Condensation Rate

11/29/2014 1:29 PM

Hi everyone,

I've finned tube heat exchanger work by saturated steam inside tubes, who to calculate condensation rate theoretically or by use a relation.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: condensation rate

11/29/2014 4:58 PM

There's a ton of variables to be worked out first.

Too many to list here, but I'll start.

1. What material is the heat exchanger?

Your turn.

2. _______

3. What is the length of the heat exchanger?

4. _______

You can take it from here.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2014
Posts: 17
#3
In reply to #1

Re: condensation rate

11/30/2014 2:22 AM

OK

2.Copper.

4. 110 cm

Register to Reply
Power-User

Join Date: Jan 2014
Posts: 206
Good Answers: 5
#2

Re: condensation rate

11/29/2014 11:49 PM

Saturated steam will give up (heat-exchange) about 1000 btu per lb of condensate. I'm not quite sure what your question is.

__________________
There are 10 kinds of people in the world.... Those who use binary code, and those who don't.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: condensation rate

11/30/2014 3:34 AM

Dear Mr.kahaten,

In continuation to Mr.lyn's Point and your reply to it, the following is needed.

1. What is the Pressure of the Steam. Temperature can be taken from the Steam Tables, since you have stated the Steam is saturated, as this Temp. has importance for the Approach Temperature.

2. What is the substance/material to be heated and its inlet temperature and desired outlet temperature, and its properties, such as Sp. Heat, Density, Flow Rate etc.

Outlet Temp. of the heated material can not be the same as the Steam Temperature. Infact it should be less by 5 to 10 Deg. C and this difference is known as APPROACH TEMPERATURE.

Since you have referred the steam is inside the copper tube, only the Latent Heat is transferred and the condensate will leave at the same temperature of the Steam.

Latent Heat will DECREASE as the pressure is increased - Refer the Steam Tables. The Latent Heat at Atmospheric Pressure of steam - at 14.696 psig, is 970 Btu/Lb., (OR) at 14.696 psig., 538. CHU/Lb., (OR) at 1.03 Kg/CM^2G is 539.9 K.Cal/Kg., (OR) at 1 bar 2257.9 KJ/Kg.

This Latent Heat will increase when pressure is less than atmosphere and will decrease when the pressure is above atmospheric pressure. Read the Steam Tables.

Further, the Heat Transfer and hence the Condensation of Steam depends upon several factors in which the properties of the substance to be heated.

DHAYANANDHAN.S

Register to Reply
Active Contributor

Join Date: Nov 2014
Posts: 17
#5
In reply to #4

Re: condensation rate

11/30/2014 7:40 AM

Thank you for your reply Mr.dhayanandhan

1.P= 1 bar (with it's Tsaturated)

2.The heat exchanger cooled by atmospheric air (Tin=25 Deg. C, Tout=91 Deg. C)

I agree with you in all your notes, and I know It's need more and more variable, but I don't know how to calculate it, so that I don't know which properties are needed.

thanks

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6
In reply to #5

Re: condensation rate

11/30/2014 10:00 AM

1 bar absolute or gauge? Do you mean you're heating the air because you need the hot air? Specific heat of air is about 1 kJ/(kg*K). You can work out the heat transfer rate from that.

__________________
Give masochists a fair crack of the whip
Register to Reply
Active Contributor

Join Date: Nov 2014
Posts: 17
#8
In reply to #6

Re: condensation rate

11/30/2014 11:19 AM

- Gage pressure.

- No, I want to calculate amount of heat transfer to air by (Q= m.cond.*hfg)

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#17
In reply to #8

Re: condensation rate

12/01/2014 2:46 AM

Well that's easy. You monitor one of the fluids, work out the difference in enthalpy between the inlet port and the outlet port, and multiply by the flow rate.

Next!

__________________
Good moaning!
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#7
In reply to #5

Re: condensation rate

11/30/2014 11:11 AM

Thank you Mr. kahaten for your reply.

I clear your doubt which is as follows:

The properties of fluid is density, thermal-conductivity, specific heat, compressibility etc. In your case, in the first posting, you have not referred air as the medium to be heated. Heat Transfer subject is a vast subject.

Now you have indicated Air (Specific Heat 0.28) is circulated and the inlet temp. is 25 Deg.C and heated to 91 Deg.C, but the Quantity of Air in Kg/Hour to be mentioned or given by you only. Also you have specified the Steam Pressure is 1 bar. Now the principle involved is

HEAT GAINED by AIR = HEAT LOST by STEAM.

