Alarm Configuration

12/09/2014 8:44 AM

Dear All,

We have Low -Low Pressure alarm connected to ESD(Emergency shutdown system ),From where it is connected to DCS On Modbus RS 485 For Low pressure alarm

Now recomendation is to segregate DCS alarm from ESD and use Independent Pressure transmitter for low pressure alarm.

May I know whether this is any Violation in this approach,since this design is proven in use in our plant.

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#1

Re: Alarm Configuration

12/09/2014 8:59 AM

If you have stated the situation correctly, then no, you have done nothing that will compromise the safety system (ESD). You will simply lose the indication on the DCS.

There are 2 consequences:

1. You will never get the 2 pressure switches to activate at exactly the same point. This could mean having a trip from the original pressure switch, with no indication on the DCS; although if your ESD has an indicator panel, that may not matter.

2. If, as stated, the shutdown is low-low and the DCS uses a low setpoint, then you will get the DCS alarm before there is a shutdown. Hopefully in time to prevent the shutdown.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#2

Re: Alarm Configuration

12/09/2014 8:59 AM

It depends on what guidelines your plant you are following and you are the only one knew it.

An alarm system is just a discrete analog I/O you may have it a single loop circuit or integrated to PLC or DCS.

You have options also to incorporate it to the old DCS via analog I/O module.

Or you may reprogram ladder on your dcs and provide discrete output module for separate annunciator.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Alarm Configuration

12/09/2014 12:22 PM

As is usually the case... the answer to this is not so cut and dried as you may think. Currently, the ESD system passes on the change in I/O data to your DCS.

Making this change will cause no issues for the ESD system, however, as your "whole" system consists of the ESD and the DCS system, no one but a person who fully "knows" and understands the entire system architecture can comment on whether or not this proposed change will perhaps introduce a failure mode that was not anticipated.

Do not make this change... until any linkages that may be impacted are "fully" understood.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#4

Re: Alarm Configuration

12/09/2014 12:58 PM

As always, a lot of questions with little information.

  • Does the ESD automatically shut down the equipment or is it a visual / audible alarm where it needs an operator to intervene and shut it down?
  • Why the recommendation to separate the alarms?
  • I don't see it as a violation in standard electrical practices, however if it also runs through the E-Stop circuit, you may need to modify that too?
  • Where is this located, Country, City?
  • What are the electrical code requirements?
  • The more information the better!
__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#5

Re: Alarm Configuration

12/09/2014 5:46 PM

Jose, what type of equipment are you talking about? does this have anything to do with a steam turbine or anything to do with Level Transmitter -Radioactive?

Being that I'm not there Mumbai, I am not familiar with your codes or what kind of equipment this alarm system is connected to, it would be irresponsible for me to make any recommendations.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#6

Re: Alarm Configuration

12/09/2014 9:34 PM

The electronic RS-485 link that communicates the alarm signal to the DCS should be electrically/optically isolated between the alarm generator and the DCS to minimize the probability of an electrical fault on the DCS side from destroying the ability of the alarm generator to function normally. Same concept as an I/S barrier protecting the I/S instrument in the hazardous area from an electrical fault in the safe area.

Register to Reply
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#7

Re: Alarm Configuration

12/09/2014 11:43 PM
  • Does the ESD automatically shut down the equipment or is it a visual / audible alarm where it needs an operator to intervene and shut it down? Auto Shut down
  • Why the recommendation to separate the alarms?, Based on SIL Report
  • I don't see it as a violation in standard electrical practices, however if it also runs through the E-Stop circuit, you may need to modify that too?
  • What are the electrical code requirements? NEC 70, cL 1 , div 2
  • The more information the better!
  • The more

7000 HP pump motor, I am refering to pressure transmitter

Register to Reply
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#8
In reply to #7

Re: Alarm Configuration

12/10/2014 9:06 AM

First: It looks as if the alarms are High, and High-High, not Low and Low-Low; although it is a little hard to be sure from the bit map you posted.

Second: If you have a "SIL Report" recommending the separation, why are you polling internet strangers to fight the idea?

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#9

Re: Alarm Configuration

12/10/2014 9:33 AM

I think you answered your own question. If the SIL report recommends you separate the alarms, You should follow their report and do it!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#10

Re: Alarm Configuration

12/10/2014 10:25 AM

Having a SIL Report or not... "No" changes to this control system should be made by anyone! Until such time as the full impact of ANY change is fully understood completely.

Doing otherwise is reckless in the extreme. I would sure hate to dead end the output from a 7000 HP pump because some timing issue was not addressed properly by way of this "minor" change!

Do the legwork first!

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#11

Re: Alarm Configuration

12/24/2014 12:47 AM

Hello josej,

Your statements are not very clear. Do you have a pressure transmitter connected to both your ESD and DCS? Or is it a pressure switch? If it's a pressure switch, does it have two settings? One for low alarm and one for low-low alarm?

It's a little hard to provide answers if the original question opens up more questions.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

dj95401 (1); Iris (1); josej (1); Kilowatt0 (2); North of 60 (2); Noudge79 (1); Original_Macgyver (2); Vulcan (1)

Previous in Forum: Most Efficient Use of Generator?   Next in Forum: Flow Transmitter

Advertisement