Regarding 50N/51N Relay

11/07/2014 9:32 PM

Why 50N/51N can not see the phase to ground fault in between generator terminal to bus if connected to the ct's at ungrounded neutral side of a generator?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Regarding 50N/51N relay

11/07/2014 9:46 PM

So tell me, how much ground current flows through an ungrounded neutral?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#2

Re: Regarding 50N/51N Relay

11/10/2014 7:11 AM

generator neutral must be grounded in order to allow earth fault current to flow.

Register to Reply