I have 150KW, 400V, 263Amp, 1486RPM, 50Hz, 4 Pole induction motor
installed at Induced Draft Fan of 35TON Boiler, The fan itself is
capable to rotate at 900RPM so Motor is to be reduced to operate at
900RPM through Variable Frequency Drive Siemens MM440.
Following are the options to operate the motor at reduced RPM.
1. As Speed is Controlled through 4-20mA signal coming from the
DCS system.
By Limiting this signal to 4-13.7mA we can then operate the
motor at 0- 900 RPM without changing the motor parameters fed into
the VFD.
Motor was operated by limiting the mA signal following was the
outcome:
At 12mA signal
Motor RPM = 750
Output Volts: 200
Amperes Drawn 265
There is a problem of Current increase as Motor will see only 240V
at 30Hz on 13.7mA signal at its terminals because of Linear V/F
control selected.
There is other option
By changing Motor Name plate data fed into the VFD.
MOTOR FREQUENCY = 30.28Hz
If we go for second option Motor will see 400volts at 30Hz which
will reduce the current.
Does it effect Motor in any possible way?
If there is some other way to reduce the RPM (1486 to 900) please
suggest. As Motor cannot be replaced.