Anonymous Poster #1

A Question About the Circuit Shown

12/28/2014 8:08 AM

I want to show this circuit but cannot get the sketch done in Paint to cooperate. so I will describe it as best I can. The power is delivered in the normal way to the building. It goes to a meter box , through fuses. Two branches pass through a fuse each and then is fed by a three core wire (red, black and white) to a second attached building about 25 or so meters away. A separate earth wire accompanies the 3 core wire. These end up in a distribution box. the red is fed through a fuse which feeds three separate lines of power points. One line loops around 4 outlets, the second around 5 outlets and the third to one outlet. The white wire also goes through a fuse to a switch and then a light. The neutrals all return to the distribution box and are tied to the earthed neutral bar with the neutral from the 3 core wire.. The earth wires from each outlet also all meet at this bar. Neutral and earth are common to both the distribution board and meter box. The question is why, when there is no current drawn from the outlets (that is nothing is plugged in or turned on) there is a spark when the fuse for the power circuit in the distribution board is pushed home. the spark is very small but definite. The radio fed by a separate circuit from the first power board picks up the static and continues to produce static till the fuse is withdrawn. The lighting circuit displays no such behaviour. The earth is fed back to the first board and then sent a good 15 meters to the systems earthing point. Would a second earth at the second board help. I inherited this system some time ago but only just picked up the spark when I replaced the fuse after pulling it while I was away for an extended period. Any explanation of this would be a help.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#1

Re: A question about the circuit shown

12/28/2014 8:28 AM

show sumtin wud you?

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#2

Re: A question about the circuit shown

12/28/2014 8:33 AM

Hello Anonymous, Would suggest draw hand sketch and post it…..hope you will appreciate..

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#3

Re: A question about the circuit shown

12/28/2014 8:48 AM

"A separate earth wire accompanies the 3 core wire."

Check you local codes!

At least here in the US you can not do that. You must drive a separate earth ground for each building.

Running a ground wire between buildings creates a ground loop. That may be your root problem. BUT...

Always, always check your local building codes for how to do things or contract the work out to a licensed contractor.

Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#40
In reply to #3

Re: A question about the circuit shown

12/30/2014 1:25 AM

The NEC does not simply require a separate ground rod for each detached structure with a sub panel. Nope.

Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4

Re: A question about the circuit shown

12/28/2014 9:16 AM

Probably sparking because of the capacitance between line and earth. There will be an initial (possibly very high but very short duration) current when the circuit is made (by plugging in the fuse) and the capacitance charges up, if the AC isn't crossing zero at the time.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: A question about the circuit shown

12/28/2014 9:22 AM

"Any explanation of this would be a help."

You have an ungrounded circuit with a phantom electrical short somewhere in the system that you can't find.

Hire a qualified electrician immediately!

Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#6
In reply to #5

Re: A question about the circuit shown

12/28/2014 9:32 AM

I think it may be his earthing scheme that is the problem.

Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: A question about the circuit shown

12/28/2014 9:38 AM

Me, too.

Also something a qualified electrician could resolve rather easily, if paid to do so.

These problems can't be solved, pro bono, sight unseen.

Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#8
In reply to #7

Re: A question about the circuit shown

12/28/2014 9:53 AM

True, and there is liability involved. This is why there are licensed and bonded professionals.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9

Re: A question about the circuit shown

12/28/2014 9:59 AM

It has become evident that there must be a shortage of qualified electricians in the world.

I say that because of the astronomical number of people who come here and ask the forum to fix their electrical problems for them. Usually without providing any meaningful information.

And of course expecting to get their problems explained to them and solved for free.

Either it's a shortage of electricians or an excess of cheap-ased people who want others to work for them for free.

I'll go with # 2.

Hire a qualified electrician!!!!!!!!!

I borrowed this from another "troubleshoot my unexplained, unknown electrical problems for me, and do it for free" thread that just came here.

Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#10
In reply to #9

Re: A question about the circuit shown

12/28/2014 10:26 AM

I understand somehow the things you've been through the years. ;)

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#18
In reply to #9

Re: A question about the circuit shown

12/28/2014 4:14 PM

"It has become evident that there must be a shortage of qualified electricians in the world.

