Power Cables Arrangement in a Conduit

01/09/2015 12:55 PM

Dear All Hope that you are doing well, Just a question, We are in process to use single core cables ( 9X240sqmm / phase) and also single core cable for earthing (9X120sqmm) to connect our 2MVA GENSET to the step up power transformer primary supply (3 phase system, 400VAC, 50Hz). These cables are planned to be laying in PVC conduits. I need to know the recommended practice we should follow when we using multiple phase conductors. The advice I received is to run each phase cables + some of the earthing cables in one conduit as following:- Conduit#1 (Phase "R") : 9 Cables 1X240sqmm + 3 Cable 1X120sqmm Conduit#2 (Phase "R") : 9 Cables 1X240sqmm + 3 Cable 1X120sqmm Conduit#3 (Phase "R") : 9 Cables 1X240sqmm + 3 Cable 1X120sqmm I am concerned about the eddy currents & skin effects, we need to avoid any possible heating resulting from wrongly assembling for the cables. Please your support Regards

Register to Reply
Pathfinder Tags: conduit power cables
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Power cables arrangement in a conduit

01/09/2015 1:00 PM

Well, you could refer to British Standard 7671 instead of asking me.

__________________
Good moaning!
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Power cables arrangement in a conduit

01/09/2015 3:20 PM

Well, by your description, you are running all phase "R" cables in the conduits. What happened to phases "S" and "T"?

To avoid problems with the electromagnetic fields, each conduit should have one of each of the phase cables, as well as your neutral and/or ground, in it. Is there some reason you cannot use larger cables so that you don't need 9 per phase? If you are planning to use only 3 conduits, you would have 3 - "R", 3 - "S", and 3 - "T" plus 3 - earth cables in each conduit. Sounds like a mess.

Either use larger cables, or more conduits, so that you limit to a single cable for each phase in a conduit.

Remember too that you have to account for (in other words, derate) the mutual heating between conduits when they are run close together in parallel. They are then not isolated, and prevent each other from cooling (whether in air or soil).

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Power Cables Arrangement in a Conduit

01/10/2015 12:13 AM

Use cable tray instead of conduit & maintain recommended formations & distances as per BS 7671

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4

Re: Power Cables Arrangement in a Conduit

01/10/2015 11:02 AM

From whom did you receive this advice?

Is the person properly qualified to give such advice,and is this person familiar with

LOCAL CODES and procedures approved by the Authority Having Jurisdiction?

It is normal procedure to put all 3 phases plus ground in each conduit,thereby

cancelling self heating that would otherwise occur due to inductive currents.

Strive to keep all conductors the same length,paying attention to bends in the

conduit routing when they are running parallel to each other.

PVC conduit will not occur any inductive heating of the conduit itself.

The ground wire size is determined by the size of the upstream breaker.

There is much additional information needed to answer your question properly,and I

have only scratched the surface.

Please refer this issue to a local qualified electrical company,and especially, the

inspector in charge of the operation.

The inspector has the final word for the approval of means and methods.

Good luck.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Power Cables Arrangement in a Conduit

01/10/2015 11:05 AM

Usually "eddy currents" are in shield or armor. These cables have to be low voltage unshielded and unarmored. Are they? Or do you mean "proximity effect"?

I don't think it will be much difference if in a pvc conduit all the cable will be of the same phase. As I know nor NEC neither BS7671 [nor IEC 60364-5-52] considers a certain order of cables in a conduit.

Your concern has to be unbalance between conductors of the same phase. If it will be close each other-no clearance between conduits at all- the unbalance could be up to 70%.In my opinion, if the clearance will be more than 1 conduit diameter the unbalance is negligible.

Anyway, it will be preferable to put them in 9 conduits each R-S-T-E phased.

__________________
Julius
Register to Reply
Participant

Join Date: Jan 2015
Posts: 4
#6
In reply to #5

Re: Power Cables Arrangement in a Conduit

01/10/2015 12:31 PM

Dear all

Thanks for your valuable advices, I think that there might be a misunderstanding, maybe I didn't explain the condition clear enough. We have to use 240sqmm for the power cables due to some purchasing deals.

The current capacity we have is about 3150Amps. And as per the cables data sheet and after reviewing the derating values we will be using 9 cables (240sqmm) per phase and 9 cables (120sqmm) for the neutral phase.

For the conduits we have to use (6 Inches) size, and it will be direct buried in the ground.

