Mine is a York Absorption Steam fired LiBr chiller which is designed at a nominal steam pressure of ~7bar max(for 400TR). However our load & recent chiller maintenance has rendered steam consumption only to be ~1bar max & we get an outlet temperature of ~8.5celsius.
Ok now the problem starts, please see pic below

Now you can see that there exists a noticeable elevation at condensate line & steam will be used as pump!
In summer for instance we were using steam ~4bar & we didn't encountered any problem however presently in winter if am using ~1bar steam & route condensate to collection pod instantly I observe pressure increment on pressure gauge at steam inlet, now because I haven't touched any steam inlet valve opening same amount of steam is allowed to enter but the gauge registers increasing pressure ~6-7bar then after 30mins it stabilises at ~2.5bar (remember I was using ~1bar). After three hours my parameters start to destablise (gauge at ~3bar)...generator temperature & pressure decreases indicating low heat transfer...
To remedy this I open bypass ball valve to route condensate to floor level drain thereby wasting it & not recovering it
Provided that gauge at condensate registers 1bar (controlled via manual globe valve opening) why not condensate travel upwards...I mean if I adjust globe valve to have an upstream pressure of ~1.5bar shouldn't the condensate should easily collect even after ~8m elevation.