I say that because of the astronomical number of people who come here and ask the forum to fix their electrical problems for them."

I don't know what your life experiences with licenced electricians has been Lyn but from my 20+ years of having to deal with licensed electricians I have came to the dismal conclusion that they are much like licensed vehicle drivers you will find in any shopping mall parking lot in that very few have any competence to justify what their licence is supposed to represent.

Given that I have zero issue with dispensing free advice to anyone, who does not post anonymously of course, in an attempt to keep one more poor soul from having to lose more money than necessary to some overpriced fool with a piece of paper that says 'I R A Letrican' that is more likely than not going to push for the most expensive fix he can get the customer to fall for and not the simple easy yet still legal one that corrects the problem.

Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#20
In reply to #18

Re: A question about the circuit shown

12/28/2014 5:09 PM

QUALIFIED. Not licensed.

Big difference.

Point is still the same.

Anons ask that their undefined problems be solved, no charge.

Reply Score 1 for Good Answer
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#45
In reply to #20

Re: A question about the circuit shown

01/01/2015 2:17 AM

If the problem is all ready undefined, then, ANY answer is also undefined. So, why not just give an undefined answer to an admittedly undefined question that was posted anonymously? Grow a pair and take a stab at it!

And go change your shorts.

__________________
Most people are mostly good most of the time.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11

Re: A question about the circuit shown

12/28/2014 11:38 AM

There are multiple problems in this thread.

  1. There is the stated problem of a spark, a fuse and a radio. I will save my reply on this problem until later.
  2. We have no idea where this failing power distribution circuit resides. The only hint is the nominal unit length of a meter. This implies that the circuit is outside of the United States. The location would provide at the very least a hint of the nominal power distribution voltages and frequency. I have no idea if this circuit resides inside a merchant marine vessel, multiple story apartment complex, sub-divided warehouse, factory floor, hospital, commercial aircraft, single family residence, etc.
  3. There is no organization of the sparse information that is provided. This makes it very difficult to troubleshoot this circuit problem. This lack of organization of insufficient information implies the next, most critical problem of this thread.
  4. The anonymous poster that started this thread has no training in electric power distribution. This conclusion makes the sparse information you do provide us suspect. While fuses are still used in critical points of all power distributions, the most common device used today is a circuit breaker, not a fuse. You do not even identify clearly where this spark happens. Is it the flash of a fuse blowing open? Is it a mild snap you hear as you screw in an Edison style fuse that leaves a tiny burn mark on the contacts? You should not be doing any work inside any power distribution panel. GET OUT! Hire an electrician to examine, troubleshoot and properly repair this circuit.

Now, as I promised, I will offer a WAG what is the problem with this circuit.

By pulling the power from this circuit while you were away you enabled something to breakdown the isolation between power and ground. This could be anything from vermin eating the insulation to water infiltrating through some insulation cracks. You may have prevented this circuit from igniting the insulation by removing power. You might have accelerated the deterioration by removing power, too. The electrician you hire should be able to identify what happened.

If your power distribution panel actually does have Edison style fuses, then don't be surprised if your electrician suggests rewiring the whole structure. Edison fuse panels have not been standard installations in the USA for over sixty years. Electrical insulation cannot last forever.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #11

Re: A question about the circuit shown

12/28/2014 12:04 PM

"don't be surprised if your electrician suggests rewiring the whole structure."

A competent, ethical electrician will NOT touch an old outdated system like that.

The old Ark. farm house, built in 1939, is an example. It's out in the country, but no one will even work on it.

OP is dreaming if they think a free, internet fix is coming.

"The supply of fools people who want a free ride will always outstrip the demand".

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #12

Re: A question about the circuit shown

12/28/2014 12:35 PM

Yes, this is probably just a cheap b@$~@rd trying to get a free internet fix.

I still find it annoying, to say the least, that people have such little respect for power distribution design and standards. I do not believe people do not ask anonymously on a website how to set a broken bone but they will ask how to wire a three phase motor with single phase power. The poorly set bone may cripple one and can often be repaired later. The poorly wired circuit can easily kill a whole family.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #13

Re: A question about the circuit shown

12/28/2014 12:47 PM

"Dears,

I have this shooting pain in my head and there's blood flowing out of my left ear.

