Induction Motor Tripping: On Same Load One Trips While Other Does Not

12/29/2014 10:52 AM

We have 22 kW, 400 V, 42 A motor. It runs a conveyor belt. During no load motor consumes 21 Amp. when material is put on the belt,motor trips on overload.

Insulation resistance of the motor is O.K. Phases resistances of all phases are the same. No abnormality is observed.

When we install another new motor 19 kW, 400 V, 37 A,that motor now runs normal, consuming about 19-20 A at no load. This motor does not trip on load (when material is put on the belt.

when we put previous motor again after changing its bearing, same overload tripping situation occurs (when material is put on the belt).

Don't understand what is the problem with the motor ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 10:59 AM

Was this a used motor (the one that was failing) or a new motor?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Anonymous Poster #1
#3
In reply to #1

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 11:19 AM

This motor was in use since 2007. from previous month, this situation happens. No issue of overload device.

Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#8
In reply to #3

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 1:41 PM

Are there predictive maintenance program like motor winding temperature data gathering daily? What is the NEMA rating of the coils? Life expectancy to certain type of winding coils at corresponding temperature is about 20,000 hrs.

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#2

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 11:09 AM

check overload device

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#4

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 11:35 AM

I suspect that the windings of your used motor are well worn. That is to say that with a full load, the additional heating is enough to break down the insulation somewhere in the tightly wound coils. It is usually less expensive to have the motor rebuilt (or rewound) with new wire than to buy a new one. Always make sure that the cooling system is open and not clogged with dust. Excess heat is not your friend.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 11:36 AM

Dear Friend,

It appears from your statement that you have checked the Stator only but not the Electrical Condition and Mechanical Condition of the Rotor. namely bend in the shaft, Bearing condition etc. You have not stated whether the the motor is of Slip-Ring Type or Squirrel Cage type.

The problem of tripping may be:

1. From Mechanical Aspect such as Bent Rotor Shaft, problems in the Bearing, causing heavy friction by damaged roller/ball causing severe resistance for rolling. There by starting current is very high and trips.

2. From Electrical Aspect - Defective Rotor - no continuity in the rotor circuit, damage in the squirrel cage rotor namely loose end of the rotor, change in the magnetic character of the rotor, very large air-gap than required between the rotor and stator etc.

Pl. check for the above items and inform us what was the problem, and how solved.

DHAYANANDHAN.S

Reply
Anonymous Poster #1
#11
In reply to #5

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 9:05 PM

Motor is squirrel cage induction motor.

Last month it was tripped on phase un-balance. when we check, we found that connection plate inside the terminal box was broken. change the terminal strip.

Motor is connected to the gear unit via fluid coupling. cooling fan is O.K.

Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#12
In reply to #11

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/30/2014 9:45 AM

The stator may have sustained damage due to single phasing, but then who am I to say anything, I shall relegate my postings to "Caption this" blog.

__________________
CRTL-Z
Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#6

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 12:44 PM

You have not stated what amps are for original or replacement motor when loaded.

__________________
CRTL-Z
Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 12:47 PM

Most likely the motor is tripping the overlaid relay because... pay attention here... it is drawing too much current under load! You posted the no-load current, which is of zero value in troubleshooting, but failed to mention what the current was when the overload relay trips.

If you used a basic hand held multimeter with a 9VDC battery to attempt to check the stator insulation resistance, and not a 500V megger (megohmeter that charges the winding circuit to 500VDC and looks for leakage to ground), you are wasting your time and likely beyond help by an anonymous Internet website. You need to have it looked at by an electrician or motor technician with the proper tools and training.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#9

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 1:51 PM

Like many post info given is incomplete or just not given. You would think some one took the time to check no load current would also check the current under load. The statement as one trips the overload the other doesn't is poor info to define a problem.

All this could be caused by some one spilling something sticky on the belt. The extra friction caused by the sticky substance. That is on the back of the belt. Under load could just be enough friction to have the old motor draw just enough amps to trip the over load. The new motor could be running just under the threshold need to trip the overload. I seen this problem in the grocery industry where damaged container leaked on the belt.

Then he says he puts a load on it. The same load? Uniform over the length of the belt.

There are over mechanical problems with the conveyor which could also cause this.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10

Re: Induction Motor Tripping: On Same Load one Trips while other doesnot

12/29/2014 2:18 PM

To say that your motor is running at "no load" when it is in fact driving a conveyor negates all the rest of your information.

What does the nameplate say the no load, and full load amp draw should be?

What NEMA class is your motor?

There's too much you don't know!

If the fact that a smaller motor is driving your conveyor without a problem should tell even you where the problem lies.

Get the motor looked at by a competent service person. Yes, that will cost you money.

Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#13

Re: Induction Motor Tripping: On Same Load One Trips While Other Does Not

12/31/2014 10:04 AM

There are multiple possibilities.

The stator and/or rotor laminations have been damaged. (Shorted due to insulation failure, shorted due to physical damage of the rotor dragging on the stator laminations surface caused by motor bearing failure.)

The rotor laminations shorting rings have been damaged or are broken/open causing loss of magnetic flux and decreased HP/torque.

The rotor is not running in true magnetic center of the stator. (Run the motor uncoupled and scribe the shaft next to the bearing then couple the motor and verify the shaft is maintaining magnetic center while operating under load.)

The motor windings are incorrect. (Wrong conductor size, wrong span, wrong number of coils, wrong number of turns in each or one or multiple wing coils.

There are one or more shorted turns in the motor winding that are not discernible with a VOM and require a motor analyzer for identification.

If the motor has been rewound more than three (3) times, the laminations are highly suspect.

I recommend you send the motor to a reputable motor winding shop for evaluation, and ask for test results as well as recommendations for possible rewinding.

I would insist on a warranty from the motor winding shop before spending any monies for repair and/or rewinding.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Score 1 for Good Answer
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); dhayanandhan (1); JRaef (1); lyn (1); NotUrOrdinaryJoe (2); Noudge79 (2); ozzb (1); SHOCKHISCAN (1); Unredundant (2)

Previous in Forum: A Question About the Circuit Shown   Next in Forum: Garage Refrigerator Trips GFCI

Advertisement