Foaming in Lub Oil

11/07/2014 12:10 PM

what happened if oil found inside the alternator( 35 Mw, 11 kv) windings ? can we run continuously run that machine ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#1

Re: Foaming in lub oil

11/07/2014 12:29 PM

Obviously you can't if oil is found where there should be none or if there's water in the oil.

How did you notice that? Leaking ol from the journals? Is there a pressure lubrication or are oil pumps only for circulation (cooling in heat exchangers)? Hydro turbine (vertical or horizontal shaft? How many poles?) driven or fast steam/gas turbine?

Foam could typically indicate water in oil, e.g. from heat exchanger leakage.

Is oil automatically monitored for water content? Are there traces of oil in the (primary where applicable) cooling water?

Are stator and rotor ground monitored? For those sizes it's usually the case.

IMO you'd rather stop the group immediately and check what happened, if not the problems will likely increase, typically ending in an way more expensive repair and longer down time than if a thourough diagnosis is performed without delay.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Foaming in lub oil

11/07/2014 2:42 PM

What does the alternator manufacturer's Operating Manual say? How did the phone call with the manufacturer's technical helpline go? When does the Service Technician arrive to assess and service the equipment?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#3

Re: Foaming in lub oil

11/07/2014 4:36 PM

When running a >40 MVA generator you're supposed to have some in-house knowledge, no?

Unless it's are relatively new unit, chance are that it has been partially disassembled during preventive maintenance so you should have own in-house documents about those overhauls.

Also there are many cases where older generators are still in use but whose manufacturer no longer exist. Of course there should be a detailed documentation available, usually it's mentioned in the contracts.

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Foaming in lub oil

11/07/2014 6:38 PM

What should have "...happened..." is that the person who authorizes operation under other than normal conditions should have been relieved of their position.

What you describe is a failure of the seal oil system to balance the lube oil pressure against the generator's internal pressure thereby allowing lube oil to travel along the shaft until it reaches the main body of the rotor where it is slung off onto the stator. This oil is a contaminant/solvent which will pick up any internal dust/debris and carry it into the cooling passages and clogging them up, and/or into the windings where it will cause tracking and ultimately winding failure.

The machine should be taken off-line until the root cause of the oil leakage is determined, and the entire internals of the machine thoroughly cleaned and degreased, including every cooling passage on both rotor and stator.

Failure to do so should result in dismissal of all personnel who authorized such operation, especially if the unit ultimately flashes-over internally.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Foaming in lub oil

11/07/2014 9:16 PM

Nothing to stop you running it to destruction. That way you'll know for certain what happens. Someone looking for a new job is one likely outcome.

I can't understand why you even ask the question.

Taking a 35MW generator off line is going to have financial repercussions but no where as bad as having it repaired after its failed.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#6

Re: Foaming in lub oil

11/08/2014 2:12 AM

What type of generator is it? In most probability it should be air cooled generator. What type of cooling does the rotor have? Is it direct cooed or indirect cooled? You have not stated how you have come to know that there is oil in the generator? Visual or alarm of liquid in the generator? How old is the generator? What type of insulation does the stator and rotor winding have? Is it class F?

Why utilities have hesitation in contacting the manufacture of the generator?

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

pcchatur (1); Plimos (2); PWSlack (1); RAMConsult (1); TonyS (1)

Previous in Forum: Selecting Circuit Breaker Size for Surge Protection Device   Next in Forum: Regarding 50N/51N Relay

Advertisement