Medium Voltage GIS

12/01/2014 1:10 PM

In 33kV modular type GIS, manometers as SF6 pressure monitoring device or SF6 gas density switch is better technique for monitoring the health of SF6 inside GIS. Or both of them are used in combination?

Regards

Register to Reply
Pathfinder Tags: Gas insulated switchgear
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: MEdium Voltage GIS

12/01/2014 2:23 PM

It depends on what is in the maintenance information you received when it arrived, Murphy.

__________________
Good moaning!
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Medium Voltage GIS

12/01/2014 6:29 PM

In an ideal gas, density and pressure are proportional. Therefore, either measures the other. Which do you think is easier?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Medium Voltage GIS

12/01/2014 8:28 PM

It would depend on the quality of the switchgear I guess. My experience with high quality SF6 insulated 33kV switchgear (selling, designing with, testing, training and commissioning) would be that the pressure monitoring device is enough.

If the switchgear is of low quality where leakage, moisture ingress, etc is a potential problem due to poor containment design or SF6 gas degradation due to harsh usage, environmental conditions, end of life (etc) then pressure monitoring alone may not be enough.

__________________
jack of all trades
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Medium Voltage GIS

12/02/2014 3:17 PM

A pressure monitor usually is just an absolute value device - it tells you the pressure no matter the conditions. The typical gas density switches used in GIS (and other SF6 insulated equipment) are temperature compensated, so that they measure accurately across the range of acceptable operating temps.

So if you expect the temp in which your GIS is operating will stay pretty consistent (such as indoors in a climate-controlled building), you can go with the manometer pressure monitor. If the temp is expected to vary, pay the extra for a temp-compensated gas density switch.

If I were paying the big bucks for a GIS installation, I'd also pay the little extra for option #2.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #4

Re: Medium Voltage GIS

12/03/2014 5:41 AM

Couldn't he just take P and T readings and use simple math in a PLC to find density? That's assuming he needs density explicitly, maybe P and T OK for monitoring. Though it would have to be transducers, not switches.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6
In reply to #5

Re: Medium Voltage GIS

12/03/2014 8:36 AM

The purpose is not specifically knowing what the pressure is, but rather that it is or is not adequate for insulation. The magnitude is not so important.

Usually there are contacts operated on specific pressure values, to indicate low gas pressure alarm point (Warning!) and low gas pressure trouble point (Danger!). The first should cause maintenance personnel to investigate and make repairs, while the second should initiate emergency action such as tripping the breaker, blocking operation, etc.

So the temperature compensated density switch is important, because at a high temp the manometer may indicate enough pressure to appear adequate and not cause an alarm, but have low enough density not to provide proper insulation. And at low temps, the manometer-based switch may indicate too low pressure and alarm unnecessarily for adequate gas density / insulation.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #6

Re: Medium Voltage GIS

12/03/2014 9:05 AM

OK thanks

__________________
Give masochists a fair crack of the whip
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Nov 2012
Posts: 18
#8
In reply to #6

Re: Medium Voltage GIS

12/06/2014 12:38 PM

Thanks Mr. Peter T for the good explanation.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: