tornado (4)