Please tell me how to fix this, urgently."

We (the forum) know not to try to give medical advice.

Sadly, we dispense free, lethal electrical advice many times a day.

Reply Score 1 for Good Answer
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#30
In reply to #14

Re: A question about the circuit shown

12/29/2014 3:23 AM

"Dears,

I have this shooting pain in my head and there's blood flowing out of my left ear.

Please tell me how to fix this, urgently."

Take 18" of sterile 2" white open weave gauze and push into left ear with an ice pick. This will solve both problems at once.

Who says we won't give medical advice? I am gooood doctr. got my debree in da mill yetserdy. you pay will trvl.

Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Reply Off Topic (Score 5)
Anonymous Poster #2
#37
In reply to #30

Re: A question about the circuit shown

12/29/2014 12:23 PM

That's crappy advice... That's how I got the problem in the first place!

Reply Off Topic (Score 5)
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#39
In reply to #37

Re: A question about the circuit shown

12/29/2014 6:44 PM

But it was free.

__________________
Where's the KaBoom? There should be a KaBoom!
Reply Off Topic (Score 5)
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#32
In reply to #14

Re: A question about the circuit shown

12/29/2014 6:52 AM

Re Lyn post 14: "...I have this shooting pain in my head and there's blood flowing out of my left ear. Please tell me how to fix this, urgently."

How about a tourniquet around the neck! that should stop the bleeding. But beware, it needs to be released from time to time to allow blood to flow again, otherwise there is a risk of gangrene setting it. It needs to be done by an expert, or if DIY, under expert medical supervision.

But in answer to the OP, you usually get a microscopic spark even with a brand new installation - it's capacitance of the cables and nothing to worry about. On the other hand it could be due to something more sinister like rogue wiring - for which you will an expert to investigate and put right.

On the question of free advice on CR4, is there a legal liability on CR4 members, leaving us open to expensive litigation if something goes wrong when advice is acted on?

__________________
When arguing, remember mud-slinging = lost ground.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#33
In reply to #32

Re: A question about the circuit shown

12/29/2014 9:08 AM

Nothing legally binding, I'm sure.

Only a moral/ethical obligation to not arm idiots with potentially lethal information that they are incapable of using safely.

I know this will not stop the forum from dispensing such information, but.......................

Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#15

Re: A question about the circuit shown

12/28/2014 1:38 PM

More than likely the white coming from the main building is the neutral and not a powered conductor.

Get a pro!!

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Anonymous Poster #1
#16

Re: A question about the circuit shown

12/28/2014 3:42 PM

Thank you all. I have no intention of fixing this myself. I do have a certificate in electronics and am just curious as to what possible explanation there is for this. the installation is an old one (early 50s)and needs changing and will be changed. It is in a remote area and electricians are hard to entice out there for this kind of a job. The fuses are pulled and till the problem is fixed it will stay that way so please don't think I am stupid about it. I thought of capacitance and that is why I wondered if a second earth line from the distribution board would help. The white wire is not neutral as it feeds the lighting circuit in the second building. The black is neutral and is common for both the power and lighting circuit. Until I can get an electrician interested enough I will have to do with out power in the second building. Also I do have some experience having worked as assistants to some electricians in the past so was able to trace the circuits. Wish I could get the drawing on here but I don't seem to be able to. I respect 3 things AC, DC and JC none of which I can see. Hope that puts all your minds at rest as to the safety issue.

Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#21
In reply to #16

Re: A question about the circuit shown

12/28/2014 8:59 PM

That's a 3 phase line with Neutral and Earth and your question was again why is there a spark on new fuse when you pull it out, even if the line is without load? Right?

Conduct insulation and line to ground test with that line, down stream extending from fuse to outlets or make voltage readings Fuse point to ground as well as the outlet to ground, if you see a little discrepancy then that's causing the spark, possibly, installation was 1950, some insulation might have been degraded already its more than 60 years now.

Get basic electrical circuits theory and make the most ou of it, research on the web far more.

Remember, safety first not electrocution first, alright?

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#22
In reply to #21

Re: A question about the circuit shown

12/28/2014 9:16 PM

Where in the world did you get a 3 phase line with a neutral and earth from? This requires five conductors.

A split phase with neutral and ground maybe run with black, red, white and ground cabling. More often than not a black, red, white and ground wire will be used between two three way switches (a misnomer) to allow control of a lamp from two locations.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#23
In reply to #22

Re: A question about the circuit shown

12/28/2014 9:27 PM

You run 3 wires into a transformer then you get a Neutral from it, if that is the case down here. I bet this raise the poor guy's level of confusion by then. =) Hey Anon, you better get an expert to see your problem, other than seeking here for a solutiom.

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Power-User

Join Date: Dec 2013
Posts: 201
Good Answers: 5
#28
In reply to #16

Re: A question about the circuit shown

12/28/2014 11:52 PM

three phase not an option in our area

Reply
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#29
In reply to #28

Re: A question about the circuit shown

12/29/2014 12:46 AM

A what????

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Reply Off Topic (Score 3)
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#31
In reply to #16

Re: A question about the circuit shown

12/29/2014 3:31 AM

Haven't done it but I have seen wires laid directly in ground instead of in a conduit. At that age there would be insulation breakdown and that would lead to.. well I am sure you know.

Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#17

Re: A question about the circuit shown

12/28/2014 4:02 PM

Too bad you chose to post anonymously. This sounds like a no brainer for me to diagnose and explain in a way that others would follow more clearly plus sounds like a rather easy problem to correct as well. .

Oh well......

Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#19

Re: A question about the circuit shown

12/28/2014 4:39 PM

Typically the power coming in to the building is 220 volts, using 3 wires colored red, black and white.. normally are terminated as follows; Red-- L1, Black-- L2 and White as the Neutral...

Normally the measured voltage between Red and Black = (L1 and L2) = approx 230 Volts, while the voltage between White and either Red or Black = approx. 115 Volts each.

In your descriptions, it seems the Black and White wires were cross-wired? A dangerous, unsafe, shock and fire Hazard situation...

1) White wire is fused.. powered? therefore either wrong or interchanged color coding used in house wiring?

2) the Black wire (is not connected or terminated to anything? Or used as the Neutral wire instead?

To be safe you should get a licensed electrician to examine and correct the existing hazardous situation!

__________________
vsar
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#24
In reply to #19

Re: A question about the circuit shown

12/28/2014 10:40 PM

The OP has offered no commentary on where in the world he is... as such, your comments about the nature of the system involved and the colours used, are pretty much only true in North America.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#25
In reply to #24

Re: A question about the circuit shown

12/28/2014 11:13 PM

Everyone knows cutting the red wire will stop the bomb timer.

Oops, wrong thread.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#27
In reply to #24

Re: A question about the circuit shown

12/28/2014 11:44 PM

Too true, the fact that the OP mentions metres for his distance would indicate that it is indeed not the US.

Here in Australia, although there is no legal requirement for neutral and active colours to be anything but green/green yellow, the norm for a 2Φ + N supply would be red and white for actives and black for neutral as the OP has stated, .

If the phases are 120° shifted, then the voltages would be 415v between actives and 240v active to neutral.

If the phases are 180° shifted then the voltages would be 480v between actives and 240v active to neutral.

Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#38
In reply to #24

Re: A question about the circuit shown

12/29/2014 4:45 PM

Not quite true North of 60!

Other countries, even those in the 3rd world categories, mostly situated in Asia, do have wiring standards to follow as a minimum as stated by the NEC guidelines!

Without any wiring diagram, The posted question, although deemed to be a wiring problem may in reality turned out to be Not a real problem!

I think It is Not problem as observed by the poster in the following scenario. If an electrical appliance happened to be directly wired across the two split source, typical to a 220 volt rated or operated system. It will be normal to experience an arc even momentarily even with the unit being Off..

__________________
vsar
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#26

Re: A Question About the Circuit Shown

12/28/2014 11:40 PM

Draw a schematic of this layout on paper.

