Earth Leakage Toroid Systems.

01/16/2015 5:26 AM

HI guys, I am a young electrician from Australia trying to learn more about what I am doing.

I installed over the past couple of days a range of gear to provide earth leakage protection on the generator supply cables to the main switch board of a small mining operation.

At the main switch board we have a Schneider toroid, shunt and earth leakage relay that protects the cables and equipment. There is personal protective devices installed in the required sub circuits.

my boss has been instructed by a mines inspector to install this extra gear to protect the cabling between the generator and main switch board.

My question is we have installed a toroid and run all 3 phases and neutral through the middle, the toroid is monitored by the relay which then shunts out the main switch upon a fault detection.

We have not tested this yet as its Friday and we will finish on Monday, but my boss is certain it will work but cannot explain how it works.

The loads are a mix of single and 3 phase and I cannot comprehend how it measures an imbalance if the neutral runs through the coil as well?

There is a separate toroid and relay that monitors the MEN link earthing conductor which shuts down the engine, this is totally independent of the described system I am installing.

What I would like is some information or direction to information so I can learn more about how the toroid and monitoring system works?

Thank you,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
6
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Earth leakage toroid systems.

01/16/2015 6:17 AM

For simplicity, consider single phase, with line and neutral both going through the CT. Provided that there is no leakage to earth, the line current must equal the neutral current (no-where else for it to go!), and since they're in opposite directions, they "cancel out" and there's no output from the CT.

If, however, there's leakage from the line to earth, the line and neutral currents are no longer equal, hence an output from the CT (and a trip).

Same sort of logic applies for 3-phase.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 6)
Active Contributor

Join Date: Apr 2010
Posts: 10
#9
In reply to #1

Re: Earth leakage toroid systems.

01/20/2015 2:14 AM

THANKS GURU for the answer, very useful information ,simple and easy to understand

Register to Reply
4
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#2

Re: Earth Leakage Toroid Systems.

01/16/2015 9:10 AM

HI there JDriethmuller hope all is well in sunny Oceania. I was 10 years in NZ and Oz and worked all across your beautiful country. I write to you from snowy Ireland where I will shortly be on top of a mountain at -15. But its a nice mountain all the same and there are no sharks, mozzies, jellyfish and other assorted beasties who never seem pleased to see me in Oz!

Anyhoo the previous post is quite correct. However you asked for a place to learn more and I recommend Cahiers Techniques. This is an assortment of technical information maintained by Schneider and available here:

http://www2.schneider-electric.com/sites/corporate/en/products-services/technical-publications/technical-publications.page

Specifically, there is a decent paper on RCD operation which will cover what you have asked for:

http://www2.schneider-electric.com/corporate/en/products-services/technical-publications/technical-publication-protection.page?c_filepath=/templatedata/Content/Technical_Publication/data/en/shared/electrical-engineering/protection-devices-monitoring/low-voltage-minus-1kv/ect114.xml

Hope this helps and welcome to CR4.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply Good Answer (Score 4)
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#3

Re: Earth Leakage Toroid Systems.

01/17/2015 12:32 AM

If, as you state, the toroid is mounted at the main switchboard, and said generator is supplying that switchboard, then I fail to see how that toroid and associated equipment will protect the cabling between the generator and switchboard, particularly if the generator is somewhat remote from the switchboard.

Not knowing the relative positions of the generator and the main switchboard, it's not possible to give a definitive answer, but be aware that the earth leakage relay will only protect against earth faults downstream of the detection toroid. Therefore, to protect the generator to switchboard cabling, it should be mounted as close to the generator as is possible but downstream of the MEN link.

All 3 phases plus the associated neutral must pass through the toroid for the device to work correctly.

The other question that comes to mind is the location of the main switch that the relay disconnects. If it is on the main switch board then it is not actually disconnecting an offending generator supply cable. The disconnection should take place at the generator.

Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2015
Posts: 8
#4
In reply to #3

Re: Earth Leakage Toroid Systems.

01/17/2015 5:44 AM

Wow that simple, don't I feel a little silly. There is so much to learn about this electrical game we play.

Thank you for the prompt replies & links.

Sorry I did not make my question that clear.

We have an existing toroid mounted at the switchboard about 10 metres away, the new one we have installed is located inside the generator where the windings are brought out and all the control gear is located behind the generators control panel, they were kind enough to leave room for extra components.

Its funny you should mention that it has to be downstream of the MEN, the reason I started to find more information is we have done 2 different generators this week and cannot work out why one of them does not trip on an induced fault, if we use the test function on the relay it shunts out the main switch but using 500 or 1000mA test from our RCD tester we cannot get a trip time.

My boss will be pleased to know we have to re locate the coils, thanks a lot I believe you solved our problem.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#5
In reply to #4

Re: Earth Leakage Toroid Systems.

01/17/2015 6:26 AM

A test function on most RCDs and sometimes on relays is normally only a mechanical test to ensure that the mechanism is working correctly, it does not necessarily test the actual capability of the device to detect and operate on an actual earth fault.

Is it possible that your second generator does not have an earth link, or that it is downstream of the RCD/toroid, either of the above will cause the RCD to not trip on an earth fault.

A generator is basically an isolated supply in that it has no winding to earth connection (no current path to earth). So, until you make that connection by either earthing the neutral in the case of a star point winding configuration, or one of the live conductors in the case of a single phase generator (there are a few other setups but we'll leave them alone), there is no path for stray earth currents to return to the generator and hence no chance of the RCD detecting such stray current.

Obviously the neutral - earth connection has to be upstream of the RCD so that the return earth leakage current bypasses the RCD and therefore creates the out of balance that causes it to trip.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#6
In reply to #5

Re: Earth Leakage Toroid Systems.

01/17/2015 6:40 AM

Perhaps I should elaborate a little on my previous comment "So, until you make that connection by either earthing the neutral in the case of a star point winding configuration, or one of the live conductors in the case of a single phase generator (there are a few other setups but we'll leave them alone), there is no path for stray earth currents to return to the generator and hence no chance of the RCD detecting such stray current."

Actually, with a "first fault" situation there will be no stray current to detect as there will be no current flow to earth and no live conductor to earth shock hazard either.

It is only upon the occurrence of a subsequent fault that the danger applies.That second fault normally needs to be in a different live conductor to the first fault for there to be a shock hazard, but there are exceptions.

Register to Reply
Member

Join Date: Jan 2015
Posts: 8
#7
In reply to #6

Re: Earth Leakage Toroid Systems.

01/17/2015 4:50 PM

I follow you and understand 100% now, we know both generators have MEN links via bus bars mounted under the main switch of then gen's.

We mounted the toroids upstream of the links so any fault currents will just re join the neutral current then back through the toroid. What a stupid mistake which will eat 4-6 hours to fix them both up.

If I had any idea how it worked before we installed it then I would have thought of that myself, how annoying.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#8
In reply to #7

Re: Earth Leakage Toroid Systems.

01/17/2015 6:02 PM

Consider that all the toroid is doing is measuring out of balance currents, therefore you may be more easily able to fix the downstream link problem by passing the main earth conductor from the earth bar through the toroid to the downstream neutral-earth connection. It doesn't matter which way the earth wire goes through the toroid as any current in the earth conductor will either add to or subtract from the total active value and will create the out of balance necessary to trip the breaker.

It is quite common for a multicore cable with included earth conductor to be passed through the toroid and then to return that earth back through the toroid to negate its previous passing and thus allow the RCD to correctly detect downstream earth faults.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Earth Leakage Toroid Systems.

01/21/2015 8:42 AM

It is not the task of an earth leakage device to detect imbalance. The clue is in the name.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: