E&H Levelflex FMP45

01/18/2015 7:32 AM

This radar level transmitter showing ( W153 initialising please wait ) , so the possible cause asper its manual is (initialisation of electronics) to do a power reset . I have done all asper its manual but still showing same error . I want to know its becasue of a electronic card problem or i have to do something instead of replacing transmitter or its card , pls ........

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: E&H Levelflex fmp45

01/18/2015 5:22 PM
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: E&H Levelflex fmp45

01/18/2015 5:40 PM

I would check your wiring again, you may have it connected incorrectly....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 23
Good Answers: 2
#3

Re: E&H Levelflex FMP45

01/19/2015 2:45 AM

Hi Orson,

I don't know what fluid you are measuring, but on our projects they have specced a variety of these "radar" level sensors, and the one common thread was they all were unreliable. During my one year warranty phases, I would have to change them 2 or 3 times--- failures were in the receivers (sometimes) and the sending units (often). Finally, with customer buy in, I switched to a drop in, membrane type, pressure transducer and never touched them again. And it gave me consistent readings, within an inch or two of my tape, in 12 meter deep tanks --- something the radar never came close too.

Expat07

Register to Reply
Associate

Join Date: Nov 2010
Posts: 30
#4
In reply to #3

Re: E&H Levelflex FMP45

01/19/2015 3:26 AM

Thanks

Hi Expat,

This electronics could not be initialized means the card may become faulty . we are in start / commissioning stage. 90% of level transmitters are E&H radar Fmp series . it was installed last 1.5 year ago . I want to make sure this is a kind of unsolvable error which is required a replacement of card or transmitters itself .

Register to Reply
2
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#5
In reply to #4

Re: E&H Levelflex FMP45

01/19/2015 8:15 AM

If you are now commissioning it, then it is essentially new. Why do you not call up an E&H representative/distributor and ask them? I use E&H instruments on every control system we build here, and I call them when issues like this come up and the manual doesn't cover the situation. No shame in asking for help from the true experts.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jan 2008
Location: kuwait
Posts: 132
Good Answers: 2
#6

Re: E&H Levelflex FMP45

02/01/2015 12:56 AM

this can be due to error in the communication portion which never getting access from the I/O (initial start OR ready for operation ) section .

__________________
love4everyone
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

EXPAT07 (1); lyn (1); Orson (1); Phys (1); sohail0110 (1); SolarEagle (1)