A simple line drawing will do.

Take a picture of the drawing and upload it to this site.

Identify the colors of each wire,show all conductors and grounds,including ground rods and bonding straps, if any.

Is the circuit 3phase,or single phase? What is the voltage of the circuit?

Where are you located?

If this is a single phase 240/120 volt circuit,why is the white being used as a hot wire?Why is the black used as a neutral?

In electronics,the black is ground,but in A/C it is always the hot wire.

By some chance,did an electronics tech wire this stuff up?

In what country are you located?

IF you provide adequate information, someone may be willing to help you,especially if you are not anonymous.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#34

Re: A Question About the Circuit Shown

12/29/2014 9:48 AM

If you are getting a spark of any magnitude, you have potential to earth. To properly diagnose this I would have to put my eyes and hands on it or at least have a hand-drawn sketch. I have run into similar issues with electricity back-feeding through a light bulb that someone connected in a hot-wire loop feeding the outlet from 2 different taps in the breaker box. Luckily they connected both the receptacle taps to the same phase so it didn't go BOOM! However, I found it by grabbing the outlet and got a nice 60 volt A/C shock. Boy did it tingle. Lesson learned and I always check all taps for any voltage potential.

Good Luck

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#35

Re: A Question About the Circuit Shown

12/29/2014 10:12 AM

Really - you need a sketch. Otherwise we are just guessing.

Here goes my best guess. Dirt in the outlets.

I was in "electrical maintenance" for 6 years where I work, until we really got rolling on process skids so that I had a full time job designing controls. In the maintenance job, I regularly had to clean out receptacle boxes (installed by a "qualified" and licensed electrician by the way with the typical handy box full of holes) in a metal grinding area of the plant, as they would blow the circuit breaker - just about every week without cleaning. You have not described the area where your outlets are, but it doesn't take much of a conductive dust to get a current flowing between the hot terminal and the neutral on a typical receptacle at 120VAC and you are probably talking 220VAC in your case. You were "away" - did the local vermin build a nest in one? Do you have a fried rat in one? The corpse would be conductive for some time.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#36

Re: A Question About the Circuit Shown

12/29/2014 10:30 AM

Don't know where in the world you are, but in the USA we use the National Electric Code published by the National Fire Protection Association. In that code using the ground as the neutral has not been allowed to an out building for many years. Separate the ground (earth) from the neutral and make sure all connections are good. -- JHF

__________________
If it's too good to be true, it probably isn't
Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#41

Re: A Question About the Circuit Shown

12/31/2014 3:53 PM

The conclusión is obvious, you have eliminated the possibility of normal loads so you clearly have an "abnormal" Load, otherwise known as a leak!

Your clue of "static'' being picked up by a radio on a another branch circuit implies insulation breakdown. This could be cable failure (rats, damage made during installation or similar) or water ingress into one of the outlets or a junction box.

The circuit will need to be checked, point by point, to find the fault.

Remember, stay within your comfort zone with electrics as there is real danger if you get it wrong

__________________
En la casa del herrero, cuchillos de palo!
Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#42

Re: A Question About the Circuit Shown

12/31/2014 4:32 PM

Where the hell is the magnanimity that used to be here on CR4? If someone asks a question then they are seeking an answer. If you are unable or unwilling to give them a useful answer then don't bother posting.

We do not know why the op hasn't contacted an electrician, money is an obvious reason but there are many other reasons, not everyone lives in a metropolitan area with easy access to tradesmen.

Regards chas

__________________
En la casa del herrero, cuchillos de palo!
Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#43
In reply to #42

Re: A Question About the Circuit Shown

12/31/2014 6:29 PM

Capblanc -

That may be one of the reasons why posting anonymously is not advisable, and therefore not being given much attention /responses by those 'knowledgeable" CR4 members!

It may also due to be a Holiday week, and most are on vacation..

__________________
vsar
Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#44
In reply to #42

Re: A Question About the Circuit Shown

12/31/2014 10:45 PM

You wish to know where my generosity went, it went the way of a non-responsive visitor. I asked for some very specific information from the AP and get none of my requests addressed. I did get a confirmation in the only reply by the AP to somebody else that this old wiring does have fuses but I did not ask for that piece of information. When I ask for a clarification I am generously offering to help.