Hence it can be expressed as , W x (Sp.Heat) x (T out - T in) = Q/ Latent Heat of Steam at 1 bar) where

W = Weight of Air in Kg.Hr (Or) Volume of Air in M^3/Hr., to be converted to Weight in Kg/Hr. Sp.Heat = 0.28 for Air, T out = 91 Deg.C, T in = 25 Deg.C, Q = Quantity of Steam at 1 bar and the Latent Heat at 1 bar is equal to 2257.9 KJ/Kg.

Therefore,

W x (0.25) x (91 x 25) = Q/ 2257.9 (Here the Radiation Loss of Heat is ignored which will be in the range of 5 % max. can be assumed)

In this equation 2 unknowns i.e., W and Q is there. Since you want to know the Steam in Kgs/Hr. Q is to be calculated and therefore you have to substitute the value for W. Once W is fixed Q can be calculated. Multiply Q by 1.05 to compensate for Radiation Loss.

Now I think I have made it clear, and you can calculate easily.

DHAYANANDHAN.S

Register to Reply
Active Contributor

Join Date: Nov 2014
Posts: 17
#9
In reply to #7

Re: condensation rate

11/30/2014 11:58 AM

OMG!

I did not imagine that there are people like you.

Thank you so much for your attention and effort.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#10
In reply to #7

Re: condensation rate

11/30/2014 1:45 PM

Not bad, but a couple of mistakes

You say Sp.Heat = 0.28 for Air. You don't give units, but that is about right for kcal/(kg*K) (in your equation you say 0.25, presumably a typo). But on the other side of the equation you have latent heat in kJ/kg. Also (91 x 25) should be (91 - 25).

And the total heat released from steam at 1 barg and 120°C is higher than the latent heat. Enthalpy is 2707 kJ/kg so heat released on cooling to water at 25°C = 2707 - 25*4.2 ~ 2600 kJ/kg. Link below gives steam data.

http://www.spiraxsarco.com/Resources/Pages/Steam-Tables/saturated-steam.aspx

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#15
In reply to #10

Re: condensation rate

11/30/2014 9:38 PM

Dear Mr. Codemaster,

You are absolutely RIGHT, thank you for your comment.

It is true, 0.28 is specific heat, ( in Btu, should have been in KJ/Kg.) and the other one is Typing Error.

Thank you once again, and in future I will excercise extreme care, since I should not misguide the person who is attempting to learn.

DHAYANANDHAN.S

and Also, Dear Mr.Kahaten,

Pl. note the comment of of Mr. CodeMaster and make the correction please.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#18
In reply to #15

Re: condensation rate

12/01/2014 4:40 AM

No problem, we can all make mistakes! My comment on heat released from the steam isn't quite right either, or at least needs clarifying. It assumes the condensate cools to the temperature of the incoming air, 21C, but this is only the case for a big heat exchanger. Otherwise the condensate temperature is higher and heat/kg lower. OP needs to assume (or measure) the temperature, or just use latent heat as a safe figure.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11

Re: condensation rate

11/30/2014 2:28 PM

This has taken on the look of homework.

<unsubscribe>

Register to Reply
Active Contributor

Join Date: Nov 2014
Posts: 17
#12
In reply to #11

Re: condensation rate

11/30/2014 2:43 PM

Is there another method?

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#13
In reply to #12

Re: condensation rate

11/30/2014 2:53 PM

To do what? (if I might speak for Lyn, as he's unsubscribed )

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#19
In reply to #12

Re: condensation rate

12/01/2014 5:29 AM

Other than homework? You tell me!

__________________
Good moaning!
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14

Re: Condensation Rate

11/30/2014 4:46 PM

By far the key datum is the surface area of the heat exchanger. Unless I missed it, this has not yet been mentioned.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#16

Re: Condensation Rate

12/01/2014 2:16 AM

Read Temperature & Pressure downstream of your heat exchanger, then see steam stables(you will able to know if steam is under saturation curve, compressed or superheated, for such application it is designed to attain saturated liquid state) and consider below equation.

by a (flow meter) Mass(total) = Mass(vapor)+Mass(liquid) ; rate (kg/s)

Quality of steam x(%) =(v-vf /vg-vf) either you use (h-enthalphy) = Mass(vapor)/Mass(total)

The condensation rate is just Mass(liquid) at kg/s unit.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Register to Reply 19 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (4); Crabtree (2); dhayanandhan (3); kahaten (5); lyn (2); Noudge79 (1); Tornado (1); tribefan1952 (1)