A steam injection skid for gas turbine has two flow transmitter which is having different kind of tapping and condensate ports. the bottom side high and low tappings are connected through condensate port and upside tappings are connected directly with out condensate port . both trasnmitters are installed at a elevated position . how does it works pls help me i dont have hookup for this
Good Answers: 11
Re: Flow Transmitter
12/10/2014 5:32 AM
It can not be helped, schematic diagram is too small to read.
12/10/2014 5:54 AM
Good Answers: 21
12/11/2014 5:28 AM
Agreed.
12/10/2014 5:35 AM
Gravity.
Gravitation - Wikipedia, the free encyclopedia
It pulls you, and liquids, "down".
Good Answers: 122
12/10/2014 8:59 AM
Both transmitters are looking at differential pressure (pressure drop across the measuring sensor).
The upside measurement is steam in a gaseous form which per the system design suffers minimum condensation in the sensing lines and therefore does not require a condensate port.
The bottom side measurement is taken at the low point of the system where maximum condensation occurs so it must have a condensate port.
Hope this helps.
Good Answers: 11
12/11/2014 5:46 AM
This is some sort of ΔPressure flow meter with a standard orifice in the middle I should say, his diagram is quite small still(I'm too lazy to see). Other side(low pressure side-after the orifice) needs to have condensate drain if High Pressure side is saturated vapor state. By PVT property diagram lowering the pressure will end up the state at Low Pressure under the saturated water region, some steam will condensate by converting pressure to high velocity at the edge of the orifice.
But this is a little bit classic set up. We have one ΔP transmitter set-up (w/ LP+HP ports already) available on the market.