Also, looking for an answer and understanding an answer are completely different things. By not answering or understanding the relevance of even the most rudimentary question of "where is this?" makes me wonder if they will understand the meaning of a good answer.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#46

Re: A Question About the Circuit Shown

01/03/2015 12:05 PM

Can't help with the answer but if you need to post a diagram there is a great free programme for schematics etc called Dia. Works a lot like Visio.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Reply
Anonymous Poster #1
#47

Re: A Question About the Circuit Shown

02/06/2015 11:23 PM

thank you all for your help. Just thought you would like some follow up. It took a while to trace the problem to an extension lead that had the active and neutral reversed on the female plug side. I rarely use the lead but have had it for over 25 + years. I can not remember if it was me or some one else who wired it up back then. I was more curious than anything as to the cause of the symptoms. I am still trying to beg borrow or even offer a large wage to get the buildings checked by an electrician. Thanks all.

Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#48
In reply to #47

Re: A Question About the Circuit Shown

02/10/2015 4:18 AM

Not plurry likely mate! But there would appear to be some problem with the lead ( or the socket you plugged it into) if the symptoms only appear when it is plugged in.Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#49
In reply to #47

Re: A Question About the Circuit Shown

02/10/2015 10:57 AM

Reversing the neutral and hot will not cause noise on the radio,but a loose,arcing connection in the cord end would do it under load.

Perhaps when you reconnected the wires you got a more solid reliable connection into the cord plug or socket and solved the problem.

Try this:Turn on the radio,and just barely make contact with any load on any

receptacle,and jiggle the connection.You will hear noise on your radio.

The noise is created by the sparking of the conductors and the arc emits a noisey magentic field.

It will be worse on AM radio than on FM,due to the signal characteristics.

Same thing happens in thunderstorms,except the effect is widespread,not local.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#50
In reply to #47

Re: A Question About the Circuit Shown

02/10/2015 11:37 AM

As I mentioned in my earlier posting the symptoms mentioned is typical for a reverse wiring polarity. As indicated in other postings, the humming noise problem is indicative of loose connection creating an open /close circuit that results into RF noise being radiated.

As in any electrical circuits, any apparent problems will only be pronounced when any actual load(s) gets connected thus creating a completed circuit!

__________________
vsar
Reply
Anonymous Poster #1
#51

Re: A Question About the Circuit Shown

03/26/2015 4:42 AM

I do not know if any one will see this post so long after I posted the original. When I made the measurements I was using a new multi meter as my old one was cactui routitus (as we say here). The new one is the type that adjusts to the voltage, the old one was not. So what looked like 112 volts AC was actually 1.12 milli volts. There never was a problem. Anyway the whole job has been sorted now. Thanks for the answers. As a matter of interest The wife just bought a new old house. I checked the roof cavity before to see the condition of the roof and wiring. All good. Checked the under flooring and all was good. I should have crawled right underneath at the time though. Ran a intercom wire under there today and found some more AC wiring that used old type wire. I guess I will need to convince the electrician to come back for another job. OH well, that's life.

Reply
Guru
United Kingdom - Member - Old New Member

Join Date: Jul 2005
Location: South east U.K.
Posts: 3695
Good Answers: 93
#52
In reply to #51

Re: A Question About the Circuit Shown

03/26/2015 5:05 AM

One you subscribe there's no escaping new posts, glad you have the 'problem' sorted.

__________________
I didn't have a really important life, but at least it's been funny (Lemmy Kilminster 1945-2015)
Reply
Reply to Forum Thread 52 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Hero (3); Anonymous Poster (3); capblanc (2); chaterpilar (1); Circuit Breaker (1); cuba_pete (1); Deefburger (1); HiTekRedNek (2); horace40 (1); JIMRAT (4); JohnDG (1); Kulas (1); lyn (7); Nigh (2); North of 60 (2); Noudge79 (4); Original_Macgyver (1); Phys (1); prof peanut (1); redfred (5); spades (1); tcmtech (2); vsar (4)