I just asked for the best arrangement for the cables, that's it.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #6

Re: Power Cables Arrangement in a Conduit

01/10/2015 1:15 PM

Save yourself a lot of aggravation, instead of arranging the conduits horizontally, place them in a triangle, symmetric and balanced, just requires a bit more defrating due to the reduced heat transfer to the surrounding soil.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jan 2015
Posts: 4
#8
In reply to #7

Re: Power Cables Arrangement in a Conduit

01/10/2015 2:14 PM

Okay, what do u recommend for cables arrangement per each conduit

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#13
In reply to #6

Re: Power Cables Arrangement in a Conduit

01/11/2015 10:08 PM

what is the length of cable run.

__________________
pnaban
Register to Reply
Anonymous Poster #1
#10
In reply to #5

Re: Power Cables Arrangement in a Conduit

01/10/2015 2:58 PM

Thanks for your help but 9 conduits !!! its an out of reach option.

The conduits we are planning to use is 6 inches diameter and we have reviewed the IEC standard to check the suitable filling degree.

The thing is that the conduits will be separated from each (as shown below)

The information that I am looking for is what is the proper arrangement for the cables inside the conduits.

We have

27 cables (240sqmm) "9 cables per phase" and

9 cables (120sqmm) "9 cable for neutral"

Our service contractor suggested to put in each conduit a complete phase cables + 1/3 of the neutral cables.

and to leave the 4th conduit as a spare.

I am still searching in the IEC & BS for the best solution and I hoped that you might help me in this issue.

For the record thanks for you all even for the passive replies

Register to Reply
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#9

Re: Power Cables Arrangement in a Conduit

01/10/2015 2:49 PM

Each conduit should contain all 3 phases plus grounds.

Yes,plural:

GROUNDS: A grounding conductor and a grounded conductor.

There is much confusion of these two terms that sound similar,but are very different.

Make sure you know and Understand the difference,take this into consideration when designing this system.

Allow me to explain why all 3 phases should be in EACH conduit:

The algebraic sum of all currents in a 3 phase system is zero; they cancel each other out.

So by running all 3 phases together, you do not generate any eddy currents unless

the phases are unbalanced.

If this is a separately derived system, there are other considerations to think

about, so consult a QUALIFIED ELECTRICAL ENGINEER.

But since you only want to know the arrangement of the wires in the conduit, your

question has been answered.

Just disregard everything else.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Good Answer (Score 2)
Participant

Join Date: Jan 2015
Posts: 4
#11
In reply to #9

Re: Power Cables Arrangement in a Conduit

01/10/2015 3:06 PM

Thanks allot for your comment,

Okay I am getting it now, As I mentioned we have 9 cables per phase and 9 cables for ground, so can we arrange the cables as following:-

Conduit#1 : 3 cables of phase "R" + 3 cables of phase "S" + 3 cables of phase "T" + 3 cables of GROUNDS

Conduit#2 : 3 cables of phase "R" + 3 cables of phase "S" + 3 cables of phase "T" + 3 cables of GROUNDS

Conduit#3 : 3 cables of phase "R" + 3 cables of phase "S" + 3 cables of phase "T" + 3 cables of GROUNDS

___________________

Its all about listening carefully to those who can teach.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12
In reply to #11

Re: Power Cables Arrangement in a Conduit

01/11/2015 3:05 PM

I don't think there is a standard for 9 cables in an underground duct-bank ampacity.

In my opinion, if the earth temperature is 25 oC and earth RHO 90 C-cm/watt then no more than 230 A will be cable ampacity for 9 single-core copper cables of 1/0.6 kV XLPE insulated 100% load factor.

You have to calculate it according to IEC60287.

It would be better to group in 3 bunches of 4 cables[R,S,T,N] in order to diminish the unbalance between the cable currents [of the same phase].However, since the temperature drop from cable to conduit, from conduit to duct-bank and from duct to Earth is the same for all cables, the temperature drop in the insulation depends only on cable individual current and could add another 1 degree C in part of the cables.

If this order is not easy to achieve I think it could be neglected.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#14

Re: Power Cables Arrangement in a Conduit

01/12/2015 12:31 AM

I meant 9 single-core cable [loaded] in one pvc conduit and 3* 6" pvc ducts.

Even 3 loaded cables in 9 pvc conduits -one conduit diameter clearance, in one row-the ampacity could not be more than 300 A.

__________________
Julius
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (3); Ahmed Osman Mohamed (3); Anonymous Poster (1); Crabtree (1); HiTekRedNek (2); PeterT (1); pnaban (2); RAMConsult (1)

Previous in Forum: Motor HP, Full Load Current and Speed   Next in Forum: DC Voltage Fuse Burnt

Advertisement